Power inverter to power well pump?

PissedOffAndAnnoyed

New member
Joined
Jul 4, 2021
Messages
4
I have a well with a 2hp submersible pump. It draws about 1.6kw @ 240v. I want to be able to power this during a power outage, but most inverters or generators that have 240v capability are absolutely huge and expensive.

I'm wondering if a generic foreign market 230v 50hz DC power inverter would work to run my pump? Would it just pump slower at 50hz? (that is OK) Is there any reason that wouldn't work since the it would be single phase power and not split phase like US 240v? I would not be using it for long periods of time, just enough for basic usage if the power goes out.

If that would work, what size inverter would I need in order to be able to start a 1600w 2hp motor? I have no idea what the startup rush is.
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
I have a 240v inverter generator that wasn't crazy expensive. Briggs q6500

You are going to need a big, big inverter and some serious battery power to run it. Most car alternators don't put out anywhere near that power at idle and many don't even max out that high, so you'll be running the car engine at 3k+,and drawing off battery
 
OP
P

PissedOffAndAnnoyed

New member
Joined
Jul 4, 2021
Messages
4
I don't need generator advice, please do not turn this into a generator/battery thread.

1600w at 12v is 133 amps. Most cars could handle that through a set of jumper cables for a few minutes, but I have other power sources. The well would not need to be used for more than a few minutes, this would be for emergency use only.

It does use a lot of power instantaneously to startup, but that is very short, and the subject of my question.
 

Ole Slewfoot

Well-known member
Joined
Feb 22, 2016
Messages
5,098
Location
Freedom, CA
Get an adequate tank to gravity feed during outages. You will never regret it.

A 2k/4K 230 inverter is under $100 on alibaba, and probably equivalent quality to the 3k harbor freight unit that pulls down the starting batteries in my diesel truck in a couple minutes at full load.
 
OP
P

PissedOffAndAnnoyed

New member
Joined
Jul 4, 2021
Messages
4
Is it really so hard to stick to the question? No, I am not installing a water tank. I asked a very simple question...
1. What is the minimum size power inverter to handle the startup current from a 2hp motor?
2. Is there any problem running a normal 240 60hz motor on 230v 50hz?
 
OP
P

PissedOffAndAnnoyed

New member
Joined
Jul 4, 2021
Messages
4
You're clearly not understanding the question. A power inverter needs to be oversized compared to the load when running an electric motor. A 2kw inverter would not start a 1.6kw motor. The question is, what is the minimum size that would? It's not something you can just calculate.

If you don't have an answer please just hit your back button.
 

RPH

Well-known member
Joined
Dec 17, 2006
Messages
4,190
Location
Michigan Thumb
Location would help. In North America 60 Hz is standard. If the pump is dual rated for 50 or 60 hertz then you be ok, slight loss of power. How ever if it’s 60 Hz only the pump will be very unhappy and will tend to cook itself to death. I have lots of experience sending power tools to Europe for projects. All worked and all were dead or close to death when done. None came home.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
12,005
Location
Fargo, ND
I know you don't want to talk generators but i am tossing this out as an example, when sizing a generator for a motor load we always went 2-1/2 to 3 times the amp out put for starting load. I would assume and inverter would need to to be sized similarly. so that turns your 1600 watts into 4800 watts. I also would find specs on your pump and use that information for sizing, as we always went off the nameplate for sizing, not the actual current draw. I would assume a 2 HP motor at full load is closer to 2400 watts so that would put your invertor at 7200 watts. 7200 watts at 12 volts will be 600 amps. You will need a good sized battery!

As for the 50 hertz invertor, I wouldn't try it unless the motor is rated for it, it might be.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,154
Location
Rhode Island
Your question is not answerable without your pump's full datasheets from the manufacturer. Generally speaking, a motor will typically draw ~4x-5x its running current during startup. Goulds Pumps say their 2HP 4" submersible well pump has an LRA of about 45A. So that means during start-up, you can expect a 45A inrush - or about 11KW.

