You know, I now have no idea what you are talking about. The receptacle side terminals absolutely feed through when downstream supply conductors are attached to them and the devices are in parallel.
By the way, I find no manufacturer stating that their non GFCI receptacles are rated for 20 amp feed through. We all seem to assume this is so, but where is the spec?
Perhaps the UL has tested this and OK's it but I consider it an open issue on the feedthrough for those that like to use the side terminals and not pigtail.
That's why a bad connection on a daisy chained device using just the screws will fail downstream outlets. A pigtail IS a daisy chain, just done in a completely electrically equivalent way to using all 4 screws. A pigtail is simply a superior substitute for using the device connection terminal feed through feature.
If all you are trying to say is that the prongs of the receptacle do not feed through then that is true but you are just being confusing right now. Maybe you are arguing that the side terminals are not part of the receptacle?
By the way, I find no manufacturer stating that their non GFCI receptacles are rated for 20 amp feed through. We all seem to assume this is so, but where is the spec?
Perhaps the UL has tested this and OK's it but I consider it an open issue on the feedthrough for those that like to use the side terminals and not pigtail.
That's why a bad connection on a daisy chained device using just the screws will fail downstream outlets. A pigtail IS a daisy chain, just done in a completely electrically equivalent way to using all 4 screws. A pigtail is simply a superior substitute for using the device connection terminal feed through feature.
If all you are trying to say is that the prongs of the receptacle do not feed through then that is true but you are just being confusing right now. Maybe you are arguing that the side terminals are not part of the receptacle?