So finally, I was able to get a full bottle of acetylene and a torch to finish the brazing... I still need to get finish the electrical on the new heat pump..
With that said, I want to get my charge right, as right as it can be by weight, so when the electric is hooked up, I'm good to go....
I ended up using 46 feet of line set. The heat pump states that it came with enough R410a for 15ft of 3/8 liquid line and the factory dryer (.6oz for each additional feet of liquid line)... So here's my numbers.. I just want o make sure they look good since I can't charge by SH/SC.. Can anyone confirm the numbers?
46ft - 15ft = 31ft.
31ft * .6oz = 18.6 oz of R410a.
18.6oz = 1.1625 lbs of Puron.
BTW, I can't remember how many decimal places my scale goes out to... So if need be, would I better better off adding 1.1lbs or 1.2 lbs of Puron ... assuming my numbers are good?
Thanks all!
With that said, I want to get my charge right, as right as it can be by weight, so when the electric is hooked up, I'm good to go....
I ended up using 46 feet of line set. The heat pump states that it came with enough R410a for 15ft of 3/8 liquid line and the factory dryer (.6oz for each additional feet of liquid line)... So here's my numbers.. I just want o make sure they look good since I can't charge by SH/SC.. Can anyone confirm the numbers?