POCO disconnect at Transformer ?

rocky1

Active member
Joined
Jul 25, 2011
Messages
42
The general method it to pull the meter, but could they not also pull the fuse on the incoming line at the transformer ? Seems like this would de-energize the entire meter socket and thus be safer.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
The general method it to pull the meter, but could they not also pull the fuse on the incoming line at the transformer ? Seems like this would de-energize the entire meter socket and thus be safer.

Not going to work when said transformer serves more then one customer, plus it's not the way the PoCo's do things.
 

DC73

Well-known member
Joined
Dec 27, 2014
Messages
1,627
Location
Lubbock TX
The general method it to pull the meter, but could they not also pull the fuse on the incoming line at the transformer ? Seems like this would de-energize the entire meter socket and thus be safer.

They could. But it's cheaper to boot the meter. They can send a field tech in a pickup. Much lower hourly rate than a journeyman serviceman with a bucket truck or extend-o-stick. Field techs generally aren't qualified to pull transformer fuses. PoCos do pull the fuses or cut the wire at the pole when morons bypass the meter after being disconnected for non-pay.

Booting the meter means to install rubber boots on the terminals to insulate the meter and prevent power from flowing. They leave the meter installed with the boots and send a field tech back out to remove them when the order comes through.

DC
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
If you're the only customer on the transformer, they will usually pull the cutouts/bayonets depending on if it's pots on the pole or a padmount. If more than one customer is on the transformer, they may just cut your wires loose from the service or unlug your wires at the padmount while keeping the other homes connected.
 
OP
R

rocky1

Active member
Joined
Jul 25, 2011
Messages
42
Just wondering because two leads in the meter base would still be hot with the meter out. Hypothetically, was moving eq grounds in the panel and one got too close to the incoming feeds. Was the original electrician sloppy or do you suppose they backed out of the breaker ?



100_3325_zpsnioq8za7.jpg
 
Last edited:
OP
R

rocky1

Active member
Joined
Jul 25, 2011
Messages
42
I want to thank everyone for their help. I have an estimate to replace panel with an Eaton ch and two ground rods. Awaiting word as to if the company will install new GE panel so I can reuse breakers. Would y'all elect to spend the additional 300 or so and just go Eaton with new breakers over a GE panel ?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,004
Location
Modesto, CA
Do u have a separate meter pan?

U could just remove one hot leg at a time and tape it...

If those were loose enough to back out that much u would see evidence of excessive heat, arcing, melting and blackness!
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
R

rocky1

Active member
Joined
Jul 25, 2011
Messages
42
Think I coud get away with using compressed air to blow the debris off them ?
 
OP
R

rocky1

Active member
Joined
Jul 25, 2011
Messages
42
I don't have a good answer. The only advantages of a new panel would be to shorten the unfused length of the service entrance wire, gain more physical space inside the box for ease of working in it, gain slack in the incoming wiring by going to a taller box, and maybe change the 1/2 space breakers to full space breakers. It started out that I was out of neutral lugs. I have corrected that. The electrician that came out bid installation of two new ground bars. The meter which was on the outside wall is now part of an add on garage. Power company seems ok with it.

Many people here suggested that if it was an older GE panel, they would change it outright. Don't know if they know something about it that I don't.
Thanks for the reply
 
OP
R

rocky1

Active member
Joined
Jul 25, 2011
Messages
42
I guess the only real reason is to shorten the entrance cable inside the box or top feed the existing box if possible
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,004
Location
Modesto, CA
Ick! It looks like those conductors are nicked pretty bad from stripping the insulation. I would cut them and restrip...carefully!
 