It's been a while since I posted here due to a string of events that diverted focus from my hobbies to the real world (military retirement, job hunting, job finding and moving).
Now that I've landed, I am building my shop back up in the attached 2 car garage and need to wire up my Hobart 210 welder and CH 60gal compressor.
Situation: There is an HVAC unit in a closet in the attached garage which is fed thru a disconnect (also in the closet) by a 4AWG Cu THHN SE (2 conductors and ground) cable from a 60A breaker in the Square D QO main panel .
Plan: Replace 60A breaker in the main panel with a QO 90A breaker and replace the disconnect with a sub panel in the closet to hold 220v breakers for the welder (30A), compressor (20A breaker (15A draw stated on motor sticker)) and HVAC (60A max over current device required as per the information sticker on the unit). I will use 10AWG wire for the compressor and welder circuits. I know 10ga is overkill for the compressor, but it is a short run and I have 100 ft of it.
Questions: 1. My understanding is that since the sub panel is exclusively feeding 220V loads, it is within code to use 2 conductor cable (separate neutral and ground not required) to supply the sub panel, am I correct?
2. Am I within code to install a 90A breaker in the main panel and supply the sub panel through 4AWG Cu wire since the stated ampacity of the cable is 85A and I can up amp the breaker?
3. Is 90A sufficient to supply power to the combination of the HVAC, compressor and welder, or am I at risk of overloading the feeder and tripping the 90A breaker in the main panel?
Thank you in advance for your advice.
Cheers,
Stump
Now that I've landed, I am building my shop back up in the attached 2 car garage and need to wire up my Hobart 210 welder and CH 60gal compressor.
Situation: There is an HVAC unit in a closet in the attached garage which is fed thru a disconnect (also in the closet) by a 4AWG Cu THHN SE (2 conductors and ground) cable from a 60A breaker in the Square D QO main panel .
Plan: Replace 60A breaker in the main panel with a QO 90A breaker and replace the disconnect with a sub panel in the closet to hold 220v breakers for the welder (30A), compressor (20A breaker (15A draw stated on motor sticker)) and HVAC (60A max over current device required as per the information sticker on the unit). I will use 10AWG wire for the compressor and welder circuits. I know 10ga is overkill for the compressor, but it is a short run and I have 100 ft of it.
Questions: 1. My understanding is that since the sub panel is exclusively feeding 220V loads, it is within code to use 2 conductor cable (separate neutral and ground not required) to supply the sub panel, am I correct?
2. Am I within code to install a 90A breaker in the main panel and supply the sub panel through 4AWG Cu wire since the stated ampacity of the cable is 85A and I can up amp the breaker?
3. Is 90A sufficient to supply power to the combination of the HVAC, compressor and welder, or am I at risk of overloading the feeder and tripping the 90A breaker in the main panel?
Thank you in advance for your advice.
Cheers,
Stump