Pump HP and Amperage

bmwpower

Super Moderator
Staff member
Joined
Apr 24, 2005
Messages
12,578
Location
NJ
Looking at sump pumps...found 2 pumps... both 1/2 HP, but one nametag said 13 amps and the other said 6.5 amps. Both 110v units. Is it possible to have 2 pumps, both with the same HP rating, so different in amperage?
 
To avoid these ads, REGISTER NOW!

Jaguar Fan

Well-known member
Joined
Mar 13, 2008
Messages
5,508
Location
Park City for Ski Season; Las Vegas for Poker Seas
I don't think so.

1 horsepower = 745.699872 watts, according to a quick google search.

So, 1/2 HP should be ~327.85 watts.

Watts = volts * amps

so... the 1st pump is 13 amps x 110 volts = 1430 watts
and the 2nd pump is 6.5 amps x 110 volts = 715 watts

I think it takes some creative rounding to make either one of them a 1/2 HP pump. Maybe those amperages listed are peak at startup but the motors each drop down significantly for sustained operation (I'm just making this up - don't know if its true).

But maybe someone who is more knowledgeable can correct me.
 
Last edited:
OP
B

bmwpower

Super Moderator
Staff member
Joined
Apr 24, 2005
Messages
12,578
Location
NJ
Interesting. Not sure how this is possible. Was going to ask the guy at Home Depot, but...

Check out this TSC listing...

This 3/4 HP* corrosion-resistant automatic submersible sump pump comes with a heavy-duty, energy efficient motor only 7.5 amps, a built-in check valve and 8 ft. power cord
......
*As rated by engine manufacturer
 
Last edited:
OP
B

bmwpower

Super Moderator
Staff member
Joined
Apr 24, 2005
Messages
12,578
Location
NJ
There are a lot of "funny" HP ratings used on consumer products.

In the case of the 1/2HP pumps you mentioned in post #1 it is highly likely there is some misprint caused by translations from Chinese and metric units.

Check out this pump:
http://www.grainger.com/Grainger/items/3XU84?Pid=search
Item number 3XU84

The pedestal pumps are more $$$ but they last a long time.

That pump look awesome, but 5 bills...ouch. TEFC motor would be nice.

Actually, at Home Depot I think the pedestals were a little cheaper.

Is yours noisy?
 
To avoid these ads, REGISTER NOW!

Torque1st

MEMBER EMERITUS
Joined
Sep 14, 2008
Messages
5,668
Location
KC Metro, Kansas
I can hear it because the pump bearings are a mite worn. Most of the noise is from the pump not the motor. The high $$$$ for a replacement is why I keep repairing the switch. I just hope it lasts a while longer. I will be replacing it with a sewage pump next year. I have a submersible pump I can drop in if it fails. I test my sump pump every month or so.


One of the problems with submersible pumps is that the electrical connections go bad from water seepage. Water gets in everything... Water migrates along potted wire connections. Water migrates thru materials, most organic materials are water permeable. When moisture gets inside the housing leakage current increases which will trip GFI circuits. I wish I had a nickel for every submersible pump that was replaced because the basement flooded after the pump "obviously" failed.
 

Torque1st

MEMBER EMERITUS
Joined
Sep 14, 2008
Messages
5,668
Location
KC Metro, Kansas
I am installing a 3/4 bath in the basement. The house used to be on a septic system so the main sewer line is 4' above the floor.
 

D KRAGER

Well-known member
Joined
Oct 16, 2007
Messages
581
Location
Central IL
They get by with that rating most likely by rating the peak hp rating. Not the running hp rating....... Kind of like most 60gl air compressors, they say 5hp motor, but that's peak hp rating, they are really 3hp while running.
 

Torque1st

MEMBER EMERITUS
Joined
Sep 14, 2008
Messages
5,668
Location
KC Metro, Kansas
They get by with that rating most likely by rating the peak hp rating. Not the running hp rating....... Kind of like most 60gl air compressors, they say 5hp motor, but that's peak hp rating, they are really 3hp while running.
-And it takes continuous HP to compress air. That peak HP can help the compressor get past that last little "hump" as the tank is building pressure but otherwise it is meaningless.

I talked to one of the Engineers down at NEMA and they get away with it using instantaneous HP related to breakdown torque. The consumer goods manufacturers don't have to conform to NEMA standards. Just look at that "5HP" circular saw or shop vacuum running on that little 18AWG or maybe even a 16AWG cord, -wear your ruby slippers, tap your heels and wish... ;)

On consumer compressors just look at the amp draw to approximate the real HP.
 