Pulling cable

engineer2

Well-known member
Joined
Dec 13, 2009
Messages
11,797
Location
Chicago burbs
Is 8-3 UF-B cable pretty easy to pull? I'm looking and about 55 ft of EMT, an LB, and 30 ft of underground RMC with a couple of elbows, all in 3/4". I can always pull it in sections.

Wanted to go with more power to my shed, but #4 or #6 copper wire is damn expensive, so two 20 A circuits it is.
 
To avoid these ads, REGISTER NOW!

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
I would of ran a bigger pipe myself,but if that's what you've got to work with I guess your stuck with it.
Thhn/thwn would be a hell of a lot easier to pull in,either way I'd soap the hell out of the wire and make sure to make sure the guy pushing keeps up.
You might want to swap the lb for a j box to male things easier also.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,883
Location
NJ
I would of ran a bigger pipe myself,but if that's what you've got to work with I guess your stuck with it.
Thhn/thwn would be a hell of a lot easier to pull in,either way I'd soap the hell out of the wire and make sure to make sure the guy pushing keeps up.
You might want to swap the lb for a j box to male things easier also.

^^^^^this. Also if you are only going with 20a circuits, you can drop down to #10's. Even 12's if you dont expect to really be close to 20a on either circuit.

I would not pull uf thru conduit. PIA.

You will also need a two pole cb and some type of disconnect in shed.

Gfci protection as well for receptacles.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
^^^^^this. Also if you are only going with 20a circuits, you can drop down to #10's. Even 12's if you dont expect to really be close to 20a on either circuit.

I would not pull uf thru conduit. PIA.

You will also need a two pole cb and some type of disconnect in shed.

Gfci protection as well for receptacles.

:thumbup::thumbup::thumbup::thumbup:
 
OP
E

engineer2

Well-known member
Joined
Dec 13, 2009
Messages
11,797
Location
Chicago burbs
Thanks for the help!!
I have a full bottle of lube. Wife will be pushing or maybe pulling. She's done it before, but doesn't like working around a live panel.

I might do 3 #8 THHN's and a #10 ground (is #10 ground OK? I didn't look it up) and it might be cheaper. Ground wire is redundant with EMT.

I thought aluminum was a no-no underground. We are essentially Chicago electrical code (EMT) and aluminum wire is discouraged (except for service entrance). No permit unless my ******* neighbor calls.


2 pole 40 Amp in main panel.

I suppose I could run 3/4" though the basement and 1" outside, but if THHN pulls OK, 3/4 throughout it is.

LB will be where it exits the rim board. It is waterproof and I think it is appropriate for that.

RMC is so I only have to dig down 6" or so.

2 x 20 A QO's in shed, ground rod, GFCI's according to code.

Trying to keep cost and PITA factor in check.
 

tyme2par4

Well-known member
Joined
May 16, 2016
Messages
571
Location
NH
Aluminum SER is not allowed underground, but Al THWN or MHF is used underground all the time.
 

pentavolvo

Well-known member
Joined
Sep 6, 2010
Messages
584
Location
Indiana
If you only intend to put 2 20 amp breakers in she'd then put a 20 in panel and pull 12 gauge, 10 if you want
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,715
Location
NW Iowa
No one has adressed the fact that 8-3 UF isn't going to fit in 3/4" conduit of any kind. UF is flat, I would say 8-3 is an inch or more wide.

As others have mentioned if you have a complete conduit from one panel to the other, individual conductors is the way to go.
Copper and aluminum can both be run underground as long as you use the correct type of wire.
Aluminum is preferred by many due to it's low cost and if you pay attention to a few small details it is just as reliable as copper.

If you do choose to use aluminum I would use either thwn or xhhw depending on what you have available. Since you are planning on conduit the whole way I wouldn't use a cable like the mobile home feeder since it will be harder to pull, but many do pull it into conduit regardless. Usually individual conductors and MHF are pretty comparable as far a price goes.
 

ducksface

Banned
Joined
Oct 25, 2012
Messages
2,477
I quit pulling u less forced.
Too easy to pull it as you build conduit.
Do ten feet, glue, do ten feet. So easy.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,715
Location
NW Iowa
I quit pulling u less forced.
Too easy to pull it as you build conduit.
Do ten feet, glue, do ten feet. So easy.

