As an expert contractor, please explain why. You throw out all replies while never delineating the reasons. Point in case: you not addressing a bad heat exchanger while claiming that could cause a combustion air fan failure/pressure switch failure.
I am sure you have procedures in place for all of your techs to comply with your business practices. I seriously believe that your viewpoint has to do with CYA as a contractor.
Seriously awaiting why my diagnoses for combustion air switch failure won't work other than that your junior tech would find it laughable.
If, as you have stated, you don't want to respond to idiot folks such as myself, I'll just treat it as such.
Carry on, sir.
Jim
I've not denied any of the answers as possible reasons for a pressure switch failure, or for a integrated control to show a pressure switch fault. I have from the start implied or intended to imply that often a pressure switch fault does not indicate a bad switch, yes it can be just a bad switch.
As for your question of how a bad heat exchanger can cause the control to show a pressure switch fault let's talk about what the pressure switch is there for... Your remark that it is only there to prove that the combustion air fan is working is incorrect. Yes a working combustion venter is necessary, and yes some lower end equipment does use the venter housing as place to attach the hose that is then attached to the switch as a source of negative pressure. This alone does not mean it's only there to prove the fan is working.
Sequence of operation for your typical modern furnace is as follows:
1. Thermostat calls for heat
2. Integrated control will initiate a check of limits and safeties. This includes the pressure switch.
3. Combustion venter is turned on.
4. The pressure switch closes.
5. The ignition process begins.
6. Burners are lit
7. Flame sensor indicates there is flame
8. After a given time the blower is turned on
9. The furnace runs until the thermostat is satisfied.
Ok so what does the combustion venter do as it runs ??? Yes it moves air... If you have looked at the required negative pressure on the switches you know it is a very low and specific pressure. If you have a restricted exhaust it will not move enough air to create that negative pressure. If you have a badly cracked, rusted out, or plugged up heat exchanger it will not move the correct amount of air and in turn will not create the required specific negative pressure...
As it's been said there are several reasons a control may indicate a pressure switch fault, sometimes it's a bad switch often times it's not...
I just left a no heat call, control indicated pressure switch. There was a spiders nest in the tube to the switch... Had one over the weekend furnace was a 90% on propane, the homeowner has a wood shop in his basement with a big belt sander right next to the furnace. The burners plugged up with sawdust which causes the flame pattern to be very dirty sooty it completly plugged the secondary heat exchanger. The fault on the control was a 3 flash = pressure switch...
I checked back just to see if Bigwil ever posted about his furnace and if replacing the switch cured his problems.
My intention is Not to stir the pot up...