power to small secondary shop building

gforster

Member
Joined
Aug 18, 2014
Messages
10
I have a small secondary shop 196 sqft; not much required for power; if I need 40amps at the subpanel, what can I pull from the main panel if 240?

The run is 100' , in 1-1/4 conduit.

is 8ga copper plenty? 8-8-8-8
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
I have a small secondary shop 196 sqft; not much required for power; if I need 40amps at the subpanel, what can I pull from the main panel if 240?

The run is 100' , in 1-1/4 conduit.

is 8ga copper plenty? 8-8-8-8

Equipment ground only needs to be 10 AWG and needs to be green, and the neutral has to be white, tape is not permitted to be used grounding and neutral conductors cannot be reidentified unless 4 AWG or larger.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,093
Location
Modesto, CA

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,974
Location
Richmond, VA
Regardless of distance, I would run aluminum, probably 2-2-4-6. At a buck a foot, it will be cheaper than copper and have all the headroom you could want for a small shop.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I agree on the aluminum, but check your codes. In my area, we are not allowed to derate the neutral anymore
 