possible 4 ton install questions

homebuilt burner

Well-known member
Joined
Dec 8, 2014
Messages
1,763
Location
central Wisconsin
I have been given free of charge a Lennox 10ACB48-5P condensing unit and A-coil. Yes, I know this is an older unit and yes I know it is not very efficient. It is however the correct size for my home according to the heating and cooling calculations I have researched on the internet. Did I mention free and worked when remove from a building that was torn down??

I am a diesel mechanic and have the AC and refrigeration certifications and have worked on vehicle AC and refrigeration units, but not residential AC. I have refrigerant scales and vacuum pumps. I also work part time for a small company that does refrigeration but not residential AC. One of the refrigeration techs is more than willing to help me and also has reclaimers and manifold gauges, but has not done any residential AC work.

So my questions, on the electrical it calls out a recommended max. circuit breaker of 50 amp. and a minimum circuit ampacity of 31.2 What size wire should I run and what size and type of out side disconnect should I use?? ( the length from the breaker box to the condensing unit will only be about 10')

Next, I have access to R22 and other refrigerants, as this unit was designed for R22 should I stay with that or are their better options now?? (On automotive systems we often do changeovers to R134)

I am planning to pressure test with nitrogen as I do with mobile systems, or is this not needed?? Also, do you add dye and or oil to the charge??

My intention is to run a new line set and filter, solder and pressure check then weigh in an appropriate charge. Any other advice??

Our home is well shaded and we get very good breezes most of the summer so we really only use the AC for about 2-3 weeks a year or I would be looking for a better more efficient unit.
 
Last edited:
To avoid these ads, REGISTER NOW!

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
Yes pressure test, no dye or oil, pull a good vacuum, # 10 thhn copper, #8 copper if romex, #6 aluminum, 60 amp fused disconnect with 50 amp fues. Stick with r-22.

Sent from my XT1254 using Tapatalk
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Yes an outlet next to the condensing unit is always a good thing,Id use a non fused disconnect myself anyway.
On an old unit like that Id get my hands on a newer r22 drop in replacement.
You might have trouble buying freon with your automotive refrigiration license,You might need to pay an hvac guy to charge it for you.;)
A 50a 2p will be plenty,Id run a 20a for the outside outlet.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
I have been given free of charge a Lennox 10ACB48-5P condensing unit and A-coil. Yes, I know this is an older unit and yes I know it is not very efficient. It is however the correct size for my home according to the heating and cooling calculations I have researched on the internet. Did I mention free and worked when remove from a building that was torn down??

I am a diesel mechanic and have the AC and refrigeration certifications and have worked on vehicle AC and refrigeration units, but not residential AC. I have refrigerant scales and vacuum pumps. I also work part time for a small company that does refrigeration but not residential AC. One of the refrigeration techs is more than willing to help me and also has reclaimers and manifold gauges, but has not done any residential AC work.

So my questions, on the electrical it calls out a recommended max. circuit breaker of 50 amp. and a minimum circuit ampacity of 31.2 What size wire should I run and what size and type of out side disconnect should I use?? ( the length from the breaker box to the condensing unit will only be about 10')

Next, I have access to R22 and other refrigerants, as this unit was designed for R22 should I stay with that or are their better options now?? (On automotive systems we often do changeovers to R134)

I am planning to pressure test with nitrogen as I do with mobile systems, or is this not needed?? Also, do you add dye and or oil to the charge??

My intention is to run a new line set and filter, solder and pressure check then weigh in an appropriate charge. Any other advice??

Our home is well shaded and we get very good breezes most of the summer so we really only use the AC for about 2-3 weeks a year or I would be looking for a better more efficient unit.

Id charge it by the gauges/pressure,not by weight.;)
 
OP
H

homebuilt burner

Well-known member
Joined
Dec 8, 2014
Messages
1,763
Location
central Wisconsin
I can get R22 through my other job. I actually have both licenses (I took both test at the time).

I should have clarified my intention was to weigh in a charge and adjust from there, according to pressure, there is a very good table in the installation manual, as I am unsure of what it would take to fill the line set.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
I can get R22 through my other job. I actually have both licenses (I took both test at the time).

I should have clarified my intention was to weigh in a charge and adjust from there, according to pressure, there is a very good table in the installation manual, as I am unsure of what it would take to fill the line set.

:thumbup::thumbup::thumbup::thumbup::thumbup:
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,269
Location
Coastal NJ
Inspect the equipment carefully. Try and figure out how long that equipment lasts in your area. My neighborhood was built in 1986. Maybe 10 years ago my A-coil sprung a leak. I replaced the system. Following year my next door neighbors unit died. So I replaced his. Then I did 3 more in the next 2 years. It was like they all had an expiration timer. It's a lot of work to do the installation so you hope to get some time out of it.

All of those systems in the neighborhood have since been replaced.

Oh, and don't use soft solder on the connections.
 
OP
H

homebuilt burner

Well-known member
Joined
Dec 8, 2014
Messages
1,763
Location
central Wisconsin
Today, we brazed on some test fittings and vacuum tested both the A-coil and the condenser. Looks good to go ahead. When I cut the ends off of the condenser I could hear the vacuum leaking( it held vacuum while it was in storage for the last year) a good sign I thought. The A-coil that came with the system is a model # C23-51-1 Lennox. Can anyone suggest a filter for this system? I do not have that or any suggestion of such in the installation manual I downloaded. FYI this is an expansion valve system if that matters.
 

magicrat

Well-known member
Joined
Jun 18, 2015
Messages
321
Today, we brazed on some test fittings and vacuum tested both the A-coil and the condenser. Looks good to go ahead. When I cut the ends off of the condenser I could hear the vacuum leaking( it held vacuum while it was in storage for the last year) a good sign I thought. The A-coil that came with the system is a model # C23-51-1 Lennox. Can anyone suggest a filter for this system? I do not have that or any suggestion of such in the installation manual I downloaded. FYI this is an expansion valve system if that matters.

