Power to the drive gate - mapping it out

trifecta81

New member
Joined
May 10, 2019
Messages
3
Location
FL
Hi all, I am planning to pull power to my driveway gate about 150'. From reading here and elsewhere it appears 10 ga wire 10/2 will be me 110 to the gate post to run an single gate automated opener (gate mounted linear actuator initially), a couple LED gate lights and a 110 outlet for occasional Christmas lights. Depending on the outcome, over time I may upgrade the opener to a commercial unit that sits on a pad adjacent to the gate. 20A breaker in the box.

Additionally planning on running it in some kind of conduit, yet to be decided. I have a 90 degree turn to make early in the run so I'm not sure it would ever be feasible to replace the wire or add to it in any way without digging again. Maybe run a 3rd wire in the conduit for a little insurance?

Additionally - open to solar but I don't see it getting me there given the activity here and all the gate operators I've looked at operate from a charged battery.

Looking forward to your thoughts!
 
Last edited:
To avoid these ads, REGISTER NOW!

Noltz

Well-known member
Joined
Mar 10, 2020
Messages
377
Location
Ontario, Canada
Using Southwires Calculator, 15A @ 150' says 8 gauge. 20A is 6 gauge. 10/2 would feed 10A. Not sure if you can get a breaker for 10A? Most gate openers are small 12v chargers keeping a 12 volt battery charged, and the battery operates the gate. The LED lamps and occasional Christmas lights would work on 10A. Worry about your "today's problem" but drop in conduit that'll support 6 gauge with a pull rope for later, just in case.
 

Walkers

Well-known member
Joined
May 17, 2021
Messages
3,912
Location
Cave Creek Az
Most of the good operators are DC now, the power only runs the battery charging system. That way you are not out of business when the power goes out. I would be surprised if you needed anything bigger than 16 gauge. I am talking about swing arm and slide operators, not the crappy little linear actuators. Avoid those or you will live to regret it.
 
To avoid these ads, REGISTER NOW!
OP
T

trifecta81

New member
Joined
May 10, 2019
Messages
3
Location
FL
Thanks for the replies and advice. Not sure of the initial amp usage Bree but low with a DC charger, LED lights, occasional Christmas stuff, maybe a wifi camera. So I'm somewhere between 6 and 16 gauge...

Answers bring more questions:
What size conduit could ensure a 6 gauge wire pull later, given that I have to navigate that 90 bend?
Would it be acceptable to tie a 6g wire into 12 gauge wire on a short run from the breaker box?
And then what type of conduit is appropriate for a 6/2 wire run at (hopefully) a 18" depth?
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,748
Location
Austin, TX
I had a gate 100' away, eventually ran 12/2 to it, but not before installing a 150 watt solar panel and 2 deep cycle batteries.. Had them powering the gate and an IP Camera system no problem.

If you're gonna do it in conduit, 3/4" will work just fine for 10ga wire. Just leave a pull string in there. You can also "vacuum" a light grocery bag through on the end of a pull string.. (old electricians trick)
 

BreeStephany

ALLIANCE MEMBER
Joined
May 19, 2012
Messages
851
Location
Oregon
Thanks for the replies and advice. Not sure of the initial amp usage Bree but low with a DC charger, LED lights, occasional Christmas stuff, maybe a wifi camera. So I'm somewhere between 6 and 16 gauge...

Answers bring more questions:
What size conduit could ensure a 6 gauge wire pull later, given that I have to navigate that 90 bend?
Would it be acceptable to tie a 6g wire into 12 gauge wire on a short run from the breaker box?
And then what type of conduit is appropriate for a 6/2 wire run at (hopefully) a 18" depth?
Minimum, not taking into account voltage drop, would be #14 THHN Cu conductors, rated at 15A and to be installed on a 15A OCPD (fuses or breaker).

Taking into account the distance and either a 15A or 20A circuit (12A or 16A maximum for loads for any loads running continuously for 3 hours or more), over a distance of 170ft (150ft run + ~10ft into panel + ~10ft into gate enclosure), a #8 line & neutral conductor would provide 2.07% voltage drop @ 12A and 2.76% @ 16A. This would provide the proper conductor sizing for either a 15A or 20A circuit, based upon the 3% allowable voltage drop on branch circuits per NEC 210.19(A).

Given the size of conductors, I would highly suggest using a 20A breaker, as it will likely be difficult to locate a 15A breaker that has a proper lug for a #8 wire. You will have to research the lug size of breakers available specifically for your panel.

Based on a 120V circuit, with a #8 THHN Cu line conductor, a #8 THHN Cu neutral conductor and a #12 THHN Cu grounding conductor, your conduit fill for 3/4" schedule 40 PVC conduit would be 23.25%, which is within the 31% / 40% limits of NEC 300.17.

I would highly recommend, given the size of conductors, to upsize your conduit to 1" schedule 40 PVC conduit for where buried and schedule 80 PVC or rigid, where subject to damage, if applicable.

Per NEC table 300.5, you will have to have a minimum of 18" of cover to the top of the conduit where buried, provided it is not under a concrete / asphalt roadway, concrete pad, encased in concrete, under a sidewalk, etc. With the 18" cover requirement, unless required otherwise by the authority having jurisdiction (AHJ), I would suggest you dig your trench no less than 20".

As you backfill your conduit, I would also recommend installing burial tape at 6" below finished grade in the trench so that the conduit will be less likely to be hit if future excavation occurs.

When routing your conduit, I would recommend the straightest shot between your panel and gate electrical enclosure and try to avoid 90s in the middle of the pull whenever possible.

It is also important to remember that you can have no more than 360 degrees of bend (standard offsets, 45 deg bends, 90 deg bends, etc.) in a conduit between pull points

If there is a spot where you see a strong / standard 90 as unavoidable mid run, I would highly recommend utilizing a ground box to 90 the conduits into so you can have easier access to the pull point.

Once the conduit is in place, as dcg9381 suggested, use a pull string, attached to a plastic bag (grocery bag, animal waste bag, etc.) and use a vacuum to **** the pull string through the entire conduit, then attach your conductors and start pulling.

You can also get a 200~250ft steel fishape (leader highly recommended) to pull in your conductors.

If you use a light weight pull string (survey string, etc.), you will likely want to pull in a larger poly rope to the pull string to ensure your pull line does not break when pulling in or cut through 90s.

When pulling conductors, I always urge people to spend a couple of extra dollars and get a roll of 3M Super33+ electrical tape to make up your wire head, as it is much stronger and has a stronger bond than traditional electrical tapes and is less likely for you to loose a conductor over the pull distance, resulting in you potentially having to pull out all of the conductors and having to start over.

Just my two cents.
 