problem with house AC, any hvac techs?

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
house A/C is a split system, 7 or 8 years old Ruud with scroll compressor. When it turns on it blows cold for a minute or two then the air becomes room temperature. Outside, the compressor and condensor fan are running. I felt the lines, and the large one is cold when it first starts up but is not cold anymore after a few min. There is a high pitch squealing noise coming from the compressor, not a mechanical noise, but it sounds like liquid flowing.

any thoughts? could it be stuck expansion valve?
 
To avoid these ads, REGISTER NOW!
OP
M

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
update: i went in the attic, the expansion valve was making some funny noises. I noticed one of the capillary tubes from it (the one that goes to the smaller line) had a very sharp bend in it. I straightened that out then the expansion valve started making the normal continuous hiss, but the air still isnt as cold as it was before the problems started.
 
To avoid these ads, REGISTER NOW!

jwillis

Banned
Joined
Aug 24, 2010
Messages
5,225
Location
SW Ohio
It does sound like it might need freon added. (Or whatever they use now days)........jwillis
 

oltruckag

Well-known member
Joined
Aug 10, 2007
Messages
171
Location
*******, GA
Is the coil frosting over? (or frozen solid?)

Take an amp draw on the compressor and compare it to the data plate on the condenser - see if the compressor is really "working".
 

bonneyman

Well-known member
Joined
Apr 22, 2010
Messages
8,857
Location
Desert SW
If the unit has been working OK for 7 or 8 years, and is now working only so-so, I'd have to guess a freon restriction issue.
Thermostatic expansion valves typically have a fine screen at the inlet port - to prevent any small particles from entering the valve and making it malfunction. Even if a system is running perfectly, it still wears. Little particles of metal, winding insulation, carbon, ect. are produced. I'd definitely check the expansion valve screen - it might be clogged. That could account for the many years of working, and only now has the screen plugged up enough to reduce the freon flow to a point that the cooling is insufficient (and it could account for the hissing noise.)
 