Keep your data cables about 12" from power cables and you should be fine.
Check out
this link and scroll down about halfway for the Do's and Don't table.
I'd ensure that extra pull ropes are pulled through the conduits when pulling your cables.. never know when you'll need to pull more (and pull new ropes through when you do).
Find the biggest conduit you think you will need, then put in one twice as big.

I put in a 2" conduit for the tower I built last summer for internet and satellite and an glad I didn't go smaller. 5 RG6 quadshield cables plus pull rope would have been too small for the 1.25" conduit I was originally eyeing. I'd not put in conduit smaller than 1.5" for a couple of CAT5 and RG runs. The bends in the trench plus the bends at the ends all end up meaning drag on your wires (shouldn't have more than 180deg - total - of bend in your conduit run). Use lots of cable lube when pulling your data wires!
I too like the idea of burying an air line plus, why not run a gas line now too? You've got the trench open. Even if it's not used right way, it's in.