pump tank alarm wiring

250

Well-known member
Joined
Oct 16, 2014
Messages
537
Location
West of the Sierras
I'm installing a high water alarm in a septic pump tank, with the alarm box about 50 ft away from the float sender. The alarm paperwork says the float signal is 12 vac. I'm looking for information on the wire gauge needed for the 50ft run. Recommendations/tips appreciated.

Thanks,
 
To avoid these ads, REGISTER NOW!

Sokoloff

Well-known member
Joined
Jun 11, 2005
Messages
400
Location
Cambridge, MA
I suspect that 18 gauge (or even smaller) wire would be fine. There is not much current that needs to flow for a switched signal to drive an alarm. For reference, most doorbells are on 18 gauge wire. A more key spec for the alarm is the current draw (and whether that all flows through the high limit switch or not). It's probably in the well under an Amp range, which would also push me towards 18 gauge being "plenty" electrically.

You probably need to be more concerned with physical issues, such as "is the insulation and overall physical strength suitable for local conditions?" [whether direct buried, in conduit, run across the lawn, etc].
 
To avoid these ads, REGISTER NOW!

BreeStephany

ALLIANCE MEMBER
Joined
May 19, 2012
Messages
849
Location
Oregon
Generally, in the alarm / controls I have wired, I run a 3/4" PVC conduit between the control box and the tank float j-box and then pull #12 THHN between, even if it is just low-voltage / control wiring.

The advantage of running a conduit is you can always easily repull conductors if a conductor was ever to fail or your control/alarm requirements were to change.

Just my two cents.
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,307
Location
Dutzow Missouri
I thought the low cost solution is a bright strobe light that you will see from the house.

Do you really want an alarm telling you about a problem a 2 AM?

Walt
 
Last edited:

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
Generally, in the alarm / controls I have wired, I run a 3/4" PVC conduit between the control box and the tank float j-box and then pull #12 THHN between, even if it is just low-voltage / control wiring.

The advantage of running a conduit is you can always easily repull conductors if a conductor was ever to fail or your control/alarm requirements were to change.

Just my two cents.

X2- That's exactly what I did on my septic system that I installed when I built my house last year.
 