Context is everything and the OP hasn't given us that. We are not even told what the machine is, whether it stands alone, or whether it is part of a larger machine or production line.
There could be a number of reasons for the "odd" values.
My best guess would be that it's been done that way for decades and is an "if it ain't broke, don't fix it" thing.
An old-school V/Hz VFD varies the Voltage and Frequency together below the Rated Frequency, giving Constant Torque. Once the motor is at rated Frequency, it is also at rated Voltage. It can continue to increase Frequency, but Voltage is at maximum safe level and can't be increased. Above the rated Frequency, the Frequency is increased, but the Voltage is constant, giving Constant Power. It may be that the values were chosen to match the motor power profile to the machine load profile.
Most likely, back in the mists of time, someone fairly bright, and with an understanding of the process, commissioned a machine, probably in consultation with the tech experts from the motor manufacturer and the VFD manufacturer.
I first used a VFD in 1989 and they've come on a long way since then. Motor efficiencies have increased, Mainstream VFDs have Sensorless Vector capability.
However, whenever we change one out, it almost invariably gets the same basic parameters as the one it replaced, simply because it's almost never worth the downtime associated with commissioning and optimizing from scratch. We have some plant out there with settings from three VFDs and 2 motors back.