Hey guys I'm getting the 2-2-4-6 mobile home feeder wired up to my shop, I have a 6x6 junction box attached to the house that I'm using to splice the copper conductors from my main panel to the aluminum MHF feeding the shop.
I'm using a greaves insulated connector USAD2-2 for the connections, the installation instructions for the connector says to torque to 130 inch-pounds, however I tried this on a test piece of #2 aluminum using my new torque wrench set to 130 inch-points and the lug went straight through the wire before it reached 130 inch-pounds. What do you guys torque #2 aluminum conductors to?
Greaves connector installation instructions.
On another note, my siemens panel said to torque the A and B lugs to 110 inch-pounds, however on the main breaker in the panel it said 55, so I used 55 which seemed plenty tight. I don't see how aluminum can be torqued to 100+ inch-pounds. What's the deal?
Any comments on my panel installation and wiring so far? Thanks guys.
I'm using a greaves insulated connector USAD2-2 for the connections, the installation instructions for the connector says to torque to 130 inch-pounds, however I tried this on a test piece of #2 aluminum using my new torque wrench set to 130 inch-points and the lug went straight through the wire before it reached 130 inch-pounds. What do you guys torque #2 aluminum conductors to?
Greaves connector installation instructions.
On another note, my siemens panel said to torque the A and B lugs to 110 inch-pounds, however on the main breaker in the panel it said 55, so I used 55 which seemed plenty tight. I don't see how aluminum can be torqued to 100+ inch-pounds. What's the deal?
Any comments on my panel installation and wiring so far? Thanks guys.