Question about 3-phase

fast one

Well-known member
Joined
Feb 13, 2011
Messages
69
Location
MD
My utility only offers 4 wire services for new construction. 3 wire services are maintenance only, if you have them, they will maintain them and you can keep them forever.

If you have a delta bank hanging outside you may be able to reconnect, they may require you to put 4 wire in.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
My utility only offers 4 wire services for new construction. 3 wire services are maintenance only, if you have them, they will maintain them and you can keep them forever.

If you have a delta bank hanging outside you may be able to reconnect, they may require you to put 4 wire in.

120v/240v Delta IS 4-wire...
 
To avoid these ads, REGISTER NOW!

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,679
Location
Central-ish, WA
its still a coil of wire that makes a circuit... ALL transformers have a no load loss figure, even though the there is no current flowing in the secondary, the transformer still hums right? there is still some current flowing to excite the windings. i doubt that the no load loss is 9% of the nameplate, but i wouldnt doubt that the full load losses (lost as heat) would be 9%...


It's called magnetizing current. It is determined from the impedance of the primary.

I have a 400a 3 phase 4 wire 240v delta at my old shop. Basic meter charge a bit more than my home service. Cost per kWh is a tiny bit less than domestic service. Will be installing similar service at the new shop. Going to cost me about $1000 to the utility plus meter base and 3 phase panel.
 