Plugs for lighting?

Train

Well-known member
Joined
Jul 20, 2010
Messages
249
Location
Alberta, Canada
I was given several warehouse type light fixtures, metal halide. They come with hangers so they don't attach to a box like a domestic light. My question is, would it be okay to put a plug on the wire, like my ceiling fans have. These will be going in the shop and about 15 feet in the air, so no chance of them getting pulled out of the socket by accident.

They're 120 v, 2.6 amp.
 
To avoid these ads, REGISTER NOW!

ezover

Well-known member
Joined
Jan 15, 2008
Messages
2,412
Location
3rd rock from the sun
that is how i did mine on a 10' ceiling. not sure why but i just did not want them hard wired. now i have lots of out lets on my ceiling too :)
 
To avoid these ads, REGISTER NOW!

AndyCBR

Well-known member
Joined
Jun 22, 2014
Messages
396
Location
Baton Rouge, LA
I was given several warehouse type light fixtures, metal halide. They come with hangers so they don't attach to a box like a domestic light. My question is, would it be okay to put a plug on the wire, like my ceiling fans have. These will be going in the shop and about 15 feet in the air, so no chance of them getting pulled out of the socket by accident.

They're 120 v, 2.6 amp.

As long as the receptacle is rated for the application it is no problem. If it was some kind of wet location or pressure washing bay then you might have an issue.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
250 watt. Gonna have to put then pretty close together.

Normally the MH fixtures have a hook on the fixture, and a cast box with a ring on it and a receptacle set at a 45° angle on the side of it with a twist lock® receptacle which prevents the plug from falling out from building vibration.

I used regular receptacles but they were commercial/industrial grade and very tight to plug and unplug from. I used large steel machine screw eyes set into cone nuts in the unistrut.

Note that 410.62 (C)(1)(1) requires that the fixture be hung "directly" below the box/receptacle/busway and thus generally be mounted on the same structure as the light is hung from.

attachment.php


attachment.php
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
If cord & plug connected they MAY require GFCI protection.
 