I have a small secondary shop 196 sqft; not much required for power; if I need 40amps at the subpanel, what can I pull from the main panel if 240?
The run is 100' , in 1-1/4 conduit.
is 8ga copper plenty? 8-8-8-8
At 196 ft would be considering alum wire. They make a wire just for this type of run. 2 2 2 4. Hook it to a 60 breaker.
Run is 100 ft, not 196 ft.
At 196 ft would be considering alum wire. They make a wire just for this type of run. 2 2 2 4. Hook it to a 60 breaker.
Run is 100 ft, not 196 ft.
Not according to the OP. sberry is correct