Pole barn posts

bryank1

New member
Joined
Jan 22, 2017
Messages
2
I’d like the get some opinions on this. I am having a barn built and this is what the posts look like. The truss will be supported by the center 2x6 but I have a really hard time believing this is ok. Any barn builders that could give me their input I’d appreciate it.
 

Attachments

  • 1EA5AFC4-C17F-4B60-9A4E-CFF0A9A09ACA.jpg
    1EA5AFC4-C17F-4B60-9A4E-CFF0A9A09ACA.jpg
    82.2 KB · Views: 357
  • ADB3C640-2080-440E-AE8B-91428E06A33D.jpg
    ADB3C640-2080-440E-AE8B-91428E06A33D.jpg
    79.5 KB · Views: 365
To avoid these ads, REGISTER NOW!

mrobins297aaa

Well-known member
Joined
Sep 20, 2010
Messages
3,283
Location
south east michigan
welcome to the forum, I think it looks kind of cobbie to me to.
First thing I would check is the type of treatment those post have for the section below grade.......it should be at least UC4B or CCA-C60. Make sure there rated for ground contact and structural.

also any of those nails into that treated wood should be galvanized or stainless

how big is the barn w x l x h

There are a lot of knowledgeable people on this board especially about barns hopefully some will chime in
 

Attachments

  • barn 6x6 post sticker.jpg
    barn 6x6 post sticker.jpg
    96 KB · Views: 138
Last edited:

bobbyjean

Well-known member
Joined
Aug 25, 2017
Messages
319
Location
hudson valley n.y.
is the builder insured?...do you have stamped drawings? if not ................stop now and get them...that looks wrong...don't know height of your barn....but how bout a rated 4x6 or better 6x6 that sits on some type of footing.
looks like some big barns behind the new one in picture....same builder?
 

dave_dj1

Well-known member
Joined
Feb 3, 2018
Messages
222
Location
Jackson, NY
That looks like how Morton does theirs. I would think a little more pride in whoever is doing it work would be in order but laminated in and of itself is fine. It's actually proven to be stronger partly because of the different grains of each piece versus one 6x6 with the same grain.
 

rburke65

Well-known member
Joined
Nov 10, 2007
Messages
12,349
Location
Canfield, Ohio
The 3 treated and staggered 2x6s, to the untreated 2x6s is nothing new and is supposedly better than a solid 6x6. BUT....I’m not liking the gap between the 2 end butts. I’d have then redo that.
 

95vette

Banned
Joined
Jul 24, 2011
Messages
119
Hello, Stop him now before he ruins the rest of your barn, that is ridiculous!!!
 
OP
B

bryank1

New member
Joined
Jan 22, 2017
Messages
2
The barn is a 40x60 14 ft walls, the guys that is building it works for a large barn builder and is the same guy that built the 120x60 in the back ground. At the time the large barn was built
he had his own company but now he works for a VERY LARGE barn builder. He is building it on the weekends with guys that work for him at that large company. I have absolutly no issues with the other barn he put up 8 years ago and was very suprised to see this. I guess my question would be, does that gap in a bunch of the posts pose a structural problem or not? I plan on talking with him tomorrow about this but expect him to say this won't be a problem. thanks for the input!
 

dave_dj1

Well-known member
Joined
Feb 3, 2018
Messages
222
Location
Jackson, NY
The barn is a 40x60 14 ft walls, the guys that is building it works for a large barn builder and is the same guy that built the 120x60 in the back ground. At the time the large barn was built
he had his own company but now he works for a VERY LARGE barn builder. He is building it on the weekends with guys that work for him at that large company. I have absolutly no issues with the other barn he put up 8 years ago and was very suprised to see this. I guess my question would be, does that gap in a bunch of the posts pose a structural problem or not? I plan on talking with him tomorrow about this but expect him to say this won't be a problem. thanks for the input!

I don't see the gap as being a structural issue (provided it is fastened properly). You (he) could always rip some shims and put them in the gaps. Worst case scenario you could have him add another layer to span the gap say from ground level to about 18"-24" above the gap. You could even suggest this to him.
 
To avoid these ads, REGISTER NOW!

johnehr

Well-known member
Joined
Nov 24, 2013
Messages
103
Location
Oak Grove, Minnesota
The builder of my pole building used laminated posts, but finger-joints at the interface of the treated and untreated sections. I think that it is a better approach. 14’ side walls here as well.

IMG_2309.jpg


Sent from my iPhone using Tapatalk
 

Homerr

Well-known member
Joined
Mar 16, 2012
Messages
379
Location
Seattle, WA
Other than the unsightly gap (which likely isn't a structural issue), what's ridiculous about this?

