A couple of things to be aware of:
Max pulling tension on a typical CAT6 cable is 25 lbs. Cable weights run around 25lbs/1000', so at the end of your pull, you have about 19 lbs of pulling tension available.
Testing for CAT6 goes well beyond just continuity as well.
Per TIA/EIA standards, a maximum of (2) 90 degree bends are allowed for a data run (mind you, these are standards, not code...)
Non gel-filled plenum and non-plenum cables will not survive in a wet environment; I've had projects where even new dry water blocked indoor/outdoor cables that were pulled through wet conduits failed immediately after installation. That cable is no longer manufactured as a result...
In my professional opinion (Registered Communications Distribution Designer), your best solution is to lay a couple of outside plant rated (direct burial) cables in the trench before backfilling. Use armored cable if you have a rodent potential.
One more thing, OSP (outside plant) cable cannot be run more than 50' inside a building outside of conduit (per the NEC) unless it's a listed (UL) cable such as:
http://ce.superioressex.com/uploadedFiles/Docs/PDF/Catalogs/Communications/OSP-Broadband-IO.pdf
Hope this helps...