I have a new compressor with 5hp baldor motor, FLA of 20.6 at 240 volts. Wanting to be NEC compliant, I know I need to be hardwired with a disconnect. I have 8 awg nm feeding the disconnect. I've done some searching and found a Square D D222ncp disconnect at amazon. This is rated for 60 amps and is a 2 pole 240 volt interior disconnect. What has me scratching my head is the following at Square D:
3 HP per NEC 240.6 or
10 HP per NEC 430.52.
Can somebody tell me if this means it is capable of 3 or 10 hp? If only 3HP, can someone point me to a 5hp capable disconnect?
If this disconnect is ok, I was thinking of using 40 amp dual element time delay fuses. I have lots of 8 awg THHN and will use this in flexible conduit from the disconnect to the compressor.
Thanks!
3 HP per NEC 240.6 or
10 HP per NEC 430.52.
Can somebody tell me if this means it is capable of 3 or 10 hp? If only 3HP, can someone point me to a 5hp capable disconnect?
If this disconnect is ok, I was thinking of using 40 amp dual element time delay fuses. I have lots of 8 awg THHN and will use this in flexible conduit from the disconnect to the compressor.