That completely defeats the point of running conduit. If you have to put the wire in as you assemble it then you probably won't be able to get it back out or new wire in if the need arises.

It is against code for that very reason.
 

ducksface

Banned
Joined
Oct 25, 2012
Messages
2,477
This is advice to a homeowner on a small project.
If you think having the wife pull and a fail happens, and There is an all time easy, no fail way to get that wire in, is a code violation instead of a common sense type fix....

And, per your scenario:
If he can't get it out because of a bend, he couldn't have pulled it in the first place.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,883
Location
NJ
This is advice to a homeowner on a small project.
If you think having the wife pull and a fail happens, and There is an all time easy, no fail way to get that wire in, is a code violation instead of a common sense type fix....

And, per your scenario:
If he can't get it out because of a bend, he couldn't have pulled it in the first place.

Op said he was running grc so he only had to dig 6".

You think spinning grc into couplings and spinning 90's on it is gonna save the wires:eyecrazy:

I'll meet you 1/2 way with a drag line but that's it.

Op needs to finalize what he wants (panel/no panel, size, ......) and provide a sketch of the job and/or pics and people here will detail out what he needs to do it correctly and easily. That simple!
 
To avoid these ads, REGISTER NOW!

ducksface

Banned
Joined
Oct 25, 2012
Messages
2,477
I'll take half way.
Thanks.

I use mule tape for just about every job imaginable. I keep a couple hundred feet in each vehicle.
Love that stuff.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Is 8-3 UF-B cable pretty easy to pull? I'm looking and about 55 ft of EMT, an LB, and 30 ft of underground RMC with a couple of elbows, all in 3/4". I can always pull it in sections.

Wanted to go with more power to my shed, but #4 or #6 copper wire is damn expensive, so two 20 A circuits it is.

You do realize that #8 NM is rated for 40a?
 

RivennHewn

Well-known member
Joined
Jun 4, 2011
Messages
10,370
Location
PNW
I'll take half way.
Thanks.

I use mule tape for just about every job imaginable. I keep a couple hundred feet in each vehicle.
Love that stuff.

I just picked up a spool from a job where it was in the dumpster. Wonderful stuff to have in the truck box.
 

ducksface

Banned
Joined
Oct 25, 2012
Messages
2,477
I didn't know about it until about 30 years ago.
The Tucson power company let their guys make only one pull with it and then discarded it.
An uncle brought me a couple of hundred feet and it's been a staple ever since.

I use amsteel for small diameter home/offroad needs and mule for others.
Paracord is bandwagoneer junk compared to those two.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,125
Location
SE MI
I don't know why anyone would use UF-B if the are laying conduit. #8 THWN is $0.33/ft (times 4) so at $1.32/ft it is less than 8-3 UF-B.

Not sure if you can pull 4 #8 through a 3/4" conduit or if you need 1".
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
I don't know why anyone would use UF-B if the are laying conduit. #8 THWN is $0.33/ft (times 4) so at $1.32/ft it is less than 8-3 UF-B.

Not sure if you can pull 4 #8 through a 3/4" conduit or if you need 1".

Why would you suggest 4 8 AWG conductors? Only 3 -8 AWG, & 1-10 AWG green is needed, but the neutral conductor has to be white, taping a grounded (neutral) smaller then 4 AWG is prohibited.
 
OP
E

engineer2

Well-known member
Joined
Dec 13, 2009
Messages
11,797
Location
Chicago burbs
Only 3 -8 AWG, & 1-10 AWG green is needed, but the neutral conductor has to be white,
That's what I'm planning.
I've abandoned the idea of UF. BTW, UF comes flat or round.
Stranded THHN is cheaper and should be easier to pull.
95 foot total distance, so #8 is the recommended size.
You can put 6 #8 in 3/4" so I should be OK.
Two 120 VAC 20 Amp circuits.
No plans for a 220 outlet, but I wouldn't rule it out in the future with the appropriate changes.
Had one of those 4am thoughts and someone here also brought it up: If I have 90° elbows on each end of the GRC, how the hell do I screw it all together? One end goes under the shed the other under a walkway so I can't just lay it in the trench. I'll have to find a GRC union, but doubt any big box store sells them.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,883
Location
NJ
That's what I'm planning.
I've abandoned the idea of UF. BTW, UF comes flat or round.
Stranded THHN is cheaper and should be easier to pull.
95 foot total distance, so #8 is the recommended size.
You can put 6 #8 in 3/4" so I should be OK.
Two 120 VAC 20 Amp circuits.
No plans for a 220 outlet, but I wouldn't rule it out in the future with the appropriate changes.
Had one of those 4am thoughts and someone here also brought it up: If I have 90° elbows on each end of the GRC, how the hell do I screw it all together? One end goes under the shed the other under a walkway so I can't just lay it in the trench. I'll have to find a GRC union, but doubt any big box store sells them.

