Hey guys, I wanted to know if I can run pvc conduit along the outside of my house. My panel is in the basement and my idea was to run the conduit outside the house to two opposite ends for where I am installing mini splits.

On the pic I attached my plan was to drill a hole above the basement window and then run pvc conduit straight up about 16 feet then split the conduit so it can go left and right to two different bedrooms. Please help
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,349
Location
Richmond, VA
Yes. If the run is long, adding an expansion joint will be prudent as the conduit will grow when it heats up in the weathet/sun
 
OP
M

Micscience

Well-known member
Joined
Aug 22, 2012
Messages
140
Ok that is what I thought but I started doubting it after a Google search. All the pvc was on the foundation.

Thanks fellas
 
OP
M

Micscience

Well-known member
Joined
Aug 22, 2012
Messages
140
I just looked up the expansion joint. Is there a section where the expansion joint would be Ideal? The distance of the circuit is going to be roughly around 90 feet or little bit less and I am going to add 3 90 degree elbows per run.
 

Yankeefarmer

Well-known member
Joined
Jul 25, 2011
Messages
1,169
Location
Connecticut
I just looked up the expansion joint. Is there a section where the expansion joint would be Ideal? The distance of the circuit is going to be roughly around 90 feet or little bit less and I am going to add 3 90 degree elbows per run.
You described your installation as a tee where it exits the building, with one run going right, and another left. The exit will be stationary, constrained by the wall penetration. Put an expansion joint in each of the horizontal runs. Doesn’t really matter where, but I’d likely locate it close to the tee or towards the middle of the run, wherever convenient.
 
To avoid these ads, REGISTER NOW!
OP
M

Micscience

Well-known member
Joined
Aug 22, 2012
Messages
140
I like the expansion pipe on the horizontal Tee idea. The wire I grabbed was THHN. I tried researching and it was a never ending road so I had to make a choice.

So I have one of the room's pretty much almost done however I didn't notice at first my disconnect box says 240 volt though my mini split is a 115 volt 9,000. Would that be an issue? Does the disconnect have to match the voltage rating?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,349
Location
Richmond, VA
I like the expansion pipe on the horizontal Tee idea. The wire I grabbed was THHN. I tried researching and it was a never ending road so I had to make a choice.

So I have one of the room's pretty much almost done however I didn't notice at first my disconnect box says 240 volt though my mini split is a 115 volt 9,000. Would that be an issue? Does the disconnect have to match the voltage rating?
No, that disconnect is fine, you will just connect to one of the legs and leave the other empty.

I doubt 120v disconnects even exist (at least in the typical a/c disconnect format)
 

inphx

Well-known member
Joined
Feb 23, 2012
Messages
1,273
Location
Phoenix/Scottsdale AZ
Does the NEC require a GFCI outlet be installed within 25 feet of the outdoor AC unit for servicing purposes? Now;s the time for that.
 
OP
M

Micscience

Well-known member
Joined
Aug 22, 2012
Messages
140
That is good to hear I kept searching for 115 volt versions and they were no where to be found. I have two different type of disconnects. The one that I mounted is fusable and the other one is non fusable. I read the fused version doesn't come with a fuse so I might switch them.

As far as a outlet goes it would be mounted on top of the sun room roof. It would only serve a purpose if I am working up there.
 

Attachments

  • 20240806_190305.jpg
    20240806_190305.jpg
    1.1 MB · Views: 28

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,750
This would depend on the data plate on the unit, but if a fusible disco was not required, I would use a non fusible disco & switch both line & neutral, it is permitted by code as long as grounded, & ungrounded conductors are switched together. Bonus is they are not expensive.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,880
That is good to hear I kept searching for 115 volt versions and they were no where to be found. I have two different type of disconnects. The one that I mounted is fusable and the other one is non fusable. I read the fused version doesn't come with a fuse so I might switch them.

As far as a outlet goes it would be mounted on top of the sun room roof. It would only serve a purpose if I am working up there.

disconnects are sold without fuses because it's very common to put in a disconnect with a higher rating that is needed, and you'd need the fuses anyway. As was noted, you would only hook up one side of the disconnect. I'd put a fuse in the other side, too, because it's harder to lose it there. Future you might be pleased...

Code requires an outlet within 25' and at the same level, specifically so a tech can plug in service equipment without having to run a cord down or up a ladder. The disconnect probably has knockouts on the side, use a short bit of conduit and hang a box off the side. Also needs to be gfci protected.
 