Your plan to use a 50Hz 230-240v inverter makes this issue worse. At 50 Hz, the impedance of the motor's windings will be lower, which means more current will flow. So the motor is going to draw more current than it normally would during start-up - about 20% more. So realistically your inrush will be up near 55-60A. At 50Hz, the pump will also spin 20% slower. The maximum pressure a centrifugal pump makes is based on the square of the pump's speed. So a 20% reduction in pump speed is going to reduce your maximum pressure potential by about 40%.

But your math for your power consumption is also going to be off. A 2HP motor is really only going to be about 85% efficient, so realistically it's going to be drawing more like 1800W in operation, and with a 85% inverter efficiency - that's 2.1KW input.

This isn't a workable plan for a variety of reasons.
 

cstmg8

Well-known member
Joined
Apr 7, 2018
Messages
519
Location
Pickerington, oh
50hz, just nope. Well explained above.
So, assuming you're going with a 60hz inverter, you need a MINIMUM of 4,000w (2.5x)for startups. That's definitely the low end. 1.6kw ÷ 240v = 6.6amps where did you get your info, motor data tag? Is it FLA?
If you're dead set on an inverter, have you thought about adding a soft start to your pump motor? It should reduce your starting current and allow a more reasonable inverter.
Something like this, I haven't done any research to see if this one will work for you:
 
Last edited:

Captain Spaulding

Well-known member
Joined
Feb 13, 2017
Messages
757
Location
Southern Indiana
Since you don't seem to have a clue about how to be remotely polite, the idea of using a 50Hz inverter on a 60Hz pump is stupid, and the idea of using any inverter to power a well pump isn't much better. Anyone who thinks either of those is remotely practical should be appreciative of any suggestion because it's virtually impossible to come up with a worse plan.
 
Last edited:

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,646
Location
BC
I work on a 50Hz jobsite... we have miserable luck with 60Hz motors. They need to be dual-rated to work under load.

I have an 1800W 120v inverter also. It will not start the little $100 air nailer compressor I have. The inrush characteristic of the motor is too much.

The gravity-tank/cistern is the way to go.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,253
Location
Modesto, CA
running a well pump from an inverter and batteries is a fools errand. you havent even told us how deep the well is which will effect things here too (ie. how much head of water in the riser pipe the pump has to push up on startup). then you want to add in 50hz... this is a disaster in the making...
 
To avoid these ads, REGISTER NOW!

tyme2par4

Well-known member
Joined
May 16, 2016
Messages
571
Location
NH
Since you don't seem to have a clue about how to be remotely polite, the idea of using a 50Hz inverter on a 60Hz pump is stupid, and the idea of using any inverter to power a well pump isn't much better. Anyone who thinks either of those is remotely practical should be appreciative of any suggestion because it's virtually impossible to come up with a worse plan.
There's nothing wrong with using an inverter to power a well pump. There are plenty of large inverters that would handle it, but they are going to be expensive.
You can get a 6kW 60Hz 240V split phase inverter for $1500. The question that needs to be answered is what is the starting load of the pump? Aims claims their inverter can surge up to 18kW for 20 seconds, so it would probably be up to the task. But this is a 24V inverter, so you aren't going to be able to run it off a car battery.
 

WisJim

Well-known member
Joined
Dec 20, 2010
Messages
2,390
Location
Menomonie, WI
Our over 22 year old Trace SW4024 inverter runs our submersible pump just fine, in a well that's about 130' to water. But the inverter can put out over 9kw momentarily as in motor starting loads, and it's big and heavy, and cost about $3k back when I bought it. Small and cheap won't do it.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
The OP’s forum name is a big clue from my read so far.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Our over 22 year old Trace SW4024 inverter runs our submersible pump just fine, in a well that's about 130' to water. But the inverter can put out over 9kw momentarily as in motor starting loads, and it's big and heavy, and cost about $3k back when I bought it. Small and cheap won't do it.
What's the hp on that pump? My last house had the pump at 125' and it was 7gpm and only 1/2 hp.

