New pole barn, approx. 200 ft run from house panel. I have 320A service to the house. Would like 100A to the barn. Will be doing the grunt work myself, uncle is retired electrician and will help. Work will be permitted and inspected.
Wire sizing calculator says 1/0 Al required. Was thinking I'd get 800 ft of XHHW, and run it from a new 100A breaker in the house panel, through buried PVC conduit to a 100A panel in the barn.
I have Cutler Hammer CH panels and can get a 100A breaker for the feeder that will accept 1/0 wire. Plan to get a 100A CH main panel for the barn.
My tight spot is I made the mistake of stubbing out a 1 1/2" conduit from the house when I built it, should have gone 2". It's under a sidewalk now, so I'd prefer not mess with that. Conduit fill charts say max of 4 1/0 conductors in 1 1/2" PVC, but I will switch to 2" for the new portion of the conduit run.
Does this general plan look reasonable and NEC compliant?
Wire sizing calculator says 1/0 Al required. Was thinking I'd get 800 ft of XHHW, and run it from a new 100A breaker in the house panel, through buried PVC conduit to a 100A panel in the barn.
I have Cutler Hammer CH panels and can get a 100A breaker for the feeder that will accept 1/0 wire. Plan to get a 100A CH main panel for the barn.
My tight spot is I made the mistake of stubbing out a 1 1/2" conduit from the house when I built it, should have gone 2". It's under a sidewalk now, so I'd prefer not mess with that. Conduit fill charts say max of 4 1/0 conductors in 1 1/2" PVC, but I will switch to 2" for the new portion of the conduit run.