I've decided to go with electric heat, a Northern Tool blower mounted unit that requires 240v. My garage is detached, 25 ft from house and has 110v already run.

Friend who is a former electrician said maybe we could pull more wire thru and not have to trench the 25. So, I just went out and checked the first outlet box and found shielded cable thru 1/2" conduit.

Is it possible to pull the old shielded cable out and run new for the 25' distance from house to garage?

Anyone ever do this before?

Thanks,
Trent
 
To avoid these ads, REGISTER NOW!

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,453
Location
East Bay SFO
How many bends?

Let's wait for some sparkles to respond ...

I've never done it but based on my limited amateur experience pulling wires through 1/2 inch conduit, I would bet against it. Maybe with a winch or come along?
 

Marctrees

Well-known member
Joined
Mar 5, 2015
Messages
6,265
Location
TX/LA border - Toledo Bend
If it's electric heater of any decent size, , 1/2" will be too small.

Legally, and realistically both.

You already said 240, but we also need the Amps to determine wire and conduit size.

If it's not a big one, like needing only #10, or even #8 THHN, possibly you could sneak by.

With nothing else in that conduit of course.

Get those specs posted, THEN a real Sparky will give you answer.

Just a link to your chosen heater should do it.

And figure on using your old cable as the puller.

I will add, you may need someone w conduit pulling experience to get it done.

Sometimes, not as simple as one may think, dealing w tight pulls, tying on correctly, and often using wire pulling lube. Marc
 
Last edited:

racingtadpole

Well-known member
Joined
Dec 3, 2011
Messages
2,029
Location
The far side of crazy.. but sometimes Australia
If my understanding is correct, 1/2" conduit is 1/2" ID. Being only 1/2" you will probably find you cant even pull the old cable out because the conduit was fed onto the cable as it was laid. If you do manage to pull the cable out with a draw string attached, it wont be a very big string, which will make it difficult to pull a larger cable in with. And if it was fed over the cable as it was laid, it may very well have right angle bends instead of swept elbows...

No idea what the digging will be like at your property, but for 25' I would pretty much guarantee that it will be easier than messing with your old conduit.

I would put in a much larger conduit, and also lay a capped spare with a draw rope inside the same trench.

Of course I'm not an American electrician, so take it with a pinch of salt
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
If my understanding is correct, 1/2" conduit is 1/2" ID. Being only 1/2" you will probably find you cant even pull the old cable out because the conduit was fed onto the cable as it was laid. If you do manage to pull the cable out with a draw string attached, it wont be a very big string, which will make it difficult to pull a larger cable in with. And if it was fed over the cable as it was laid, it may very well have right angle bends instead of swept elbows...

Of course I'm not an American electrician, so take it with a pinch of salt

It's a code violation to pull the wire as you assemble the conduit. The conduit has to be assembled first, then the cable pulled. Of course, that doesn't mean the job was originally done to code.

If what the OP means by "shielded cable" is some kind of data line, it should be simple to tie a pull line to it and remove the old cable and get the new pull line ine. That being said, 1/2" is not going to be receptive to pulling any real heavy lines.

Tommy
 
Last edited:

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
It's just a suggestion, I know you just want to run the wiring for the heater, but if I were you I would consider some other options. Since it is only 25 ft you could rent one of those trench digging machines and be done digging a new trench in a fairly short period of time. Then you could run more than one conduit, one for the electrical line and if you want, run a conduit for cable TV and a Cat-6 cable for Internet. You could even run wiring for a home phone and/or an intercom.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,687
Location
NW Iowa
Everybody is assuming that the run is all in conduit. It sounds like the wire is UF and I'm not sure OP has checked it out enough to be sure.

If you can move the wire you could try to pull in some #8's and set a 50A sub-panel in the garage. Of course that's assuming it's something like a 5kw heater anything bigger and it doesn't leave much room to run power tools.

If none of our suggestions work out 25' really isn't very far to dig. At 25' forget a trencher just get out your spade.
 
Last edited:

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
Everybody is assuming that the run is all in conduit. It sounds like the wire is UF and I'm not sure OP has checked it out enough to be sure.

If you can move the wire you could try to pull in some #8's and set a 50A sub-panel in the garage. Of course that's assuming it's something like a 5kw heater anything bigger and it doesn't leave much room to run power tools.

If none of our suggestions work out 25' really isn't very far to dig. At 25' forget a trencher just get out your spade.

I believe he will need to pull a ground. 3 #8 and 1 #10 will not go into 1/2".
 

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
Everybody is assuming that the run is all in conduit. It sounds like the wire is UF and I'm not sure OP has checked it out enough to be sure.

If you can move the wire you could try to pull in some #8's and set a 50A sub-panel in the garage. Of course that's assuming it's something like a 5kw heater anything bigger and it doesn't leave much room to run power tools.

If none of our suggestions work out 25' really isn't very far to dig. At 25' forget a trencher just get out your spade.
Not trying to be a jerk, but the thread title is "Pulling Shielded Cable thru 1/2" rigid conduit" so just what else are we supposed to think?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,687
Location
NW Iowa
Not trying to be a jerk, but the thread title is "Pulling Shielded Cable thru 1/2" rigid conduit" so just what else are we supposed to think?

I guess it sounds like his shielded cable is UF and he hasn't tried to pull it yet. I was just suggesting that it might not be ran in conduit the whole way. The rigid could just be a sleeve where the wire emerges. If he hasn't checked into it very far he might not know for sure.

