Hello,
I'm in the planning stages for a 30x40 pole barn and was hoping to get some feedback on my electrical plans.
This building will be used for storage, some light vehicle maintenance, woodworking projects, etc. My initial usage will be general lighting and small power tools. No high draw compressors, welders, fabrication equipment, etc.
The two biggest loads I can foresee are a Level 2 EV charger (48/60 amps) and a mini split to heat/cool a small 150 sq ft office space (18 amps @ 120v). I'm sure a 60 amp sub panel would be more than sufficient for my initial use, but thinking 100 amp may be the best long term option given the EV charger.
My 5 year old house has a 200 amp Siemens PN Series main panel. The wire run from the main panel in the basement of the house to the sub panel in the new barn is 275 feet (possibly as little as 265’ depending on final location of the barn sub panel, this includes vertical rise).
Here are my thoughts, please critique:
Low voltage
Finally, one last question:
I currently have a manual generator interlock kit installed on my main house panel. Is there any way I could connect the generator to the pole barn sub panel, and then back feed the house through the sub panel in the barn? When the power is out, it would be nice to move the running generator further away from the house. I cannot see a way this is possible, without running separate feeders from the main panel out to the generator inlet plug, but figured it wouldn’t hurt to ask.
I'm in the planning stages for a 30x40 pole barn and was hoping to get some feedback on my electrical plans.
This building will be used for storage, some light vehicle maintenance, woodworking projects, etc. My initial usage will be general lighting and small power tools. No high draw compressors, welders, fabrication equipment, etc.
The two biggest loads I can foresee are a Level 2 EV charger (48/60 amps) and a mini split to heat/cool a small 150 sq ft office space (18 amps @ 120v). I'm sure a 60 amp sub panel would be more than sufficient for my initial use, but thinking 100 amp may be the best long term option given the EV charger.
My 5 year old house has a 200 amp Siemens PN Series main panel. The wire run from the main panel in the basement of the house to the sub panel in the new barn is 275 feet (possibly as little as 265’ depending on final location of the barn sub panel, this includes vertical rise).
Here are my thoughts, please critique:
- For the 100 Amp Sub panel in barn
- Install 100 amp breaker in main panel that will feed sub panel. Locate this 100 amp breaker as close as possible to main breaker at the top of the panel. May need to shift some breakers to make room.
- In the barn, install Siemens PN Series 100 Amp, 20-Space, 20-Circuit main breaker panel. Keeping with the same Siemens PN series panel because why not match the main house panel.
- Feed the sub panel with three Aluminum 1/0 XHHW (2 black hot, 1 white neutral) and one Aluminum #4 XHHW (green ground).
- At 100 amps, calculated voltage drop is 4.77%
- At 60 amps, calculated voltage drop is 2.86%
- Use 1-½” schedule 40 PVC Conduit buried with minimum 18” cover. My soil is mostly sand, but I do contend with some rocks. Cover halfway, install buried electrical tape marker, then complete the remainder of the backfill.
- With 1-½” conduit, the fill percentage is 27.66% with my proposed feed wire.
- May need to transition to schedule 80 at side of house if the vertical conduit is exposed at the house.
- Use conduit expansion coupling at transition from horizontal to vertical run.
- I am seeing that 2” PVC may actually be cheaper (or very similar in price) to 1-½” PVC. If that is the case, I may just use 2”.
- Do NOT bond neutral and ground in sub panel
- Install Two ground rods with continuous wire at sub panel location.
Low voltage
- Install 1” PVC Conduit for data. I have no idea what this looks like yet. Still need to learn more about cable options for this long of an underground run. But I would like to have WiFi in the barn.
Finally, one last question:
I currently have a manual generator interlock kit installed on my main house panel. Is there any way I could connect the generator to the pole barn sub panel, and then back feed the house through the sub panel in the barn? When the power is out, it would be nice to move the running generator further away from the house. I cannot see a way this is possible, without running separate feeders from the main panel out to the generator inlet plug, but figured it wouldn’t hurt to ask.