To avoid these ads, REGISTER NOW!

Planning for EV charging?

infinkc

Well-known member
Joined
Jan 19, 2012
Messages
862
you need an ATS that it talks to. no details on if its a 2 wire hook up or if its something ford integrated more tightly.
yea, must be more involved as they said that sunroom is partnered to do the charger installs.
 
To avoid these ads, REGISTER NOW!

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,835
yea, must be more involved as they said that sunroom is partnered to do the charger installs.

you technically dont need anything fancy to charge at home. the fancy charger can operate on its own. or if you're buying the basic model you only get 9.6kw charging anyways.


here is an 80a J1772 home unit.

here is a more reasonably sizes 9.6kw unit: thats still 115kwh delivered in a 12 hour session. Likely plenty for most people.
 

infinkc

Well-known member
Joined
Jan 19, 2012
Messages
862
you technically dont need anything fancy to charge at home. the fancy charger can operate on its own. or if you're buying the basic model you only get 9.6kw charging anyways.


here is an 80a J1772 home unit.

here is a more reasonably sizes 9.6kw unit: thats still 115kwh delivered in a 12 hour session. Likely plenty for most people.
I was referring to the new pro charger model that does bi-directional charging/backup. Most likely has some type of interlock.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,835
I was referring to the new pro charger model that does bi-directional charging/backup. Most likely has some type of interlock.
it has an ATS between the meter and the main panel. a totally separate unit that will need to be installed in conjunction with the pro charger. its unclear if its a specific unit ford and an ATS company have worked out OR if the pro charger will take a 2 wire input from any ol ATS
 

Syberia

Well-known member
Joined
Jan 13, 2014
Messages
1,451
Location
Perris, CA
The "standard," which I would expect to remain so, is a 14-50 outlet for either a 32 or 40 amp charger. Remember, though, that an electric vehicle is just find charging below its maximum rate, and for most people that don't deplete the battery daily, that is fine. My wife is one of those people who drives more than average, so we have a 32-amp EVSE for her, but I get by fine charging off of the 12-amp 240-volt EVSE that came with my Volt. Since it is a plug-in hybrid with a small battery, it fully charges in about 5-6 hours, and would be good for about 100 miles overnight in something with a larger battery. Plus the total load comes to 44 amps and doesn't overload our 60-amp subpanel.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,835
The "standard," which I would expect to remain so, is a 14-50 outlet for either a 32 or 40 amp charger. Remember, though, that an electric vehicle is just find charging below its maximum rate, and for most people that don't deplete the battery daily, that is fine. My wife is one of those people who drives more than average, so we have a 32-amp EVSE for her, but I get by fine charging off of the 12-amp 240-volt EVSE that came with my Volt. Since it is a plug-in hybrid with a small battery, it fully charges in about 5-6 hours, and would be good for about 100 miles overnight in something with a larger battery. Plus the total load comes to 44 amps and doesn't overload our 60-amp subpanel.

clippercreek makes a 2 cord - 32a j1772 charger that plugs into 1- 14-50 outlet. IMO that's a really solid solution for 2 car family. it handles all the sharing between the two. when one finishes it kicks the other up to full 32a.
 

tdkkart

Well-known member
Joined
Jun 17, 2006
Messages
6,887
Location
Eastern Iowa
Given the fact that installing a dedicated EV charging outlet in many homes could, and probably will, cost $1000 or more, it will be cost prohibitive for many potential buyers, and we haven't even begun to talk about apartment, trailer park, and condo dwellers. I suspect in the interest of gathering as much market share as possible, there will be a real push to get as much charging capability as possible out of a 20 amp outlet.
A lot of people can jump right into a 96 month loan or a 3-5year fleece, however many of them will be hesitant to buy vehicle that can't charge at home without spending large sums of money for the place to plug it in.

On a large scale, we're talking a HUGE infrastructure change if we expect even 20% of the population to be driving EVs. "Oh, you can charge at work". Ok, lets give my company credit for being on the leading edge of installing EV outlets in our parking lots. We have 10,000 employees here in town, I think we're up to EIGHT charging stations, most of which are currently empty when I see them. It's gonna be a hell of a long time before we have even 200 on site.
 

Syberia

Well-known member
Joined
Jan 13, 2014
Messages
1,451
Location
Perris, CA
clippercreek makes a 2 cord - 32a j1772 charger that plugs into 1- 14-50 outlet. IMO that's a really solid solution for 2 car family. it handles all the sharing between the two. when one finishes it kicks the other up to full 32a.
That would definitely have been an option had we both been planning on getting EVs when we installed the first charger.