2/3 of a post is a structural issue...

14' high walls are a bit of a big deal and I imagine the wind loading on this building will likely be controlling. Throwing this in Strucalc with an assumption of 8' and 6' o.c. trusses and 15# dead/#25# live load this column fails by 53% and 15%, respectively as (3)2x6 #1 SPF.

I would ask the builder to see the plans and engineering if you don't already have a set. Verify he isn't field substituting (3)2x6 for a 6x6.

In contrast, a #1 SPF 6x6 works at 8' (by 14%) and 6' (by 52%) o.c.

This stuff matters and it's how buildings fall down.

Edit: 14' wood columns get to be a bit of a deal not only because of the vertical gravity load on them but also they will tend to bow out of vertical in the middle under stress. You can't just increase the length of a post with the same downward load and have the same result. It's like pushing down on a standard length straw with your finger compared to one of the long straws for tall cups. Using the same pressure the tall one will fail first.
 

Attachments

  • Capture.JPG
    Capture.JPG
    45.7 KB · Views: 48
Last edited:

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,893
Location
oregon
2/3 of a post is a structural issue...

14' high walls are a bit of a big deal and I imagine the wind loading on this building will likely be controlling. Throwing this in Strucalc with an assumption of 8' and 6' o.c. trusses and 15# dead/#25# live load this column fails by 53% and 15%, respectively as (3)2x6 #1 SPF.

I would ask the builder to see the plans and engineering if you don't already have a set. Verify he isn't field substituting (3)2x6 for a 6x6.

In contrast, a #1 SPF 6x6 works at 8' (by 14%) and 6' (by 52%) o.c.

This stuff matters and it's how buildings fall down.

There are lots of building out there with these 3 ply posts. In your calcs above did you just compare the 3 ply to a 6x6 or did you compare a 3 ply with tight **** joints to one with a gap that is shown in the OP?

In my opinion, not backed up by any engineering degree, the tight **** joint would only come into play if the post was hit from the side so that the bending force would close the joint. If the bending force were from any other side it would not matter. It would matter in compression some.

lg
no neat sig line
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
IMO the pre-made laminated posts are a much superior product. Around here they use stainless steel wire to tie the 3 plies together and steel splice plates as well.

https://www.midwestmanufacturing.com/MidwestWebsite/web/cms/docs/LamCol903-0101.pdf

I definitely wouldn't settle with what you have. Not only is the gap a stupid show of poor craftsmanship, it results in a much weaker post. You only show a small portion but I am guessing the nailing schedule is insufficient as well... I'd expect to see another row or two in your photo.
 

Homerr

Well-known member
Joined
Mar 16, 2012
Messages
379
Location
Seattle, WA
There are lots of building out there with these 3 ply posts. In your calcs above did you just compare the 3 ply to a 6x6 or did you compare a 3 ply with tight **** joints to one with a gap that is shown in the OP?

In my opinion, not backed up by any engineering degree, the tight **** joint would only come into play if the post was hit from the side so that the bending force would close the joint. If the bending force were from any other side it would not matter. It would matter in compression some.

lg
no neat sig line

Hi larry_g, the number of buildings out there with three ply posts isn't really a factor in this - it's the specifics of this structural situation that really matter.

I ran calcs for (3)2x6 (nail laminated) and a 6x6 post. I figured the trusses were spanning 40' so a tributary area of either 20'x8' or 20'x6' in the examples. I don't see the gap as being structurally sound, I think 1/8" max. would account for some compression of the dead loading of the building for the vertical loading. But the 1/4"-3/8" looking gap, to me, is beyond what should be there. There is a lot of extra force on the laminating nails and 2 other studs as pictured.

The 'bowing' factor, as described by the straw example, is really the larger issue. To close that joint means the opposite outer stud is probably broken at that point, but really the whole point is to not have the posts be in a situation where they would flex that much. With the size gap shown and running the column effectively as (2)2x6x14' - well my program won't even allow it because it exceeds the required slenderness ratio.

The size of the wall surface is like a giant sail. I don't do lateral engineering, but from what I have picked up over the years from engineers think of a single one of these posts like this: those (3)2x6, (2)2x6, or 6x6 are cantilevering out of the ground with a 6,400 lb Ford F350 on the top and it also has a sail tied top to bottom at 1' increments to distribute the load; the wind blows and the sail generates a total of ~1,680 lbs total over the 14' sticking out of the ground, and the sail can pivot to either the X or Y axis. Will these posts take that load? Well, the calc says only the 6x6 can.

That isn't technically a totally fair example because a building acts as a system and sheathing will counter the wind shear, but it's just meant to illustrate the magnitude of the forces in play here.

