Question on Trenching and Materials

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
Good morning all,
I am starting a project on my new 30ac property out in the countryside and I have a couple of questions concerning getting power up to a remote location from my new future shop. A shipping container cabin is going to be set up on top of a fairly steep hill about 350ft feet from the panel in the shop.I am going to plan on a 40amp sub-panel in the cabin.Considering the material and labor cost of using pvc I want to use 1" 100lb black poly water pipe instead.There is no electrical code or inspection in this area... just a building, septic and plumbing permit. Is there any reason why this won't work and what aluminum wires would you use for this purpose? Thanks:thumbup:overhead shop-cabin-power.JPGshop-power shed.JPG
 
Last edited:
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,135
Location
Minneapolis
While there may not be local inspections, the state of Maine does require you follow the 2020 edition of the National Electric Code. If budget is a driving factor, check pricing on direct bury cable instead of using conduit. You'll also need to consider voltage drop because of the distance.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,128
Location
VT
It's not code/rated for electric.

It's probably going to **** (black poly is soft and wire can hang up).

35 sticks of 1.5" conduit is only $440. This will fit #1 aluminum wire. Looks like wire is $600-700 depending on if you reduce neutral
 
Last edited:

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,289
Location
Illinois near St. Louis, Missouri
It's not code/rated for electric.

It's probably going to **** (black poly is soft and wire can hang up).

10 sticks of 1.5" conduit is only $440. This will fit #1 aluminum wire. Looks like wire is $600-700 depending on if you reduce neutral
Did you mistype that? 10 sticks is only 100 feet and it shouldn't be $44 a stick. Even if you are figuring 20' "sticks" it doesn't add up. They need 35 pieces of 10' for garage to cabin. And more for meter to garage if that is buried too. I'm totally confused about price. Looks like the local big box stores are about $17 for 10' of 1.5"! Some of the electrical supplies show much less on google but I didn't drill down to check it out.

For voltage drop of 3% they need #1 aluminum. #2 gives 3.6% drop which would work.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,753
Location
NW Iowa
If you use direct bury wire the the poly would not break any codes for the underground portion at least.

I often use foam core plumbing PVC to protect direct bury wire. The wire does not require conduit so if it needs to be protected anything can be used.

Direct bury wire does need to be in conduit above ground. So you need to switch back to an actual conduit. That's another reason why I like the foam core PVC. The pipes are the same size so it's easy to change back and forth from conduit.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,987
Location
NJ
Have you considered adding sand or stone dust to the open trench?

This could eliminate any conduit and you just lay the conductors into the trench.
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
Back in the day (I'm old) everyone in the back country up here used well pipe for buried service because it was cheap
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,128
Location
VT
Back in the day (I'm old) everyone in the back country up here used well pipe for buried service because it was cheap

Where in Maine is "up here"?

By well pipe do you mean black poly?

Everytime I've dealt with direct bury in Maine it's either been a problem or over trenched and buried in so much sand they should have just paid for conduit.

What size poly pipe would you use? Does it come in 350' rolls? How much?
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
Have you considered adding sand or stone dust to the open trench?

This could eliminate any conduit and you just lay the conductors into the trench.
I am going to have a trench open for water anyway and can't see not using conduit of some kind
 

tarmy

Well-known member
Joined
May 28, 2014
Messages
4,690
Location
Nor Cal
I had several 200’-500’ runs. Once the trench was open I buried 3 extra conduit, a 2”water line and propane line. Years went by and I have used all of them. Just a thought OP.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,128
Location
VT
350 foot is a long run for 1" plastic. It would be a lot easier to pull that through 2".
Conduit or water pipe?

I asked OP several questions and no replies. But I still think <$500 for the correct conduit probably isn't much more then the roll of black poly
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
Where in Maine is "up here"?

By well pipe do you mean black poly?

Everytime I've dealt with direct bury in Maine it's either been a problem or over trenched and buried in so much sand they should have just paid for conduit.

What size poly pipe would you use? Does it come in 350' rolls? How much?
Anywhere in "rural" Maine

SDR-11 100lb HDPE poly pipe....300ft,500ft,1000ft

poly or conduit it will be 1 1/2"
 
Last edited:

beltfeed

Well-known member
Joined
Jan 22, 2006
Messages
224
Location
USA
PCustoms, Conduit. I just put in a new 400-amp service that goes 375 feet to a meter pedestal. I had to run 3" for the poco. My system splits at the meter pedestal into two 200-amp feeds, one to my house and one to the shop. I used 3" conduit for the 200-amp feeds also. They are about 175' runs each. Bigger conduit costs more but it sure helps pulling service wire in it.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,128
Location
VT
Anywhere in "rural" Maine

SDR-11 100lb HDPE poly pipe

poly or conduit it will be 1 1/2"

I spent a lot of my life in Maine.