EDIT: Ah, I see, $1,350. Since we have enough power available in the garage, I'd rather just go with the $500 one we bought and the free one that came with my Volt.

Sent from my moto g stylus using Tapatalk
 
Last edited:

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,835
That would definitely have been an option had we both been planning on getting EVs when we installed the first charger.

EDIT: Ah, I see, $1,350. Since we have enough power available in the garage, I'd rather just go with the $500 one we bought and the free one that came with my Volt.

Sent from my moto g stylus using Tapatalk

its basically 2 - 600 dollar units smashed together. if you're power limited at your house with a 100a service it is a pretty good option to get 2 cars charged without having to do a 200a service upgrade
 

Evilcactuar

Well-known member
Joined
May 31, 2013
Messages
94
Location
Connecticut
Man, this is alot of discussion on this. If I was worried about it and closing up the wall, I'd run conduit to a box so I could do it later and avoid snaking the wall. Super cheap and future proof. Who knows what charging will look like even 5 years from now.
 

jkeyser14

Well-known member
Joined
Dec 19, 2008
Messages
1,816
Location
(rural) Maryland
Man, this is alot of discussion on this. If I was worried about it and closing up the wall, I'd run conduit to a box so I could do it later and avoid snaking the wall. Super cheap and future proof. Who knows what charging will look like even 5 years from now.
It will look the same in 5 years. Houses are all different and have different electrical panels/capacities. Therefore chargers will continue to just work off whatever voltage/current you have available and your charge times will be a reflection of that.

Put in a NEMA 14-50 outlet and you'll be able to charge at around 30-40 miles of range per hour regardless of the car. And if the charger doesn't have a NEMA 14-50 plug you just pull the outlet and hard wire the charger where the outlet was.
 
OP
A

andyvh1959

Well-known member
Joined
Feb 15, 2020
Messages
2,590
Location
Green Bay WI
When I started this thread as the OP, I hardly thought it would go three pages worth. Lots of good discussion and ideas.

Two months ago, I had three extra spaces in my CH Load Center in the attached garage. Now that I added a duplex breaker to feed the sub-panel in my detached garage, and after I installed another single breaker after I found two circuits doubled into a single breaker (by a previous owner), my Load Center is full. So if I were to install NEMA 14-50 outlets for future charging needs I'd also have to replace the entire 70's vintage Load Center. That will have to wait, finances wise, and I'll likely sell the house before that happens.
 

tdkkart

Well-known member
Joined
Jun 17, 2006
Messages
6,887
Location
Eastern Iowa
So if I were to install NEMA 14-50 outlets for future charging needs I'd also have to replace the entire 70's vintage Load Center. That will have to wait, finances wise, and I'll likely sell the house before that happens.

Exactly the point of my post above. I would imagine to run the circuits to my garage to charge 2 vehicles it would probably cost close to $2000, maybe more if the breaker panel comes into play, and it's less than 20ft to the front center of my garage from the breaker panel, but it has to go above 2 finished ceilings in 2 different rooms, plus the garage ceiling.

"BTW, before you drive your car home, here's a $5000 estimate for wiring."
 
OP
A

andyvh1959

Well-known member
Joined
Feb 15, 2020
Messages
2,590
Location
Green Bay WI
Haven't read of too many people driving electric cars including the costs to install proper charging stations to their "cost to operate an electric vehicle", but I could see $2000 or more to get the right stuff installed. Sure, its a one time cost IF you pay it all up front. But it is a cost to operate an electric vehicle that must be included if you want to fast charge any vehicle at home.

In my Load Center I have four standard width 15 amp CH breakers. If I changed those four 15 amp standard breakers to the CH half width 15 amp tandem breakers I'd gain enough space in the panel to add another 50 amp duplex breaker to power a NEMA 14-10 charging outlet.

I have never used this style breaker, but considering it is an Eaton CH product I'd expect no problems using a tandem breaker versus a single breaker. Anyone else have concerns with tandem breakers?
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,835
because it varies from needing 10" of wire and an outlet to an entire service upgrade for thousands to get 240v-30+a . Also assuming you're driving the national avg of 14,000 miles a year you can simply charge on a 120 outlet.
 
