Someone said to put the screw side inside the box, because you can then loosen the screws if necessary.
 
To avoid these ads, REGISTER NOW!

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,288
Location
Illinois near St. Louis, Missouri
Normally I put them outside. I have put them inside a few times - such as on some 4' tube fixtures where I put a box up for lights and then put the fixture over that. Hard to tighten if it's above and then push the wire into a small box. But in hindsight I didn't need the box and could have just put the clamp on top (outside) and pushed the extra wire into the ceiling. So put them outside unless there is a reason to put them inside - just being able to loosen then later in most situations isn't a good reason IMHO.
 

wssix99

Well-known member
Joined
Mar 2, 2011
Messages
5,159
Location
Chicago, IL
This has come up before... but doesn't make sense and doesn't pay off. If the wire is installed correctly, it should be stapled inside the wall and loosening the clamp doesn't get one anything.

Having the clamp inside-out also puts sharp edges inside the box and reduces the ability to fill, which are all bad.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,481
Location
Richmond, VA
I've never seen manufacturer's instructions.

How do we know its designed for the screws to be outside?
Locknut goes inside the box. It's SOP. Excerpt below from Halex documents as a reference.

Also found this from Halex " Insert threaded portion of connector into knockout in outlet box so that the clamp portion is outside the box."

1000003335.jpg
 

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,418
Location
Western North Carolina
Locknut goes inside the box. It's SOP. Excerpt below from Halex documents as a reference.

Also found this from Halex " Insert threaded portion of connector into knockout in outlet box so that the clamp portion is outside the box."

1000003335.jpg
All nice and dandy but do we really want to take advice from a company that promotes the use of handy boxes? 😉
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,967
Location
Central Iowa
I've done it. It isn't a habit but there have been times a pancake box was the only thing that would work. I put the clamp in so that when the drywallers rotozip the wires off, all I had to do was loosen the clamp and pull a little more cable in. Now. I use the plastic connectors. Pulling some slack in easy, sometimes too easy and I do it when I don't want to.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,481
Location
Richmond, VA
I've done it. It isn't a habit but there have been times a pancake box was the only thing that would work. I put the clamp in so that when the drywallers rotozip the wires off, all I had to do was loosen the clamp and pull a little more cable in. Now. I use the plastic connectors. Pulling some slack in easy, sometimes too easy and I do it when I don't want to.
Begs the question... Who causes more problems... Drywallers or plumbers?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,967
Location
Central Iowa
Begs the question... Who causes more problems... Drywallers or plumbers?
That's easy. Since I won't begin a rough in before the plumbers and HVAC are finished, it's the rockers. I'm trimming out a house now and on the walk through was able to point out five receptacles and a switch that were covered by drywall.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
That's easy. Since I won't begin a rough in before the plumbers and HVAC are finished, it's the rockers. I'm trimming out a house now and on the walk through was able to point out five receptacles and a switch that were covered by drywall.
time to get the hammer out and have fun blowing holes in the wall to find your receptacles

:lol_hitti :lol_hitti :lol_hitti
 

Fatboy148!

Well-known member
Joined
Mar 11, 2023
Messages
248
I got to the point where I would mark the floor with a permanent marker line where the boxes were. Two OO's through the line for an outlet and a line through it for a switch height box. It's also fun to clean all the dust, Durabond and joint compound out of the boxes,
 
To avoid these ads, REGISTER NOW!

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,151
Location
Northern Virginia
I got to the point where I would mark the floor with a permanent marker line where the boxes were. Two OO's through the line for an outlet and a line through it for a switch height box. It's also fun to clean all the dust, Durabond and joint compound out of the boxes,
Our electricians just use a key hole saw and start poking and cutting till they find the buried items without care of the damage they cause. They get it done and the drywall crew ***** it up with the repairs. 🤷‍♂️
 

whateg01

Well-known member
Joined
Mar 13, 2006
Messages
11,227
Location
doo dah, kansas, usa
I've done it. It isn't a habit but there have been times a pancake box was the only thing that would work. I put the clamp in so that when the drywallers rotozip the wires off, all I had to do was loosen the clamp and pull a little more cable in. Now. I use the plastic connectors. Pulling some slack in easy, sometimes too easy and I do it when I don't want to.
If they cut the wires, how do you get ahold of the loose wire that's outside the box behind the drywall to pull more in?
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,151
Location
Northern Virginia
6 foot level/straight edge finds 90% of the covered boxes, close enough to put a sheetrock saw inside the box and cut it out like the drywaller should have.
Electrician’s use pocket levels at best to plumb devices. A 6 footer is not in their toolbox so poke poke stab saw cut cut bingo and the drywall crew solves the mess on their dime.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
I have heard of the sledge hammer box finder, sometimes they deserve it but it is not recommended. (Impulse control).
 

ybnormal

Well-known member
Joined
Jan 3, 2016
Messages
5,002
That's easy. Since I won't begin a rough in before the plumbers and HVAC are finished, it's the rockers. I'm trimming out a house now and on the walk through was able to point out five receptacles and a switch that were covered by drywall.
they are that dumb they actually covered up the outlets? :headscrat
 

cmandp

Well-known member
Joined
Dec 22, 2011
Messages
1,277
Location
New Jersey
Plumbers cause issues for framers since they just hacked half a joist away for that drain line. Electrical is just collateral damage if he didn't look behind the joist to see that cable he just cut with his sawzall.

