To avoid these ads, REGISTER NOW!

Possible and How?

YankeeFlyGuy

Well-known member
Joined
Jul 10, 2017
Messages
81
Location
Central Indiana
Hello! These are questions I plan to ask my electrician when I hire him, but I want to make sure he gives me the correct answers.

What size wire and breaker would I need to run electric to a small campsite shower house that is exactly 200' from the main panel in my barn? I would need to power an RV outlet, 3-4 lights, a small water heater, and 2 outlets for hair dryers, small heater etc.

Can I run it to another small panel in the shower house so I have a cut off switch there instead of running back and forth to the main barn panel?

Thanks!

15qq344.jpg


2v7tipv.jpg


8we2xh.jpg


ae64ww.jpg
 
Last edited:
To avoid these ads, REGISTER NOW!

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,909
You'll need to run fire wires (two hot, neutral, ground) to a panel, which will also need a pair of ground rods. Size of the wire depends on how big a panel you plan on. 60A is probably plenty, for that at that distance, probably 2-2-2-4 MHF for direct burial. Similar size individual conductors if you're going to run a conduit. Do a load calc based on the actual appliances you're planning on, and any expected growth (RV hookup?), because you might get away with less, which would take smaller, cheaper wire. d
 

wagoncrazy

Well-known member
Joined
May 5, 2016
Messages
81
Location
Newhall CA
Just blurtin' in here...
Elec. hookups in most RV parks are either 30amp or 50amp.
30 should power one rooftop AC and a microwave, but a big RV with 2 AC's running needs 50 amp. Just blurtin' in here...
 
To avoid these ads, REGISTER NOW!

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,328
Location
Alexandria, VA
2-2-2-4 AL Mobile Home Feeder in conduit to a sub-panel is a common solution. MHF is rated for up to 90 amps, so it should work well for about 60 amps and 200 feet. Allowing for line loss, you could probably run more than 60, but I don't know the exact calculation.

Given the small space and intended use, I would consider a weatherproof, lockable, sub-panel mounted on the outside. You need 30" wide unobstructed access to the sub-panel, and it should not be in a bathroom, and that would be a lot easier to get when mounted outside. Then use conduit, wet-rated wire, and GFCI's for all the receptacles, since they may be exposed to water.

Bruce
 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,775
Location
NW Iowa
2-2-2-4 AL Mobile Home Feeder in conduit to a sub-panel is a common solution. MHF is rated for up to 90 amps, so it should work well for about 60 amps and 200 feet. Allowing for line loss, you could probably run more than 60, but I don't know the exact calculation.

Given the small space and intended use, I would consider a weatherproof, lockable, sub-panel mounted on the outside. You need 30" wide unobstructed access to the sub-panel, and it should not be in a bathroom, and that would be a lot easier to get when mounted outside. Then use conduit, wet-rated wire, and GFCI's for all the receptacles, since they may be exposed to water.

Bruce

+1 ^

Great advice on both wire size and the panel location!
 
To avoid these ads, REGISTER NOW!
Top Bottom