Pressure washer GFCI issues

EP3

Member
Joined
May 2, 2020
Messages
10
Location
Smyrna, TN
I have a Campbell Hausfeld 1600 psi pressure washer that kept immediately tripping the GFCI when I plugged it in. (This is two wire, and double-insulated insulated. Not that that means anything to me.) I went to multiple plugs around the house, inside and out. Each time it had the same results. So last weekend I decided to replace the plug. Home Depot had the exact match. After replacing the plug, the pressure washer ran like it was brand new, and I used it for about 45 minutes.

Now here comes the interesting part. Today I start to use it, and once again it immediately tripped the plug. Once again I made the rounds to multiple plugs, and all had the same results as before. So I tore down the washer hoping to find the culprit, but still don’t know what my problem is. The guts are basically the on/off switch, and the pump. I didn’t meter the switch because I don’t know the reading I’m looking for.

Does anyone have any suggestions as to what I can do to resolve my issue?
 
To avoid these ads, REGISTER NOW!

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,631
Location
BC
Is this on several different GFCI receptacles, or all std ones on the same GFCI breaker? Try the receptacles with other power tools. See what happens.

In my experience, GFCIs don't last forever. Motor loads seem especially hard on them.

I run most power tools - including pressure washer - on non-GFCI circuits. YMMV.
 
OP
E

EP3

Member
Joined
May 2, 2020
Messages
10
Location
Smyrna, TN
Not all of the plugs that I’m trying the washer on are GFCI...to my knowledge. Some are in the garage, some in the house, and some outside. I’ve tried about 5 different plugs in different areas of the house.

Other tools work just fine on the same plugs that I’m trying; drill, circular saw, trimmer. They might not be putting the same amount of draw on the system, though.

The part that really throws me is how it worked perfect after replacing the plug, and now this weekend it is acting up again. It’s almost like I didn’t replace the plug.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,631
Location
BC
Sounds like it is the pressure washer itself.

Try metering between metal parts and the cord for continuity (while unplugged of course.) Keep checking as you take things apart and re-assemble. Odds are something is chafed or corroded and causing a trace current to 'leak'.

I have a cheapo pressure washer myself. I'll simply replace it when it dies.
 
OP
E

EP3

Member
Joined
May 2, 2020
Messages
10
Location
Smyrna, TN
Thanks. I should probably just buy one as well, but I just feel the need to figure this out.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
Not all of the plugs that I’m trying the washer on are GFCI...to my knowledge. Some are in the garage, some in the house, and some outside. I’ve tried about 5 different plugs in different areas of the house.

Other tools work just fine on the same plugs that I’m trying; drill, circular saw, trimmer. They might not be putting the same amount of draw on the system, though.

The part that really throws me is how it worked perfect after replacing the plug, and now this weekend it is acting up again. It’s almost like I didn’t replace the plug.

But you said it was tripping the GFCI on all the recep's you tried. How can you be unsure if it's on GFCI if you say it's tripping them? Like sberry asked, is it tripping the GFCI or the breaker?
 
OP
E

EP3

Member
Joined
May 2, 2020
Messages
10
Location
Smyrna, TN
But you said it was tripping the GFCI on all the recep's you tried. How can you be unsure if it's on GFCI if you say it's tripping them? Like sberry asked, is it tripping the GFCI or the breaker?



Just the GFCI on the cord of the washer.
 
To avoid these ads, REGISTER NOW!

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
If the GFCI is tripping as soon as you plug it in, then there's leakage somewhere. You say two-wire; there's no ground from the washer itself? Can you post a link to the replacement plug you bought?
 

bmxr4life87

Well-known member
Joined
Mar 21, 2009
Messages
872
Location
Bixby Oklahoma
Those cord end GFCI units are sensitive to water intrusion. I work for Hotsy and see it from time to time. Occasionally they just **** the bed for no real obvious reason
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,775
Location
East Bay SFO
A friend gave me her light duty Craftsman pressure washer because one of the wheels was off. It had a plug with GFCI built in. That GFCI tripped regularly even though it stayed dry. Since I’m the only user and I always plug into a GFCI protected circuit, I simply cut off the factory plug and changed it over to a high quality replacement plug. Never a problem any more. But I realize that I have voided the UL listing of the machine.
 
Last edited:

Bogie1632

Well-known member
Joined
Feb 18, 2018
Messages
1,303
Location
Southeastern Wisconsin
Just curious, so I'm asking for clarification.

The GGCI tripping as soon as you plug it in, before you turn it on? After plugged in and you reset it, does it run as normal?

Just wondering because I've had many GFCI cord ends that would automatically trip when plugged in (as designed, but I dont recall the manufacturer). Hit the reset button and the devise ran fine until unplugged/plugged back in. Had to have them on all our shop stationary equipment and that's how they all worked. Kinda sounds like what your cord is doing.

Just curious so following this one.

V/R
Bogie
 
Last edited:
OP
E

EP3

Member
Joined
May 2, 2020
Messages
10
Location
Smyrna, TN
If the GFCI is tripping as soon as you plug it in, then there's leakage somewhere. You say two-wire; there's no ground from the washer itself? Can you post a link to the replacement plug you bought?



Nope, just a black wire and a white wire. This washer is double insulated (but that’s above my realm of understanding.)
 
OP
E

EP3

Member
Joined
May 2, 2020
Messages
10
Location
Smyrna, TN
This was the exact plug that was originally on it.

f57f7b2b446c3897c8c3cac77059f513.jpg644537e4d2d888d24bf77dee8803d3ce.jpg
 

Attachments

  • f57f7b2b446c3897c8c3cac77059f513.jpg
    f57f7b2b446c3897c8c3cac77059f513.jpg
    40.4 KB · Views: 1
  • 644537e4d2d888d24bf77dee8803d3ce.jpg
    644537e4d2d888d24bf77dee8803d3ce.jpg
    39.6 KB · Views: 1
OP
E

EP3

Member
Joined
May 2, 2020
Messages
10
Location
Smyrna, TN
Those cord end GFCI units are sensitive to water intrusion. I work for Hotsy and see it from time to time. Occasionally they just **** the bed for no real obvious reason



I can guarantee that the replacement plug had NO water intrusion the one and only time I used it. I was approx. 20 ft away AND around the corner when I was using the washer.
 
OP
E

EP3

Member
Joined
May 2, 2020
Messages
10
Location
Smyrna, TN
Just curious, so I'm asking for clarification.

The GGCI tripping as soon as you plug it in, before you turn it on? After plugged in and you reset it, does it run as normal?

Just wondering because I've had many GFCI cord ends that would automatically trip when plugged in (as designed, but I dont recall the manufacturer). Hit the reset button and the devise ran fine until unplugged/plugged back in. Had to have them on all our shop stationary equipment and that's how they all worked. Kinda sounds like what your cord is doing.

Just curious so following this one.

V/R
Bogie



As soon as I plug it in, it trips before turning it on. Every time I push reset, it trips.

After replacing the GFCI plug, on the cord, it worked perfectly from the start. I used it once for about 45 min. That was weekend before last. Last weekend it wanted to act up again.

I’ve been on 3rd shift this week so I haven’t dealt with it. I’ll get back in to it this weekend. I’m tempted to try putting a regular plug on it like a couple others suggested.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,219
Location
Modesto, CA
Only way to properly diagnose this is to remove the GFCI plug and meter from frame to neutral and see if you get potential.

I assume its on rubber wheels.

If so, then leakage current would have no where to go and thus something else is going on here.
 
To avoid these ads, REGISTER NOW!