Landor
Member
I'm working on a mini split install and ran into something that I'm not sure about. The unit is a Mr Cool DIY 2 ton mini split. I've used 10ga. wire to supply the unit and the only disconnect I could find seems to require 30A fuses.
The label on the compressor reads as follows:
Outdoor Fan Motor Load 0.6A
Compressor Load 12.0A
Minimum Circuit Ampacity 15.0A
Max Fuse 25.0A
So does this mean that the breaker should be 15A and the fused disconnect should be 25A?
Any help is much appreciated, thanks!
The label on the compressor reads as follows:
Outdoor Fan Motor Load 0.6A
Compressor Load 12.0A
Minimum Circuit Ampacity 15.0A
Max Fuse 25.0A
So does this mean that the breaker should be 15A and the fused disconnect should be 25A?
Any help is much appreciated, thanks!