OP
A

andyvh1959

Well-known member
Joined
Feb 15, 2020
Messages
2,590
Location
Green Bay WI
Y'know, one aspect of EV versus internal combustion engines with little discussion is what do you do when the "fuel" runs out due to not watching the fuel gauge. In the good old days, you walked a distance to buy a gallon or two of gas, poured it in and once the car starts you drive to a close by gas station and fill up. Maybe call a friend or family member to bring you some fuel. Sure you suffer some embarrassment, loose a few hours time, but you're back on the road and rolling.

With an EV, if you run out of juice on the road, IF you can get a tow truck to a local super-charge station, IF the super-charge station is available, you're going to be there for a number of hours before you gather just enough charge to get to another super-charge station, or to home. Then you are car stranded until the EV is fully charged again. Unless, that is the aspect of fast change out battery stations becomes the EV equivalent of a gas station:
https://www.caranddriver.com/news/a35717014/ample-battery-swapping-station/

But to us gas station enthusiasts, an EV battery change out station has none of the allure of the traditional gas stations. Doubt there will ever be the modern equivalent Super-charger "pump" like the classic Tokheim, Wayne, Bowser, Bennet vintage gas pumps.
 

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
Anyone else have concerns with tandem breakers?
As long as tandems fit and are listed for your panel you should be good. Not all panels take tandems and for those that do, not all spaces will take them. Look at the sticker on your panel. Note that there are non-CTL tandems that might fit but are not listed/approved. Also with CH panels sometimes older panels won't take newer breakers.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,835
Y'know, one aspect of EV versus internal combustion engines with little discussion is what do you do when the "fuel" runs out due to not watching the fuel gauge. In the good old days, you walked a distance to buy a gallon or two of gas, poured it in and once the car starts you drive to a close by gas station and fill up. Maybe call a friend or family member to bring you some fuel. Sure you suffer some embarrassment, loose a few hours time, but you're back on the road and rolling.

With an EV, if you run out of juice on the road, IF you can get a tow truck to a local super-charge station, IF the super-charge station is available, you're going to be there for a number of hours before you gather just enough charge to get to another super-charge station, or to home. Then you are car stranded until the EV is fully charged again. Unless, that is the aspect of fast change out battery stations becomes the EV equivalent of a gas station:
https://www.caranddriver.com/news/a35717014/ample-battery-swapping-station/

But to us gas station enthusiasts, an EV battery change out station has none of the allure of the traditional gas stations. Doubt there will ever be the modern equivalent Super-charger "pump" like the classic Tokheim, Wayne, Bowser, Bennet vintage gas pumps.

you assume the tech never arrives to have portable DC to DC charge solutions. but ill talk about current situation: yes you need a tow. no it doesnt take hours at the super charger to get filled up. you're not stranded until its fully charged. i hardly ever charge past 60% at super chargers.

also the car is screaming at you LONG ahead of time that you're outside charger range. tells you to slow down to make it. etc.
 
To avoid these ads, REGISTER NOW!

ericm

Well-known member
Joined
Apr 17, 2016
Messages
1,963
Location
Southern Oregon
Y'know, one aspect of EV versus internal combustion engines with little discussion is what do you do when the "fuel" runs out due to not watching the fuel gauge. In the good old days, you walked a distance to buy a gallon or two of gas, poured it in and once the car starts you drive to a close by gas station and fill up. Maybe call a friend or family member to bring you some fuel. Sure you suffer some embarrassment, loose a few hours time, but you're back on the road and rolling.

The last (and first) time I accidentally ran a vehicle's fuel tank empty was in 1976. I don't see it being an issue.

I think I'll plan my new garage/shop to have capacity for a charger. While I'm not a fan of electric cars now (though unlike some I'm fine with other people using them), that may change.
 

PFSard

Well-known member
Joined
Sep 12, 2013
Messages
2,423
Location
Mesa, AZ
I was watching This Old House last night and they were talking about the next thing in home charging may be non-contact inductive charging, from a pad built into the floor. It's anyone's guess when and if that will become common, but it's an example of how the charging and installation requirements may change in the future.