My concern really is that there may not even be a plan or calc done for these columns. If the OP's project is done by someone on the side, on the cheap, and/or in a rush and they are just relying on what they did in the past. But maybe the 'past' was a 36' span and a 12' height but the contractor figures it will work at 40'/14' - but it really doesn't. And it might not fall down right away, but structural design is meant for worst-case for 10 or 40 years years from now when a big storm or earthquake rolls through.
 

dave_dj1

Well-known member
Joined
Feb 3, 2018
Messages
222
Location
Jackson, NY
Hi larry_g, the number of buildings out there with three ply posts isn't really a factor in this - it's the specifics of this structural situation that really matter.

I ran calcs for (3)2x6 (nail laminated) and a 6x6 post. I figured the trusses were spanning 40' so a tributary area of either 20'x8' or 20'x6' in the examples. I don't see the gap as being structurally sound, I think 1/8" max. would account for some compression of the dead loading of the building for the vertical loading. But the 1/4"-3/8" looking gap, to me, is beyond what should be there. There is a lot of extra force on the laminating nails and 2 other studs as pictured.

The 'bowing' factor, as described by the straw example, is really the larger issue. To close that joint means the opposite outer stud is probably broken at that point, but really the whole point is to not have the posts be in a situation where they would flex that much. With the size gap shown and running the column effectively as (2)2x6x14' - well my program won't even allow it because it exceeds the required slenderness ratio.

The size of the wall surface is like a giant sail. I don't do lateral engineering, but from what I have picked up over the years from engineers think of a single one of these posts like this: those (3)2x6, (2)2x6, or 6x6 are cantilevering out of the ground with a 6,400 lb Ford F350 on the top and it also has a sail tied top to bottom at 1' increments to distribute the load; the wind blows and the sail generates a total of ~1,680 lbs total over the 14' sticking out of the ground, and the sail can pivot to either the X or Y axis. Will these posts take that load? Well, the calc says only the 6x6 can.

That isn't technically a totally fair example because a building acts as a system and sheathing will counter the wind shear, but it's just meant to illustrate the magnitude of the forces in play here.

My concern really is that there may not even be a plan or calc done for these columns. If the OP's project is done by someone on the side, on the cheap, and/or in a rush and they are just relying on what they did in the past. But maybe the 'past' was a 36' span and a 12' height but the contractor figures it will work at 40'/14' - but it really doesn't. And it might not fall down right away, but structural design is meant for worst-case for 10 or 40 years years from now when a big storm or earthquake rolls through.

I'm not disputing your findings but did you forget the fact that there will be pulins on the outside every 24-32" and then solid metal over that? Just wondering how it will all tie together. I'm no engineer nor do I play one on tv and no, I didn't stay at a Holiday Inn last night :) Some buildings even have diagonal braces from the truss to the post.
 

Homerr

Well-known member
Joined
Mar 16, 2012
Messages
379
Location
Seattle, WA
Ishiboo, those columns look like the right tool for the job.


I'm not disputing your findings but did you forget the fact that there will be pulins on the outside every 24-32" and then solid metal over that? Just wondering how it will all tie together. I'm no engineer nor do I play one on tv and no, I didn't stay at a Holiday Inn last night :) Some buildings even have diagonal braces from the truss to the post.

The horizontal purlins are just a means to hang siding, they have little to no structural value. Doesn't matter about metal or wood siding on those purlins. To really get a wall to perform as a shear wall the structurally sheathed wall would need to sit on and be tied to a continuous concrete stem wall or thickened turned down slab edge, which is usually what pole barn buildings are avoiding (meaning non-concrete floor and/or also building sequence of installing posts before floor/slab).

The structural value in shear will come from one of two methods generally, 1) diagonal bracing, probably large X bracing that fills the entire bay between posts, or 2) the posts are adequate cantilevering out of the ground as a sort of lightweight portal/moment frame.

There are exceptions to the above, I'm just trying to speak in general terms that cover the majority of these buildings.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,243
Location
SE MI
The 3 treated and staggered 2x6s, to the untreated 2x6s is nothing new and is supposedly better than a solid 6x6. BUT....I’m not liking the gap between the 2 end butts. I’d have then redo that.
I can not believe any inspector would approve that post with the gap in it !

I also can not believe they would NOT use PT on all layers of a post that contacts the ground. Guaranteed to rot early.
 

3rdgendslmech

Well-known member
Joined
Mar 12, 2017
Messages
499
Location
Maryland
That's how mind came but they were better looking than that. The bottoms are 3 pressure treated 2x6s cut at different lengths and spliced with a special blade.
Other than the splice joint you could probably make your own but that gap though........
 