I always test with pressure not vacuum unless using a micron gauge.....Ive been burnt by vacuum testing more than once on a very slow leak.....using a micron gauge though vacuum is accurate.....but what do i know...ur mileage may vary.
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
Today, we brazed on some test fittings and vacuum tested both the A-coil and the condenser. Looks good to go ahead. When I cut the ends off of the condenser I could hear the vacuum leaking( it held vacuum while it was in storage for the last year) a good sign I thought. The A-coil that came with the system is a model # C23-51-1 Lennox. Can anyone suggest a filter for this system? I do not have that or any suggestion of such in the installation manual I downloaded. FYI this is an expansion valve system if that matters.

Air filter or filter/ dryer for the refrigerant? If filter/ dryer i would use a 16 cubic inch version of whatever brand is available, i like sporlan if given a choice.

Sent from my XT1254 using Tapatalk
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Charging by weight as per manufacturer recommendations works great most of the time.

Charging strictly by pressure? I sure hope you mean using superheat/subcool measurements.

Yep,Ive seen plenty of new installs over the years that were off by using the factory charge in the condensing unit.
You check equipment using temp/pressure,why wouldnt you charge an empty unit the same way?:dunno:
 

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
Just curious. How do you know what the oil level is in the old compressor? And how much does it matter?
 
OP
H

homebuilt burner

Well-known member
Joined
Dec 8, 2014
Messages
1,763
Location
central Wisconsin
Next question in the series. What size wire do I need to run from the furnace to the condenser for thermostat hook up? The diagram shows the cool (signal) wiring running from the furnace to the contactor and a common. I am thinking that is probably 24 volt thermostat type wiring.
 
To avoid these ads, REGISTER NOW!

Brian_WK

Well-known member
Joined
Jun 30, 2015
Messages
1,177
Location
NE South Dakota
I would also recommend running at least a 5 wire. Never know when you might want to add a thermostat with a outdoor temp sensor or have a wire break or get nicked in the wall. The extra cost is negligible. Or just run 3 sets of 2 wire labeling both ends.

Brian
 
OP
H

homebuilt burner

Well-known member
Joined
Dec 8, 2014
Messages
1,763
Location
central Wisconsin
I am finally getting some time to hook things up. I am having questions about the wiring of the signal lines for the condenser contractor. See attached photos of thermostat wiring where I attached the blue wire. Is this correct? And which terminals do I hook onto for the contractor signal wires?
 

Attachments

  • image.jpg
    image.jpg
    18.7 KB · Views: 35
Last edited:

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
I am finally getting some time to hook things up. I am having questions about the wiring of the signal lines for the condenser contractor. See attached photos of thermostat wiring where I attached the blue wire. Is this correct? And which terminals do I hook onto for the contractor signal wires?
Y and C normally go to the outside condenser contactor/relay.
 

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
In your first picture you have the blue wire on C of the furnace control board. The board connects C to one side (usually grounded) of the 24vac transformer. The other side of the transformer is connected to the R terminal of the board (does go through fuse and other protection). The R goes to the thermostat and when a call for cooling the 'stat will connect R to Y. That way the compressor contacts get 24 volts. One feed from both sides of the transformer.

In general, the old thermostats don't need a C. The new ones rely on batteries. WiFi models use a C.
 
OP
H

homebuilt burner

Well-known member
Joined
Dec 8, 2014
Messages
1,763
Location
central Wisconsin
With it wired as shown it will not put 24 v to the contractor when the thermostat is switched to cool. I can manually depress the contractor and the compressor runs.

Do I have the thermostat hooked up correctly? I hooked the blue wire up there as well as taking the resistor out.
 
OP
H

homebuilt burner

Well-known member
Joined
Dec 8, 2014
Messages
1,763
Location
central Wisconsin
I put the blue wire on the RC terminal on the thermostat and the C terminal in the furnace. And hooked to the C wire in the condenser. Also there was a resistor that I took out of the thermostat. It was between the RC and the Ph which has the red wire on it as well.
 
OP
H

homebuilt burner

Well-known member
Joined
Dec 8, 2014
Messages
1,763
Location
central Wisconsin
I tried it to see if the condenser would come on with thermostat set below room temp and set to cool. It did not work and I did not get power on the Y terminal wire and C terminal wire. When it did not work I shut all power off to wait for assistance.
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
Unhook the blue wire at the stat if there is no C only terminal and unhook it at the furnace as well. The RH and RC should be jumpered together unless you have a dual transformer system so either reinstall the little resister or simply use a piece of wire to connect them again, should be good to go at that point.

Sent from my XT1254 using Tapatalk
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
I always test with pressure not vacuum unless using a micron gauge.....Ive been burnt by vacuum testing more than once on a very slow leak.....using a micron gauge though vacuum is accurate.....but what do i know...ur mileage may vary.


You cannot leak check with vacuum, PERIOD. Micron guage or not.

Tommy
 
Last edited:
OP
H

homebuilt burner

Well-known member
Joined
Dec 8, 2014
Messages
1,763
Location
central Wisconsin
Unhooked the blue wire. Set to cool waited about 1 min blower fan kicked on 30 sec later condenser came on.

Thanks guys. Now to make refrig connections and leak check.
 
OP
H

homebuilt burner

Well-known member
Joined
Dec 8, 2014
Messages
1,763
Location
central Wisconsin
Finally had time to get the freon lines hooked up and charge the system. Pressures match the install manual.

Works great. Wife is happy.

Thanks for everything gentlemen.
 