Pulling 7 #12 through 1/2" EMT

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
Will pulling 7 #12 THHN conductors through 1/2" EMT be difficult. Will lube be required.

Any tricks?

Thank You
John
 
To avoid these ads, REGISTER NOW!

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,674
Location
Maine
Pulling depends on length of run and more importantly how many bends. Its easy to pull seven #12 in a short run, make it longer and it might not be. Not sure I've heard of or ever seen anyone use lube to pull into 1/2 emt.
 

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
7?
would that be 3 120v circuits (3 blk, 3 wht and a ground)?
just asking for my own knowledge.
I am thinking of running (2) 220 circuits (4- 12ga wires + ground), but wasn't sure about conduit fill
 

Delta74

Well-known member
Joined
May 6, 2011
Messages
320
Location
Peachland B.C. Canada
it should pull thrue, not sure about your fill thou, think you may be over, but yea lube can help if there are lots of bends or long pulls, just use a proper wire lube, not whatever you have handy, HD sells it along with most other places, its been designed to not break down the insulation on the wires, its probably too late now, but I know when we do long runs on a commercial job, we will often dump some lube in the conduit as we are doing the runs in places we know will give us problems.

and agree, I hate 1/2 inch, I try to avoid it whenever possible and upsize to 3/4, just in case.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Anything over two bends and some distance you will have trouble doing it by yourself, if you can have someone push the wires as you pull them. If you can run 3/4 emt. How many bends do you plan on having.
 

rev1

Well-known member
Joined
Sep 30, 2009
Messages
92
Location
Oklahoma, Oklahoma, . . .
laser, Someone else can jump in but for 220~240 circuits, I'd recommend 10 ga. I'm planning on using 12ga for my 120v circuits and 10 ga or maybe even 8 ga for my 240v circuits.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,000
Location
Minneapolis
You need to go to a 3/4" conduit for that many #12 wires, 1/2" is too small. You didn't mention what the wires are for so I can't comment on whether you have to consider derating them for current carrying capacity.
 

PRH44

Well-known member
Joined
Dec 25, 2009
Messages
563
Location
Indiana
(9) #12 THHN is the max by code. Not a smart thing to do in 1/2" but legal. I normally cut 1/2" off after (4) #12 conductors. You can pull (7)#12 in a 1/2" pending bends (360 max between boxes) length and your ability to feed the wire and serve the head on the fish tape. I would recommend 3/4".

The best way to insure a successful install is minimum bends and square cuts that are reamed smooth.
When pulling wire the three most important things are a good feed, a smooth staggered head and steady pull strokes. You would be amazed at how much more difficult a pull becomes when the wire is fed incorrectly and your timing is off . One should group the conductors avoid crossing and basically push it into the conduit. Usually the Apprentices job.
You pull with 2' to 3' strokes allowing the feed man to reposition for the next push between strokes.
Its amazing how fast and easy you can pull wire with two guys that develop timing. You develop codes like two taps on the pipe with your linesman pliers when you are ready to pull. Listen for two taps from the feed man when his ready to take off . Use multiple taps for a stop in case you get tangled up.

Normal the minimum I use is 3/4", I use 1/2 when necessary like jumps between can lights with boxes that have 1/2" KO, single switch drops, single circuit devices etc. More often than not our minimum specification on projects is 3/4"
 

volleyball

Well-known member
Joined
Aug 29, 2011
Messages
4,127
Location
NY, not NYC
I say get your 7 wires and pull it through a section of 1/2" to get a feel for it. Nothing wasted and you know before you try it. I agree the upcharge to 3/4 is nothing.
 

PRH44

Well-known member
Joined
Dec 25, 2009
Messages
563
Location
Indiana
If 9 is legal he is well under with 7. I probably wouldn't plan it that way but if its the way is is then its fine too.

He is perfectly legal. (7) #12 THHN " STRANDED" in a 1/2" conduit CAN pull fine and have no problems if you set up correctly. Depends on your ability not to cross them up when feeding, keeping them straight and smooth is paramount. I can see an inexperienced person getting into difficulty with this. You twist them while feeding ....it will go south in a hurry.
Damaging the conductors is very possible. Hence the reason I recommend 3/4"
 

m.b.0331

Well-known member
Joined
Nov 22, 2013
Messages
70
Location
Maryland
+ 1 more for upping to 3/4". It's slightly more expensive (but still close to nothing) and sure you may not have a 3/4" bender, but you'll be glad you upgraded.

Make sure your pull head is as small and tight as possible. Some guys insist on stripping out every conductor and hooking them all through the fishtape or string...this makes them not pull off easily, but with a head that big you won't be able to pull worth a damn. I would strip 2 or 3 out, loop them through, and stagger the other wires on to them. Don't use too much tape, and make sure the tape you do use is pulled tight as possible.

