this is interesting:
i have recently installed a subpanel in my detached garage. i ran #4 wire from the main panel in the house to the garage. i installed 6 20A circuits on four walls and ran 2 lighting circuits, 1 50A 220V circuit, a garage door circuit, furnace/outdoor lighting circuit. so far it all works great!
i am still deep in the build phase, right now i am working on the walls.
anyway i noticed yesterday that i had an issue with my tablesaw. up until yesterday i have had the TS close enough to the wall that i plugged it directly into the wall. TS is a 10" delta contractor, not a direct drive but a very heavy saw. when i have the TS plugged into the wall (12/2 romex) it starts up in around 1.5 seconds. i had it pulled away from the wall yesterday and had to use an extension cord, so i picked a decent 12/3 50' cable. plugged into this cable the TS starts slow and sounds like its working hard until it comes up to speed, takes maybe 3.5 seconds to fully start.
i'm not really seeing how 50' of 12/3 could cause enough drop to cause this issue. in any case, when the shop is done i wont have the TS located close enough to a wall to plug in directly, so i will need a cable. if 12/3 is causing issue, what cable can i use instead?
i have recently installed a subpanel in my detached garage. i ran #4 wire from the main panel in the house to the garage. i installed 6 20A circuits on four walls and ran 2 lighting circuits, 1 50A 220V circuit, a garage door circuit, furnace/outdoor lighting circuit. so far it all works great!
i am still deep in the build phase, right now i am working on the walls.
anyway i noticed yesterday that i had an issue with my tablesaw. up until yesterday i have had the TS close enough to the wall that i plugged it directly into the wall. TS is a 10" delta contractor, not a direct drive but a very heavy saw. when i have the TS plugged into the wall (12/2 romex) it starts up in around 1.5 seconds. i had it pulled away from the wall yesterday and had to use an extension cord, so i picked a decent 12/3 50' cable. plugged into this cable the TS starts slow and sounds like its working hard until it comes up to speed, takes maybe 3.5 seconds to fully start.
i'm not really seeing how 50' of 12/3 could cause enough drop to cause this issue. in any case, when the shop is done i wont have the TS located close enough to a wall to plug in directly, so i will need a cable. if 12/3 is causing issue, what cable can i use instead?