They also touched on being able to use an EV to provide power to the house in the event of an outage. Of course it wouldn't be practical for a long term outage, and also not for running large inductive loads like air conditioning, but for short term (like a few hours, which is what most people probably face) being able to run a few lights , a gas furnace, and the fridge it would be useful.
I watched this also. Found the video posted on YouTube today :

What's New with EV Chargers | Ask This Old House
Jun 2, 2021
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,835
I watched this also. Found the video posted on YouTube today :

What's New with EV Chargers | Ask This Old House
Jun 2, 2021

if they're putting in dedicated 120-20a into each bay by code thats pretty good news. you can swap it out for a 240v-20a. thats 3.8kw of charging. that actually makes me really happy to see.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,638
Location
Austin, TX
They also touched on being able to use an EV to provide power to the house in the event of an outage. Of course it wouldn't be practical for a long term outage, and also not for running large inductive loads like air conditioning, but for short term (like a few hours, which is what most people probably face) being able to run a few lights , a gas furnace, and the fridge it would be useful.

Definitely an interesting option. Word is around here in the "great freeze" that a few Ford dealers dispatched the new electric F-150 for power generation. I haven't looked at how that connection would work and dunno if they actually were powering up breaker panels, but it's kinda a cool option.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,583
Location
BC
As an electrician, I'm unable to decide what to stick in my my own garage walls before I close them up. So I just close them up and run any electrical afterwards, as I come to need it.

If you are set on burying a large future circuit in the wall.... Maybe just run a 3/4 or 1" conduit into a box, and leave it empty until you get that hungry piece of equipment, or at least know it's actual electrical specs.
 
Last edited:

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,918
Location
Coronado, CA
Just as Photo Voltaic (Solar Electric) wiring is now being mandated in some states as a requirement during new construction; pre-wiring for ca chargers is certainly soon to follow.

If you have the walls open; future proof your project, for example; prepping for A/C by running a Line Set during construction is much cheaper to install than doing it later.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,835
Just as Photo Voltaic (Solar Electric) wiring is now being mandated in some states as a requirement during new construction; pre-wiring for ca chargers is certainly soon to follow.

If you have the walls open; future proof your project, for example; prepping for A/C by running a Line Set during construction is much cheaper to install than doing it later.

I thought NEC was gona require new construction to have a 20a per spot in garages for EV.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,835
One county in MD that I was building new homes in that had adopted 2015(?) NEC requires us to provide this.

home runs right? so you can swap it out for a 240-20a. 3.8kw charging is a decent amount. plenty for most commutes
 

Yankeefarmer

Well-known member
Joined
Jul 25, 2011
Messages
1,171
Location
Connecticut
home runs right? so you can swap it out for a 240-20a. 3.8kw charging is a decent amount. plenty for most commutes
I don’t see anything explicit in the code supporting this. It does not require an individual circuit for each bay, just that at least one receptacle outlet per bay be provided on a 20 amp circuit with no other receptacles. It then allows an exception “This circuit shall be permitted to supply readily accessible outdoor receptacle outlets.” That would seem to preclude provision for future upgrading to 240v.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,835
I don’t see anything explicit in the code supporting this. It does not require an individual circuit for each bay, just that at least one receptacle outlet per bay be provided on a 20 amp circuit with no other receptacles. It then allows an exception “This circuit shall be permitted to supply readily accessible outdoor receptacle outlets.” That would seem to preclude provision for future upgrading to 240v.

so the charging circuit could also be the exterior GFCI's. hummm. well its better than nothing 20a of 120 still covers the majority of commutes.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,638
Location
Austin, TX
My experience with modern AFI/GFI (combo) breakers has been craptastic. They don't seem to like anything that hits with a hard start-up load - dunno if most EV chargers have a ramp or not...
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,071
Location
Northern Virginia
home runs right? so you can swap it out for a 240-20a. 3.8kw charging is a decent amount. plenty for most commutes

I don’t see anything explicit in the code supporting this. It does not require an individual circuit for each bay, just that at least one receptacle outlet per bay be provided on a 20 amp circuit with no other receptacles. It then allows an exception “This circuit shall be permitted to supply readily accessible outdoor receptacle outlets.” That would seem to preclude provision for future upgrading to 240vThese are not dedicated outlets. These extra outlets one per bay are all common with the garage door motor(s) above and how knows what else. A single GFI in the garage trips them all.
No the outlets one per bay were not dedicated 20a’s. They were ganged together and included the garage door openers.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,835
My experience with modern AFI/GFI (combo) breakers has been craptastic. They don't seem to like anything that hits with a hard start-up load - dunno if most EV chargers have a ramp or not...

mine ramps up.
 
To avoid these ads, REGISTER NOW!
Top Bottom