Hello Garage Journal. This is my first thread. First off, I would like to thank all of you who have helped me with my research. This website has been the most informative. I am a stubborn DIYer.
This is my situation:
I am running a 100amp service to my pole barn from my 200amp service in my house. The soil here (central MN) is mostly sand. My 30' x 60' barn has a small woodshop, a shallow well pump (dedicated to my garden), some overhead lights, and other outlet receptacles. My future plans are a complete bathroom (the room is built), and a small recording studio.
Yesterday I bought 150' of AL MHF 2-2-2-4 ($1.47 per foot) and a 90 amp breaker ($70
). The MHF has USE-2 OR RHH OR RHW-2 SUN-RES printed on it.
From what I've been reading, I can direct bury this cable 24" down (no conduit)from structure to structure and bring it out of the ground in conduit to both load centers. I plan on buying a 100 amp load center today along with a ground rod and conduit. Here are some questions:
1. I will be crossing a driveway. Do I have to use conduit? Can I run conduit just the driveway distance? What size conduit?
2. When I hook up the feeder, is it as simple as directly connecting the 2 hots, neutral, and ground? (Thought I read that the neutral and ground need to be tied together in the 100amp barn load center)
3. Where does the ground rod have to be in relation to the load center?
4. If I want to run CAT5 (internet) and possibly coax (satellite TV) , should that be buried in conduit 12" above the MHF?
5. If I can bring the MHF into my (unfinished-attached)garage 20' before the load center, can I drill holes in the 2x6 studs and run it in that way? This would keep the MHF underground coming into the house, which would make my wife happy about the "messy conduit sticking up".
Thank you,
Bill
This is my situation:
I am running a 100amp service to my pole barn from my 200amp service in my house. The soil here (central MN) is mostly sand. My 30' x 60' barn has a small woodshop, a shallow well pump (dedicated to my garden), some overhead lights, and other outlet receptacles. My future plans are a complete bathroom (the room is built), and a small recording studio.
Yesterday I bought 150' of AL MHF 2-2-2-4 ($1.47 per foot) and a 90 amp breaker ($70
From what I've been reading, I can direct bury this cable 24" down (no conduit)from structure to structure and bring it out of the ground in conduit to both load centers. I plan on buying a 100 amp load center today along with a ground rod and conduit. Here are some questions:
1. I will be crossing a driveway. Do I have to use conduit? Can I run conduit just the driveway distance? What size conduit?
2. When I hook up the feeder, is it as simple as directly connecting the 2 hots, neutral, and ground? (Thought I read that the neutral and ground need to be tied together in the 100amp barn load center)
3. Where does the ground rod have to be in relation to the load center?
4. If I want to run CAT5 (internet) and possibly coax (satellite TV) , should that be buried in conduit 12" above the MHF?
5. If I can bring the MHF into my (unfinished-attached)garage 20' before the load center, can I drill holes in the 2x6 studs and run it in that way? This would keep the MHF underground coming into the house, which would make my wife happy about the "messy conduit sticking up".

Thank you,
Bill



idea: