Pressure Relief valve placement?

Joe Cool

Active member
Joined
Jun 24, 2012
Messages
39
Location
Winnipeg, MB Canada
I need some help with the final placement for the pressure relief valve on my radiant heat system.
I know that it is recommended that the valve be the first device coming from the boiler and the boiler manual also states that the valve must be installed in the vertical position.

2f6b8a25-c67c-409d-866d-8fe0b39001d2_zps4f6kntto.jpg


I would like to plumb the valve towards the right of the entire system but to do this I would need to raise the valve about 4" to clear the boiler. Can I install a 4" piece of copper pipe between the Tee fitting and the valve or must the valve be connected right on the tee fitting as pictured?

Thanks in advance.

Joe
 
To avoid these ads, REGISTER NOW!

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,872
Location
oregon
I'm not a plumber so take the following as a good guess. Doesn't that valve relieve on over temp and/or over pressure. So the further you remove it from the temp source the less sensitive it will be.

lg
no neat sig line
 

acmikee

Well-known member
Joined
Feb 2, 2005
Messages
301
Location
olympia, wa
yes you can raise it up. it is on the outlet of the boiler?
also install a union on the discharge side of the relief and pipe the drain to outside of the bldg.(check local codes)
 
OP
J

Joe Cool

Active member
Joined
Jun 24, 2012
Messages
39
Location
Winnipeg, MB Canada
yes you can raise it up. it is on the outlet of the boiler?
also install a union on the discharge side of the relief and pipe the drain to outside of the bldg.(check local codes)

It is on the outlet side and I fully intend to use a union on the piping so that I can disconnect the pipe and easily remove the valve if it ever needs to be replaced.

I would like to pipe the valve over the boiler and down the opposite side of the boiler away from all the other plumbing.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,582
Location
Long Island
I'm not a plumber so take the following as a good guess. Doesn't that valve relieve on over temp and/or over pressure. So the further you remove it from the temp source the less sensitive it will be.

lg
no neat sig line

No. A T&P valve is for a storage tank (like a water heater). This is a pressure (only) relief valve.
 
To avoid these ads, REGISTER NOW!

dfiler2

Well-known member
Joined
Dec 15, 2014
Messages
2,858
Location
NW Minnesota
No. A T&P valve is for a storage tank (like a water heater). This is a pressure (only) relief valve.

T&P stands for Temperature and Pressure, generally the probe needs to be long enough to be inside the actual heating appliance.
 

BadgerBoilerMN

Well-known member
Joined
Aug 4, 2011
Messages
837
Location
Minneapolis
Don't get fancy. This config could fill the valve full of water and make you boiler a bomb.

The valve must be in the upright position, your first picture was correct. Just run the pipe strait done to the manifold area and be happy.
 

pstnbly

Well-known member
Joined
Jul 20, 2010
Messages
766
Location
So. Vermont
Like this? I originally planned to mount the valve horizontal in order to achieve my goal but then I finally decided to read the boiler manual where it clearly states the valve must be installed vertically. Duh!

20151206_172122_zpsglxcrjzc.jpg

It is not legal nor recommended to be installed in the manner shown in the picture. Any release or weeping will collect in the valve body possibly causing the valve to seize closed defeating safe operation. Non operable boiler valve turns the boiler into a bomb.:shocking:
 
OP
J

Joe Cool

Active member
Joined
Jun 24, 2012
Messages
39
Location
Winnipeg, MB Canada
I have changed the orientation of the valve since reading in the manual that it must be placed vertically in the system. The above picture of the entire layout was an old picture to demonstrate where I wanted to route any water/steam exiting the valve.
 

sands35

Well-known member
Joined
May 29, 2012
Messages
936
Location
St. Joseph, MI
Rotated it on the wrong 90* axis. From the original orientation, rotate it about a vertical axis, not a horizontal one as you did. Looks like you may need to re-solder that joint back to vertical. If you can't clock the valve 90* in the thread, then you will have to re-solder the female joint clocked ~90*.

Just blow the over pressure straight down from the valve. One 90* elbow to turn it down from the outlet of the valve. Maybe put two 45*s to kink it behind the bottom manifold.

No need to go over the heater. If you must, then space the valve up so you don't add in two 90* elbows. Any over-pressure needs to be blown off cleanly.

It needs to terminate within ~4" of the floor.
 