But since this is a drywall thread now. How do I patch all those holes that electrician just made in my beautiful, uninterrupted by outlets, rock work?
 

bronc076

Well-known member
Joined
Jul 17, 2023
Messages
190
Location
Ozarks
My dad was an electrician in Chicago back in the 50s/60s. He told me about a job where the bricklayers just pushed some boxes back into the wall and bricked up in front of them because the electricians had not put the boxes at the right height to correspond with a mortar line or something. There was a fist fight. :)
 

Fatboy148!

Well-known member
Joined
Mar 11, 2023
Messages
248
The masons have also been known to cut the PVC pipe right off using a piece of their string line
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,260
Location
Coastal NJ
Seems to me that there's a rule about exposed screw threads in a box anyway.
What does that rule say? Device (switch and receptacle) mounting screws and light fixture screws have exposed threads in the box.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
What does that rule say? Device (switch and receptacle) mounting screws and light fixture screws have exposed threads in the box.
Oh the rule exists and has been discussed many times here. Just feeling combative? I'm not going to look it up and cite chapter and verse.

It was just a comment. Like it or lump it.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,260
Location
Coastal NJ
Oh the rule exists and has been discussed many times here. Just feeling combative? I'm not going to look it up and cite chapter and verse.

It was just a comment. Like it or lump it.
Not combative at all. I've read a lot on this forum and never saw mention of this. Since you have, I figured you would share.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
314.23(B)(1) Nails and Screws.Screws shall not be permitted to pass through the box unless exposed threads in the box are protected using approved means to avoid abrasion of conductor insulation. Mounting holes made in the field shall be approved.

N 314.5 Screws or Other Fasteners. (1) Screws shall be machine type with blunt ends. (2) Other fasteners shall have blunt ends. (3) Screws attaching a cover shall extend no more than 3⁄8 inch.

406.5 Receptacle Mounting. Receptacles shall be mounted in identified boxes or assemblies. The boxes or assemblies shall be securely fastened in place unless otherwise permitted elsewhere in this Code. Screws used for the purpose of attaching receptacles to a box shall be of the type provided with a listed receptacle, or shall be machine screws having 32 threads per inch or part of listed assemblies or systems, in accordance with the manufacturer’s instructions.

There's one for panel cover screws allowed as well. I'm not the code police. I'm providing my findings simply to satisfy a statement.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
Probably doesn't. I should have never replied.

All I know is the last box I made up tripped a breaker and smoked a wire. It was a screw supplied with a device. Also in this gang box was a dimmer that took up nearly 1/3rd of the box putting the make up behind a recep and another flip switch. Somehow while stuffing the box with folded wires, grounds first way to the back, then neutrals with yellow nuts and finally the dimmer leads, nuts, jumper, switched and hot, I got one close enough that while driving said supplied screw with a driver drill, it wore into a hot. Blunt or not.

I like the 3/8ths rule but they are for covers, not the tabs of the device. It might be a hassle to get shorter screws started. I have seen really long screws for a fixture crossbar long enough to hit the back of the box. I try to use the shortest screw that I can get started w/o cussing.

So my thoughts are to limit screws and to use proper ones. It's just a thread about screws. I'm surprised no one brought up drywall screws. Now there's a topic for discussion. Even I, a long time ago, may have used a DW screw when a device screw stripped out. Not good, but I've seen it.

And I'm surprised at the sentence, "Mounting holes made in the field shall be approved." I've read that screw heads are not allowed inside a box.

314.43 Nonmetallic Boxes. Provisions for supports or
other mounting means for nonmetallic boxes shall be out-
side of the box, or the box shall be constructed so as to
prevent contact between the conductors in the box and the
supporting screws.

You have to conjure up some unusual circumstances for that one to make sense. Well, here it is: likely this scenario would occur during a remodel where an old work box is not that stable so someone drives 2 screws through the side of the box. (I believe they make a metallic box with provisions to drive screws from the inside at an angle.) But on the NM box whatever screw Mr. Remodeler uses may hit a shear wall or lathing screw therefore potentially energizing the lath if the screwhead in the box comes in contact with a hot.

Sorry, it's just a slow day and I'm bored if not a bit cranky.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,260
Location
Coastal NJ
I suspect this:

314.43 Nonmetallic Boxes. Provisions for supports or
other mounting means for nonmetallic boxes shall be out-
side of the box, or the box shall be constructed so as to
prevent contact between the conductors in the box and the
supporting screws.
May refer to this where all the metal is outside the box and therefore can't be energized.

1702074252644.png
The nonmetallic boxes for dryers have a large plastic cable clamps with metal screws in the box, but the screws in those are recessed into the plastic.

1702074389208.png
 