goneflyin2002
Well-known member
I'm setting up the plumbing for my new boiler- it's a Viessmann 100W-26 mod/con unit, connecting to my radiant floor.
Some specs:
floor- 2000 sq', 1/2" pex tubing 2100', spaced 12" in the grid
manifolds- simple copper 1" , with 9 branches
circulator pump- Grundfos UPS 26 3 speed
I've done heat loss calcs, and the results range from 37K to 50Kbtu's.
The question that I'm having a hard time finding an answer to is, can I just plumb this circuit directly or does it have to have a 'low loss header'/closely spaced tees?
Flow rate calcs show 2.7gph, head loss 4.7 and water temp 108*.
Many thanks!
Don