Wow lots of misinformation in this thread!!
I had a question about 3-phase and wanted to figure it out before I even bother calling my local POCO about getting the service.
From what I understand, with a 4 wire 3-phase service, any hot leg to neutral is 120v. Like most shops I have a variety of single-phase 120v and 220v machines that I need to power, along with wanting to get a 3-phase mill.
Can I still power my 120v and 220v machines by using 1 and 2 legs of the service like on a normal 1-phase service or does some other arrangement have to be made to power those?
As u already found out on your PoCos site, theres actually several flavors of 3-phase. For 4-wire 3-phase theres several options.
Theres 208Y/120v (Wye), which will give u 120v between any of the 3 hot legs and neutral. Line to line(either 2 or 3) will be 208v.
Another 4-wire wye service is 480Y/277v- 277v between any hot and neutral and 480v line to line.
Next is Delta. 240v/120v- 120v between 2 hot legs and neutral. The third leg is the high leg or stinger and its called this because its 208v to neutral. U obviously cant use this leg for 120v loads!
Many PoCos are getting rid of or no longer supplying new service with 240v Delta so many people are limited to 208Y/120v service. Delta services are inherently imbalanced and Ive been told can end up providing dirty power due to the imbalance.
Theres also some other varieties of 3-phase that wouldnt apply to u so i wont go into them.
Now if u have a lot of 120v equipment, a 208Y service might be a better bet for u.
Your equipment may very well be rated for 208v. Check the motor nameplate!
Nope, only 120v across one hot....two hots will equal 208volts. Some (220)240v tools will run on 208v but don't think you want that for any typical machine as it can damage the motor. 3 hots equal 277volt. You can however use a transformer to get true 240v with a 3p service. ( at least this is what I recall from my tech. school days with John Joyce teaching us at Alfred.)
Huh? Theres no such service where u will get 120v across neutral and only 1 hot. And theres NO system that gives u 277v between all 3 hot legs. You are confused! 277v is a line to neutral voltage for a 480Y/277v system.
Found this on my POCO's site:
"also has available the following four wire three phase voltages: 120/240, 240/480, 120/208, and 277/480. Customers may obtain three phase service at no cost if their forecasted load is sufficient to support the installation of three phase equipment."
Would 120/240 be more preferential in this situation?
I'm also struggling to understand how one hot equals 120v but two equals 208v... but maybe that's for another thread.
U the customer needs to figure out what voltage your machines need.
The 240/480 must be a typo because no one provides service like that as there is no point to it. The 480v Delta service is ran as a 3-wire service.
for light 3 phase usage with heavy single phase usage (as i assume your load would be), the ideal set up would be an open delta service. uses a large "lighting" transformer and a smaller "power" transformer. lighting transformer gives you a center tapped neutral, which basically makes 2 legs and a neutral behave just like 120/240 single phase. power transformer gives you the third leg, which allows you to have 240 volts between any 2 phases. this would be most ideal for a 240v motor and would likely be the least expensive route to go. if i were you, i would install 2 panels, one for single phase, and a smaller one for 3 phase, that way theres no chance of putting a single phase load on the high leg.
doojus, you just have to accept the math for what it is unless you want to go in to detail learning about EE stuff. 120x1.73=208 1.73 is the square root of 3, and shows up a LOT in 3 phase calculations...
No the power transformer means u will have 240v between ALL 3 PHASES! U already have 240v between 2 phases with the single phase transformer.
Measure the voltage at your compressor. I'll bet it is 208V.
They do make 208v - 240v transformers.
Many "modern" motors (especially A/C) are actually designed to run on 200-250V.
No it depends on the system! Read above!
Billk and a couple of other are correct.
You power company does NOT need 3 transformers on the pole. For you the ideal would be a Delta configuration which is what we have (ours is 4 wire, 3 phase, high leg Delta service). One additional transformer on the pole is all that is needed by the poco.....
....On the 4 wires, we also have a ground at the main disconnect so we have 3 hots, neutral, and ground. Most of the grounds are connected via rigid metal conduit.
Two of the hots to neutral are 120v, the third hot (the high leg) to neutral is 240v, any hot to hot gives 240v. Our service also runs on the high side, actual voltages average about 253 volts and 128 volts.
One thing I've considered trying (although its probably against code for some reason) is to use the high leg for certain 240v single phase loads like all the overhead lighting. I have not had a chance or time to look at the electrical code and possibly look into using the wild leg for that though. As I said, it might be a code violation but I'd think if can get a non slash rated single pole 240v breaker why it would not work.
yes, u can get delta service with just 2 transformers. However, your 3-phase power is limited to about 58% of what u would get with a 3 transformer bank so an open delta configuration is for limited power loads.
And the high leg is ~208v to neutral NOT 240v! If u have a 240v high leg, then the voltage on the primary side of the transformer is TOO high!
And yes people have tried using the high leg for single phase loads. Your lighting would need to be rated for
208v NOT 240v. Using the high leg with neutral does create some weird imbalances in the transformer bank and u could possibly overheat it. Also, the voltage on the high leg varies and isnt stable. I dont recommend using the high leg for line to neutral loads!