Question on 20amp circuit / breaker
SweetD
Rhode Island
Guys,
Couple quick questions, replacing an outdoor non-GFCI receptacle:
If I have a 20AMP breaker on a circuit which includes our main floor lavatory and a single outdoor receptacle on our back deck, would that likely indicate I can use a 20AMP GFCI to replace the old crappy non-GFCI outdoor receptacle?
The breaker box is labeled 'bathroom and outside' for that 20AMP fuse. I also read that outdoor receptacle circuits are often 20AMP to account for potential larger draw of outdoor use of power equipment, etc.
Is this typical?
Thanks -
Dave
thewatusi
Philly Burbs
Both the bathroom and the outside outlet have to be gfci protected. You can either put in a gfci breaker (more expensive) or put a gfci outlet in place of the first outlet in the circuit (cheaper)
SweetD
Rhode Island
Thanks! I should've mentioned that the breaker is in fact a GFCI protected breaker. So no need for the GFCI receptacle at the outdoor location then?
If that's the case, can I use a "regular" non-GFCI receptacle at the outdoor location, covered with an outdoor rated bubble cover?
Dave
Eriehunter
Yes if you have gfci protection at the breaker all down stream outlets are protected.
SweetD
Rhode Island
Thanks guys! I bought the GFCI tester today along with the new outdoor rated box. You have confirmed my procedure - thank you!
Dave
pattenp
Virginia - USA
Got it, thanks!
The 5-20R is what you don't want to use. You should use a 5-15R.
Use the 15A on the right....
SweetD
Rhode Island
Ok now I'm confused. I was planning on using what I had on hand, which I'm not exactly sure what the type is. It says on the back of the receptacle:
"For 15AMP branch circuit only" #14-#12 AWG
I don't see much else on it that makes sense other than "USA"...?
pattenp
Virginia - USA
Also, you need to use a weather resistant rated receptacle, for outdoor use. It has real brass contacts in it, now required by code.
Charles
Good point Charles. This is a 2011 NEC requirement. Also, weather resistant devices must have a “WR” marking clearly visible when installed.
SweetD
Rhode Island
The GFCI receptacle I picked up for this job has the "WR" marked on it. I will get the 5-15R with the "WR" when I return the GFCI tomorrow.
You guys are a huge help, thanks again!
Dave
Charles (in GA)
50 mi south of Atlanta
NEMA 5-20 and 5-15 are the standards for pin configuration on plugs and receptacles for 120v. The number 5 tells us it is for 120v, and the number 15 or 20 tells us the amperage. Despite the fact that you have a 20 amp circuit breaker/12 gauge wire, you do NOT need a 20 amp rated receptacle
Code only requires that the receptacle rating conform to the circuit amperage IF and only if, you have ONE SINGLE receptacle on the circuit. Since a DUPLEX receptacle is considered TWO receptacles by the code, you only need to use the common 15 amp configuration, and not the 20 amp T slot version (which usually cost somewhat more).
Note in the illustration above, the R is the receptacle (or female) view, and P is the plug (or male) view.
You do need to seek out a weather resistant receptacle at the big box store, supply house, or local hardware.
Charles
SweetD
Rhode Island
Charles, thanks for the explanation behind the coding and terminology. I really appreciate it - and one of the reasons I love this website and its great membership...!
:beer:
Dave
SweetD
Rhode Island
Re: Question on 20amp circuit / breaker - update, job done!
Well I got the receptacle switched out just as this nasty weather gets here this morning - here is the old receptacle - bad shape:
And the new setup - it's a "low profile" expandable water resistant cover:
THANKS again guys - I'm just a weekend warrior, so it's great to learn something and apply it myself!
:beer:
Dave