Your description of your job scope has been confusing to me and others.
You are putting in a subpanel and then from that you are running two 120 VAC 20 Amp circuits.
You also need 2 rods and gfci's on recept ckts.
Max 6 throws of hand for the disconnecting means.
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
I ran 7 or 8 #6 THNN wires or was it THWN wires in a 1 1/2 GRC outdoor it is fine even with one LB... the other 90deg are sweeps elbows....it is fine... the painful one is when those elbows are too close to each other.... within less than 4 or 5 foot before another turn.... that section is painful no matter what lubes you used... so plan your wiring with the minimum amount of bends close to each other..... if possible...
 
OP
E

engineer2

Well-known member
Joined
Dec 13, 2009
Messages
11,797
Location
Chicago burbs
Sorry, but I couldn't resist....I stopped myself 6 times
Just seeing if you guys are paying attention... and you are.

Sketch to help 'splain things. Want it to be to code. 1 ground rod is the norm around here because of our wet soil. Thanks for everyone's help so far. #8 because of the distance, per code, I believe. Possible future upgrades too.
 

Attachments

  • shedelectricrouting.jpg
    shedelectricrouting.jpg
    113 KB · Views: 32

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,125
Location
SE MI
OP
E

engineer2

Well-known member
Joined
Dec 13, 2009
Messages
11,797
Location
Chicago burbs
My local pricing for 100 ft:
THHN: 3x#8 + 1x#10 = $130.
2-2-2-4 MHF: @ 1.62 /ft = $162, but then I can have 100 amp service which is probably overkill.
Just need to run a table saw or a miter saw and some lights and maybe a small heater. No plans to do welding in a wooden shed.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Just seeing if you guys are paying attention... and you are.

Sketch to help 'splain things. Want it to be to code. 1 ground rod is the norm around here because of our wet soil. Thanks for everyone's help so far. #8 because of the distance, per code, I believe. Possible future upgrades too.

Are you saying you need #8 for 2x 20a(20a on each leg) circuits because of 55' distance?

If so, youre way off.

@ 55' you should be able to do 50a with #8 cu no problem.

BTW there is no NEC code for a certain maximum distance or voltage drop.

Maybe you have a local amendment??

My local pricing for 100 ft:
THHN: 3x#8 + 1x#10 = $130.
2-2-2-4 MHF: @ 1.62 /ft = $162, but then I can have 100 amp service which is probably overkill.
Just need to run a table saw or a miter saw and some lights and maybe a small heater. No plans to do welding in a wooden shed.

#2 al is limited to 90a in this application.
 
Last edited:
OP
E

engineer2

Well-known member
Joined
Dec 13, 2009
Messages
11,797
Location
Chicago burbs
95 ft, not 55 ft. I used a few online tables. Google "wire sizing calculator". Maybe they are too conservative.
 
Last edited:
OP
E

engineer2

Well-known member
Joined
Dec 13, 2009
Messages
11,797
Location
Chicago burbs
Thanks for your input. Project has been but on hold. We just found out our income tax plus property taxes are going up $300 per month. Welcome to Illinois where you get the shaft so state employees can have a glorious retirement, or I'm making a new car payment for some state employee.
 

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
13,726
Location
Lebanon, TN
Thanks for your input. Project has been but on hold. We just found out our income tax plus property taxes are going up $300 per month. Welcome to Illinois where you get the shaft so state employees can have a glorious retirement, or I'm making a new car payment for some state employee.

Vote with your feet. It might be time to get the hell out of that state like so many others are doing. Most are leaving for the same reasons you just stated. If they don't turn things around soon, your property values are going to plummet - just like Detroit did. Now might be the time to sell and relocate before the values crash. I take it by your posting name that you are an engineer, they are in demand everywhere right now.