PVC conduit connection to panel - clamps required?

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,349
Location
Alexandria, VA
I have MHF running in PVC conduit under the ground and up to the subpanel in my detached garage. I have not made the final connection to the sub panel.

Do I need to have a clamp to secure the MHF as it enters the sub panel? Based on my research online, I don't think a clamp is required, but want to make sure.

I have a threaded PVC connector that fits the 2" punch out in the bottom of the box, but it does not have any type of clamp or retainer for the wire. The MHF will run straight down from the panel (in conduit) to an LB, and then through the wall (in conduit) to another LB, and then through conduit down into the ground.


Thanks,

Bruce
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
7

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,349
Location
Alexandria, VA
Thanks for the info.

Conduit comes into the panel on the bottom, and I was considering leaving the sub-panel in its normal orientation (main breaker at the top), and feeding the conductors up the far left/right inside of the sub-panel and back down into the connectors on the bus. I will only have about six circuits in a 24 breaker panel, so I don't think space will be an issue.

Does this make any sense, or am getting too OCD about having the panel right side up? For me, it just makes more sense to have the panel in the standard orientation, since I have enough wire to run the power up to connectors on top.

Bruce
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
The PVC terminal adapter does require a bushing if the conductors are 4 AWG & larger.
 
To avoid these ads, REGISTER NOW!
OP
7

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,349
Location
Alexandria, VA
This is the adapter I plan to use to connect the conduit to the panel.
http://www.homedepot.com/p/Carlon-2-in-Non-Metallic-Male-Terminal-Adapter-E943JRR/100404004

Since this is a PVC adapter, what type of bushing is required for 4 AWG and larger cable?
Is this the right type? http://www.homedepot.com/p/2-in-Rigid-Plastic-Insulated-Bushing-4-Pack-27526/100169597
The bushing is not expensive, but I don't see how it really provides any additional protection from abrasion for the MHF wires entering the panel.

Bruce
 
Last edited:

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
Does this make any sense, or am getting too OCD about having the panel right side up? For me, it just makes more sense to have the panel in the standard orientation, since I have enough wire to run the power up to connectors on top.

Agree. Dont think it is OCD. Once the wires are run and covers on, you wont see how its wired-
 