I'm not trying to say it's the only possibility, just one that had not been mentioned yet. I also gave input that could be helpful if the pipe IS ran the whole way.

I believe he will need to pull a ground. 3 #8 and 1 #10 will not go into 1/2".


Since the majority of his load will be a 240v heater he could down size the neutral to a #10, giving a total of 2 #8's and 2 #10's. Definitely not an ideal pull but it could work.
 
Last edited:

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
If it were me and I was running a new cable out to the garage, I would run a cable capable of handling 100 amps. My thinking is, if I am going to spend the time and the money to do this, I may as well do it so in the event that at some point in the future I want to add more equipment in the garage, I would have the available power to do it. We are only talking about a 25 ft run so the cost difference between the wire sizes shouldn't be all that terrible.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,845
Location
NJ
Unfortunately, you will need a subpanel as this heater makes you exceed the one permitted circuit to a detached building.
i.e. - 3 conductors plus ground, subpanel with unbonded neutral block, ground block added, 2 ground rods. need main cb in subpanel if you ever plan to be over 6 throws of hand.
 
OP
E

E30bimmer

Well-known member
Joined
Dec 1, 2009
Messages
79
Location
Chicago
Okay then, lots of opinions here. My buddy is coming over shortly to take a look at the situation and will post a follow up, but I'm kinda leaning toward running a new line(s) and 100A subpanel, even though heater only requires 30A. I like the option of being able to run cable internet out there. Using a network extender now and will sometimes drop the connection.

The thought trying to pull existing through the conduit and then getting stuck isn't ideal obviously.

This is the heater info btw:

http://www.northerntool.com/shop/tools/product_595_595
 
To avoid these ads, REGISTER NOW!
OP
E

E30bimmer

Well-known member
Joined
Dec 1, 2009
Messages
79
Location
Chicago
How about a picture of the wire that's in the conduit so we can settle that part of the question?

It's just Romex. I decided that I'm going to wait til warmer weather and run a new 1" conduit and cable to provide for the heater, cable internet, air con, frig, compressor, etc.

Always go big as they say.

Thanks for the input guys.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,845
Location
NJ
It's just Romex. I decided that I'm going to wait til warmer weather and run a new 1" conduit and cable to provide for the heater, cable internet, air con, frig, compressor, etc.

Always go big as they say.

Thanks for the input guys.

I hope this means that you plan to provide power for a new subpanel in the garage and not running several circuits out to the detached garage. If you care about being NEC complaint, you need the sub panel. Since you are planning to spend $ for improvements, it is better to spend it properly and be up to code so it doesn't haunt you later.

Also you should run the internet/low voltages/comms wirirng in a seperate conduit.
 

73RR

Blank Email
Joined
Dec 13, 2016
Messages
300
Location
Central Ory-Gun
If you are trenching for a 1" tube then step up to at least 2" and then not have to worry later about how to get something else to the shop.
You already have the trench so the 2" pipe is only a small upcharge.
 
OP
E

E30bimmer

Well-known member
Joined
Dec 1, 2009
Messages
79
Location
Chicago
I hope this means that you plan to provide power for a new subpanel in the garage and not running several circuits out to the detached garage. If you care about being NEC complaint, you need the sub panel. Since you are planning to spend $ for improvements, it is better to spend it properly and be up to code so it doesn't haunt you later.

Also you should run the internet/low voltages/comms wirirng in a seperate conduit.

Yes.
 

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
Okay then, lots of opinions here. My buddy is coming over shortly to take a look at the situation and will post a follow up, but I'm kinda leaning toward running a new line(s) and 100A subpanel, even though heater only requires 30A. I like the option of being able to run cable internet out there. Using a network extender now and will sometimes drop the connection.

The thought trying to pull existing through the conduit and then getting stuck isn't ideal obviously.

This is the heater info btw:

http://www.northerntool.com/shop/tools/product_595_595
I would say that is a very wise thing to do. It meets your current needs and it gives you plenty of power for future equipment should you need it.
 

royalton10

Well-known member
Joined
Oct 19, 2007
Messages
247
Location
Lancaster, Ohio
Don't do the 1" conduit. Go bigger. You could do a conduit for the sub panel, conduit for internet, and a spare. Overkill, yes! But you already have the trench opened. Use that to your advantage. Only 3 sticks of conduit for the trench.


Sent from my iPhone using Tapatalk
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
+1 for . . . . . . Do It ONCE, Do It Right !! ;)

Dig out portion next to house and garage to see what EXACTLY you have now. More than likely that 1/2" conduit it only useful for future low-voltage wires like CATV, Internet, Security, Phone, etc. Even at 1/2" it will be pretty skimpy. Eventually you'll need to remove that power, as garage can only have ONE source of power.

RE-TRENCH the 25' and put in 2" buried conduit for subpanel you'll add in garage. The "GJ economy" setup could include MHF (mobile home feeeder) aluminum 2-2-2-4 that will get you 90A at the garage at only $1.50/ft. Put in 100A subpanel with plenty of spaces for garage, and 90A breaker in house to feed the garage through MHF wire. Extra thing you need to do is also run the MHF wire in conduit all the way inside garage to the subpanel, along with conduit in house to main panel.

Sparky's will give you Copper option wire size as well.
 