Problems with Hydro Smart boiler

tcabinets

New member
Joined
Nov 14, 2014
Messages
1
I installed a Hydro Smart boiler in my shop/garage and it works great except that once in a while it will start to "growl" and make noise in what seems to be the top of the boiler. I found that adjusting/ increasing the pressure seems to fix it temporarily.
The system has 3 zones that I switch on and off depending on the area where I'm working.
Any suggestions.
 
To avoid these ads, REGISTER NOW!

custom1

Well-known member
Joined
Jan 8, 2008
Messages
307
Location
Pa
Welcome.
First guess would be trapped air. Give us some more details and maybe a picture. How long has it been in service and has it done that the whole time?
 
To avoid these ads, REGISTER NOW!

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
You should has some dip switches for exhaust fan speed based on elevation , try setting your elevating dip switch for the next higher elevation.
I believe that will cure your growling issue.
 

JackDiddly

Well-known member
Joined
Oct 6, 2014
Messages
185
Location
SE WI
make sure its not happening when you open a zone that has been closed and cold for awhile. I am not at all familiar with the brand you mentioned, but with the copper fin tube style of heat exchanger dumping cold water into your hot heat exchanger will make some noise and cause some damage, if that were to be the prob you could pipe in a bypass from supply to return to help keep the boiler temp up while operating.
 