Good chance my definition of rural is different then your definition of "rural". Unless you're building a secret off grid compound I don't see the harm in mentioning a town...
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
Sorry, I have been doing my research to properly sus :dunno: this out.It turns out in this day and age poly is basically the same price ($420)...no savings.I may say screw it and just direct bury MHF. My next question is can I use 2-2-4-6 for this or 2-2-2-4? The only 240v load will be the smallest size mini split I can find and some sort of water heater.This cabin will only be used late spring until late fall.



Attachments​

fill-v drop.jpgcosts.jpg
 
Last edited:

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,128
Location
VT
Anywhere in "rural" Maine

SDR-11 100lb HDPE poly pipe

poly or conduit it will be 1 1/2"
Looks like that pipe is over $1/ft, so there goes at least $400 (assuming you buy in 100' rolls). Not sure how you would join the lengths and still pull wire either...
 
To avoid these ads, REGISTER NOW!
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
I spent a lot of my life in Maine.

Good chance my definition of rural is different then your definition of "rural". Unless you're building a secret off grid compound I don't see the harm in mentioning a town...
If I tell yah, I'll have tah kill yah:bounce:
:cool:
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,128
Location
VT
Sorry, I have been doing my research to properly sus :dunno:this out.It turns out in this day and age poly is basically the same price...no savings.I may say screw it and just direct bury MHF. My next question is can I use 2-2-4-6 for this or 2-2-2-4? The only 240v load will be the smallest size mini split I can find and some sort of water heater.This cabin will only be used late spring until late fall.
I think the smallest size 240v mini split I saw last year was 18k btu, the 12k were 120v.

My gut says 2/2/4/6 is OK but technically you're supposed to run the calc.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,753
Location
NW Iowa
I get 1 1/2" foam core PVC for about 50 cents a foot. 2" is what I use the most, 65 cents a foot.

20' sticks go together quick. Can glue an electrical 90* right to it and easy to change the electrical PVC to go above ground.
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
I get 1 1/2" foam core PVC for about 50 cents a foot. 2" is what I use the most, 65 cents a foot.

20' sticks go together quick. Can glue an electrical 90* right to it and easy to change the electrical PVC to go above ground.
Technically not code worthy and foam core is very prone to punctures from rock. It is forbidden underground in the plumbing code for that reason.Also I don't think you could use a blanket on it to bend a sweep.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,753
Location
NW Iowa
Technically not code worthy and foam core is very prone to punctures from rock. It is forbidden underground in the plumbing code for that reason.Also I don't think you could use a blanket on it to bend a sweep.

There is nothing in the electrical code that prohibits it when you run a direct bury rated wire.

Direct bury cable does not require conduit. So if you choose to protect it you can you use whatever you want.
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
I think the smallest size 240v mini split I saw last year was 18k btu, the 12k were 120v.

My gut says 2/2/4/6 is OK but technically you're supposed to run the calc.
There's a bunch of 208/240V 9K units out there with a SEER of over 20. They draw around 7.5 amps typically.
 
Last edited:
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
There is nothing in the electrical code that prohibits it when you run a direct bury rated wire.

Direct bury cable does not require conduit. So if you choose to protect it you can you use whatever you want.
I was not aware...thank you. Foam core can be had in 20ft sticks...I am going to check it out next week.
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
And black poly is?
No it is not.However the original premise of saving money and no couplings is moot...same price basically. I will investigate price and availability of 1 1/2" x 20ft foam core...maybe I can save a few bucks.Can fiber be run safely in the same conduit?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,764
There is nothing in the electrical code that prohibits it when you run a direct bury rated wire.

Direct bury cable does not require conduit. So if you choose to protect it you can you use whatever you want.
Due to a incident many years ago, I get real pissy about electrical cables in white PVC. There is P&C duct that would work quite well & is gray.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
Sorry, I have been doing my research to properly sus :dunno: this out.It turns out in this day and age poly is basically the same price ($420)...no savings.I may say screw it and just direct bury MHF. My next question is can I use 2-2-4-6 for this or 2-2-2-4? The only 240v load will be the smallest size mini split I can find and some sort of water heater.This cabin will only be used late spring until late fall.



Attachments​

fill-v drop.jpg

when i do the calcs by hand for #2 AL 40a @ 350' i get 8.4v or 3.5% drop
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
There will be a 2 burner Empava induction cooktop which draws 1800 watts @120v, a small Vissani fridge that draws less than 1 amp,split draws less than 8 amps,lighting is negligible, fan on composting toilet. Perhaps a GE Profile heat pump washer/dryer combination unit (11 amps@120v). The water heater is all that is left to figure out.Is anyone aware of a small heat pump water heater? 40 gallon way too big.
 