I have an attached garage to my home, and when the home was built, the garage was insulated and sheet rocked with a 5/8" fire code and then plastered. A few years later I added an additional garage onto the existing one, and what was the outside wall that has texture 1-11 on it is now the inside wall of the additional garage. When this garage was added on, it was never sheetrocked or insulated. I am now planning on having it spray foam, and will be adding 5/8" fire code sheetrock. My question is, do I need to cover the T 1-11 with fire code sheetrock also? If so, would it be best to just go over it with the sheetrock, or does the T 1-11 need to be removed first? Going over it will be the easiest and most cost-effective. Your thoughts? thanks Junk
 
To avoid these ads, REGISTER NOW!

Youngandfree

Well-known member
Joined
Dec 29, 2020
Messages
877
Location
VA
I'd cover it if you don't want to hassle with removing it. I'm not a fire marshal or building inspector.
 
Last edited:

jack stand

Well-known member
Joined
Feb 29, 2012
Messages
3,368
Location
Lakes Region Maine
If you need permits and inspections I'd ask before you start.
The thinking used to be that the party wall between garage and living (sleeping) spaces needed a certain fire rating.
A garage addition to a garage..... common sense would say your already protected, but we know where beauracratic "creep" leads to.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,034
Location
Richmond, VA
The drywall needs to separate the garage from living space. If the t1-11 is just on a wall inside the garage, you are fine
 
Last edited:

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,972
Location
Thousand Islands NYS
I agree with Mike. Here's the chart from 2018 IRC. Note that in code terms, this is not "rated" construction.
SEPARATION​
MATERIAL​
From the residence and attics​
Not less than 1/2-inch gypsum board or equivalent applied to thegarage side​
From habitable rooms above the garage​
Not less than 5/8-inch Type X gypsum board or equivalent​
Structure(s) supporting floor/ceiling assemblies used for separationrequired by this section​
Not less than 1/2-inch gypsum board or equivalent​
Garages located less than 3 feet from a dwelling unit on the same lot​
Not less than 1/2-inch gypsum board or equivalent applied to the interiorside of exterior walls that are within this area​
 
To avoid these ads, REGISTER NOW!

Jay H 237

Well-known member
Joined
Apr 24, 2005
Messages
1,995
Location
Torrington, CT
Seeing as some people finish wall thier garages with OSB I don't see much of a difference between that and T11, as long as a living shared wall is drywall.
 
OP
J

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,658
Location
Northeastern CT
Because the new addition is cantilevered off the original garage exterior wall, there is no living space above, just the roof.
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,972
Location
Thousand Islands NYS
then no need to do anything special
I would agree as long as there is no attic connection to the dwelling. Somewhere between new garage attic and dwelling there needs to be min 3' of exterior or a drywall separation. Admittedly, very unlikely there is any connection or required separation. A gable to gable to house gable connection is possible.
 