What are you using for batteries and chargers?
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,888
Location
East Bay SFO
Our over 22 year old Trace SW4024 inverter runs our submersible pump just fine, in a well that's about 130' to water. But the inverter can put out over 9kw momentarily as in motor starting loads, and it's big and heavy, and cost about $3k back when I bought it. Small and cheap won't do it.

I bet you have an impressive bank of batteries to back that up.
Maybe 8 six volt golf cart batteries wired up in series parallel ?
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
The NEC table shows a 2HP, 1Ø, 240V motor's full load as 12A, not 1.6kw @ 240v (6.6A)
The least load I can find is a SPL(Special) 2HP motor that draws 7.5A:ROFLMAO:
 
Last edited:

WisJim

Well-known member
Joined
Dec 20, 2010
Messages
2,390
Location
Menomonie, WI
To answer the questions about my well pump, inverter, batteries etc., we have a set of 1500 amp hour 2 volt lead acid cells, similar to large fork lift cells, about 200 pounds each, 2400 pounds or more total. They were new in 1999 and are reaching the end of their useful life. The pump is a half horse unit. The system is charged by 7.4 kw of photovoltaics and a 2.5 kw wind turbine and we have grid connection for backup. The wind turbine is a Jacobs from the 1940s (rebuilt in 1977 and due for bearing renewal soon), and our oldest PVs were bought in 1981 or 82, and still work well.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
To answer the questions about my well pump, inverter, batteries etc., we have a set of 1500 amp hour 2 volt lead acid cells, similar to large fork lift cells, about 200 pounds each, 2400 pounds or more total. They were new in 1999 and are reaching the end of their useful life. The pump is a half horse unit. The system is charged by 7.4 kw of photovoltaics and a 2.5 kw wind turbine and we have grid connection for backup. The wind turbine is a Jacobs from the 1940s (rebuilt in 1977 and due for bearing renewal soon), and our oldest PVs were bought in 1981 or 82, and still work well.
Sounds like a really neat setup. I imagine you have a good chunk of coin in all that.

Do primarily run your whole home off that setup?
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,154
Location
Rhode Island
The NEC table shows a 2HP, 1Ø, 240V motor's full load as 12A, not 1.6kw @ 240v (6.6A)
The least load I can find is a SPL(Special) 2HP motor that draws 7.5A:ROFLMAO:
The NEC motor tables are pretty old and outdated these days. They're basically worst-case-crusty-ancient-motor. They still rate a 5HP 3-phase motor at 15.2A for example. It's not even legal to sell a 3-phase motor that inefficient anymore. They spec 28A for single phase 240v 5HP motors, when most of them these days are down around 20-21A (or even a little lower for the very best motors).
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,932
Location
oregon

You may find that a Monodrive controller from the above link will solve your problem. I have a sub drive and it will start fine on a regular generator. These have a 'Soft start' feature that does away with high inrush current.

lg
no neat sig line
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,646
Location
BC
The NEC motor tables are pretty old and outdated these days. They're basically worst-case-crusty-ancient-motor. They still rate a 5HP 3-phase motor at 15.2A for example. It's not even legal to sell a 3-phase motor that inefficient anymore. They spec 28A for single phase 240v 5HP motors, when most of them these days are down around 20-21A (or even a little lower for the very best motors).

That's not strictly efficiency. On single-phase motors, capacitors are the main reason for these lower FLAs.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,620
Location
SE MI

You may find that a Monodrive controller from the above link will solve your problem. I have a sub drive and it will start fine on a regular generator. These have a 'Soft start' feature that does away with high inrush current.
This is the key to running a pump off of either an inverter or generator !

There are after market "soft starters" like the one from Micro Air that really work. You do NOT want a "hard start" kit !
 

Williams B

New member
Joined
Jul 7, 2021
Messages
3
I have a 240v inverter generator that wasn't crazy expensive. Briggs q6500

You are going to need a big, big inverter and some serious battery power to run it. Most car alternators don't put out anywhere near that power at idle and many don't even max out that high, so you'll be running the car engine at 3k+,and drawing off battery
Same one with me.
 