If I'm going to use PVC conduit, would I want THHN stranded or solid? and would it need to be THHN-2?
Sent from my XT1060 using Tapatalk
now Free
Stranded is somewhat easier to pull in conduit, however, it is much more difficult to terminate to receptacles and switches.
You will almost have to buy backwire type receptacles (NOT the push in type, but the spec/commercial/industrial type) so that you can put the wire in the back of the receptacle and tighten the screw and it is pinched/clamped in place by a plate, usually serrated that grips the wire tight. We recently had a discussion about this, wrapping stranded wire around screws, and while some of the pros acted like its not a problem to do it..... it simply is more trouble and the odds of you having to try, more than once to get it right, are great.
I won't use a receptacle or switch that is not backwire type.
That being said, I much prefer solid THHN and it is not that difficult to pull. I have pulled quite a few feet of it thru EMT (metallic conduit) in my building (without any help) and it was not that difficult. Either make, or buy a rack that you can mount the 500 ft spools of THHN on and if you make it, put a large enough base on it that you can weight it down some, and pull away. Sometimes I had to fabricate a "funnel" to shove up in the box at the conduit end to help smoothly feed the wire, and I'd pull a few feet, lube up some more and pull it and lube some more.
Not sure what pulling thru PVC is like, I only use it for outdoors, underground, or very unusual installations. I used EMT for everything inside the building.
Rec on left is cheapie push in type, rec on right is much better screw and clamp type, usually marked spec, commercial, or industrial.
Charles