That is not a "double pole breaker" but rather, a "tandem" breaker. The difference being that the double pole is supplied off of separate stabs that are opposite "sides" of the alternating current wave, while the tandem is simply two individual single pole breakers that are supplied off the same stab.
That being out of the way..................
Your panel may have, toward the bottom of it, stabs with notches in them, that allow the installation of the breaker you are referring to. You don't give us any info about the panel, but if it is, say, a 30 space panel that is also a 40 circuit panel, then the bottom five stabs will have notches in them for these tandem breakers. Otherwise, it is not legal to install the breaker in the the panel. If the panel is a 4040 meaning it has 40 spaces and 40 circuits, then you are not allowed to use the tandems, as you can put 40 standard breakers in the panel.
Charles
Stabs which accept the "restricted" breakers such as the tandem you have.
Upper stabs which do NOT accept the breaker like you have.
Comparison of two 20/20 tandem breakers, one being designed for installation on any stab position (on the right side of pic) and only for use in breaker panels before a certain date (what that is, I cannot remember) and the one on the left is a restricted breaker, which will only install in a stab with a slot in it.
Charles