Question about running a circuit from one outbuilding to another

b-boy

Well-known member
Joined
Oct 2, 2013
Messages
2,158
Location
Buffalo NY
I have a pole barn about 250 ft from my main house. I've got a sub-panel in the pole barn. The sub-panel is properly wired, and there are 2 ground rods in place.

There is a 15x30 lean-to about 50 ft from my pole barn. I'd like to trench and run wire to this structure. I want to be able to add some outdoor lights and an outlet.

I'd like to add a circuit to the sub-panel and run it out through the wall underground, and into the side of the lean-to. I want to add at least 1 outlet, 1 switch, and some outdoor lights. This area is basically covered, but can be exposed to the elements during a heavy storm. I'd most likely use a GFCI breaker at the sub-panel.

Any issues doing this?
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
You can do this. Dig ditch deep, 24, use UF wire, number 12. What I do instead of a gfci breaker add an outlet with gfci and feed it from there and actually allowed to dig only 12 inch if you want. If this is a separate building add a switch for this line just after it enters the building as a means of disconnect.
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
If the circuit is GFI protected at the source and only 120 volts and 20 amps in a residential setting, the burial depth can be decreased to 12" unless it will be subject to vehicular traffic.
 

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,942
Location
Central New Jersey
If the circuit is GFI protected at the source and only 120 volts and 20 amps in a residential setting, the burial depth can be decreased to 12" unless it will be subject to vehicular traffic.

This is how I did my shed wiring. It is GFCI protected before it goes into the ground from the garage. It is a single run of 12 gauge UF-B, and is buried at 12 inches deep since it is protected before it enters the ground.

I put a simple switch as a disconnect in the shed which shuts the power off to it if need be.

Jim
 