Like PRH44 said, work together with a partner and your pull will go easier. If you can't grip your fishtape with your hands, use your pliers to grip it. There's no need to go buy a $40 pair of Kleins with a built-in fishtape puller, any linemans pliers worth their salt will be able to grip a fishtape right under the rivet, opposite the cutting edges.
 
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
Thanks for the replies everyone. I just realized that this will be a no go due to box capacity limitations of 18 cu. I'm calculating even 2 120V circuits with one ground cannot pass threw an 18 cu box with a device.

I will need to find a way of getting a 21 cu box or larger just for 2 circuits with one passing through.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Use a 4 square deep, the 2 1/8" deep one. You're also forgetting the raised cover you use will add some box volume as well.

Take a look at this list, you can see the cubic inch volume of each different cover. Not that it matters, a 4 square deep and a raised cover will give you lots of room, but you can see for yourself how much it adds.

https://www.platt.com/platt-electri...ID=34&CatID=1105&SubCatID=2866&navPage=2_16_0
 
To avoid these ads, REGISTER NOW!
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
Yes I am aware of those, but not to sure if they will fit in my corrugated steel panels. I am fast coming to the conclusion my boxes will need to be surface mount with 4" square like those.
 

mobiledynamics

Well-known member
Joined
Mar 14, 2010
Messages
5,034
Location
Gotham City
600SL - FWIW, they make even bigger boxes. Can't recall what I have in my stash but a 4" by 3 1/4'ish deep exist. It's DEEP...
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Don't forget, code requires you to derate by 20% with 4-6 conductors, 30% for 7-9 & 50% for 10-20...

Tommy
 
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
Don't forget, code requires you to derate by 20% with 4-6 conductors, 30% for 7-9 & 50% for 10-20...

Tommy

Yes my understanding is that 12THHN is good for 30 amps. Therefore I should be able to go up to 9 conductors on a 20 amp circuit.
 
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
600SL - FWIW, they make even bigger boxes. Can't recall what I have in my stash but a 4" by 3 1/4'ish deep exist. It's DEEP...

The ideal box is a 3x2 old work box that can be screwed right to the steel wall panels and covered. Would require 21 cu to pass a second circuit through it. There fore I need 4" deep. :dunno:

4" square boxes will just barely fit between the corrugation's of the steel panels but I cant put a cover over them and I would have to make mounting flanges for each box that would not be covered. So it would end up looking like a hacked out hole around the box. At this point its starting to look like putting the boxes on top of the steel is the way to go.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Yes my understanding is that 12THHN is good for 30 amps. Therefore I should be able to go up to 9 conductors on a 20 amp circuit.

Yes my understanding is that 12THHN is good for 30 amps. Therefore I should be able to go up to 9 conductors on a 20 amp circuit.

OK, I didn't k now what your intended current capacity was going to be. THHN is indeed rated for a max of 30A. Your math on the derating is good, you end up with a max of 21A.

12 THHN is rated for 30A, but the max allowable current rating of the circuit changes based on code. Code 110.14(C) generally limits it to 25A and code 240.4(D) often limits the protection to 20A. 240.4(G) lists the types of circuits where 12 AWG can be protected above 20 amps.

Tommy
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I got some hack around boxes, I could go back and finish it a little, if I was worried I might come up with a simple way to trim them out from flashing.
 
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
OK, I didn't k now what your intended current capacity was going to be. THHN is indeed rated for a max of 30A. Your math on the derating is good, you end up with a max of 21A.

12 THHN is rated for 30A, but the max allowable current rating of the circuit changes based on code. Code 110.14(C) generally limits it to 25A and code 240.4(D) often limits the protection to 20A. 240.4(G) lists the types of circuits where 12 AWG can be protected above 20 amps.

Tommy

Thanks

All these little branches in the code are driving me nuts. I'm beginning to regret purchasing the 2014 code in hard copy over a searchable PDF on CD.
 
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
I got some hack around boxes, I could go back and finish it a little, if I was worried I might come up with a simple way to trim them out from flashing.

I could do some reasonable trim work but I have about 30 of these boxes to install. I really starting to warm to the idea of running the conduit and boxes outside the walls.

John
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
Nothing to go crazy about, just run the pipe and boxes and pull the wires, you don't even have to pull a ground if you use the emt as a ground, just ground tails from back of box to outlet. Are you just having 120 volt circuits and how many outlets.
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
I could do some reasonable trim work but I have about 30 of these boxes to install. I really starting to warm to the idea of running the conduit and boxes outside the walls.

John

If pipe is nice and straight it doesn't look bad at all on the outside of the wall.
 
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
If pipe is nice and straight it doesn't look bad at all on the outside of the wall.

Absolutely, but for non dedicated circuits it also tends to get in the way of things like shelving etc. So it looks like the best bet is to come down from the ceiling with each box with two conductors plus ground in 1/2" EMT to the shallowest 4" box available. 12cu total or 21cu for double duplex assuming I run a ground.
 