Question on wiring inside detached garage - Will this approach pass NEC?

luvtheheat

Well-known member
Joined
Jan 28, 2017
Messages
489
Location
Tucson AZ
I have 4AWG MTW/THHN/THWN-2 stranded copper wire that I want to use inside a detached garage.

Capture.JPG


Idea is to run it from a 60 amp 2 pole breaker in the panel which is in the detached garage, up through wooden framed top plate (13' high), along the bottom of one of the wooden roof trusses, across to the wall opposite the panel, then down through top plate and terminate in a 3 gang junction box.

I'd run two hots, a neutral, and one 6 ga bare copper. I'd secure the 4 wires every 4? feet with one of this style multi-cable staples.

Can I run two hots and one neutral and one ground through a single hole in the top plate, say 1.25"?

Would this pass NEC 2017?

Thanks

Capture2.JPG
 
To avoid these ads, REGISTER NOW!

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
No, that would be against code. THHN wire must be run in conduit only. You cannot staple it to framing members or run it outside of conduit for any length at all. You'd need to run conduit from the panel, across the garage, to the junction box, and pull the wires through the conduit in order to use it.
 

BreeStephany

ALLIANCE MEMBER
Joined
May 19, 2012
Messages
851
Location
Oregon
THHN must be run in an approved raceway / conduit and protected from damage, so running it "free-air" would not be code compliant. You may use NMB or SER cable, provided that you plan on putting up sheetrock, wood sheeting or another means to protect the cable from damage, but you may NOT run exposed THHN conductors without running them in conduit from the panel to the point of termination.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,994
Location
Central Iowa
1) Got it. Thanks.
2) Potential future EV charger. Potential 30 amp for welding. Potential ?? for future.
A two gang box is all that's needed.
Understood. I have 600 feet of #4 on hand from a project that never happened 10 years ago. May as well use it rather than buy more copper.
scrap the #4 and use the money to buy 6/3 with ground NM-B (romex) for a 14-50R for a 50 amp charget. As far as the 30 amp for a welder, get 10/2 romex ( A lot of welders can get by with #12). If the lengths are short enough, you might still have money left over.
 
Last edited:

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,836
Location
Southern Oregon
A two gang box is all that's needed.

Idea is to run it from a 60 amp 2 pole breaker in the panel which is in the detached garage, up through wooden framed top plate (13' high), along the bottom of one of the wooden roof trusses, across to the wall opposite the panel, then down through top plate and terminate in a 3 gang junction box.

2) Potential future EV charger. Potential 30 amp for welding. Potential ?? for future.

Seeing this as OP wants to run a 60A circuit with his #4 and connect multiple receptacles in a 3 gang box to that #4.

OP, you need a separate circuit for each of those. And the appropriate sized cable. And a separate 2 gang box for each will make wiring much easier. And you'll be able to locate each receptacle where you need it.
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,994
Location
Central Iowa
Seeing this as OP wants to run a 60A circuit with his #4 and connect multiple receptacles in a 3 gang box to that #4.

OP, you need a separate circuit for each of those. And the appropriate sized cable. And a separate 2 gang box for each will make wiring much easier. And you'll be able to locate each receptacle where you need it.
You may be right. I never even considered it a possibility that anyone would think about trying to stuff three 30+ amp receptacles into a box and/or put them on the same circuit. I was putting "or" between every thing on the list of possibilities. charger or welder or ???
Why do I need separate circuits from breaker box? Not arguing; I want to learn from those who've done this more than I.
Because that's the way it is. I'm not going to go look up a code reference just to prove it, but it's true.
 
Last edited:
OP
L

luvtheheat

Well-known member
Joined
Jan 28, 2017
Messages
489
Location
Tucson AZ
I really appreciate all the responses. Again, I'm here to learn, not to question/challenge those who have much more experience.

Thanks
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,274
Location
Coastal NJ
I really appreciate all the responses. Again, I'm here to learn, not to question/challenge those who have much more experience.

Thanks
Seems you have some heavy wire you'd like to use for some down the road powering of some larger loads. If that is as far as you can commit at this juncture then:
Run conduit and install a subpanel at the end of the run. With the correct size conduit and breaker in the main panel, you will be able to power many many different types of loads in a code compliant fashion.

Sub panels are cheap. A main lug panel is sufficient.
 
Last edited:
OP
L

luvtheheat

Well-known member
Joined
Jan 28, 2017
Messages
489
Location
Tucson AZ
Seems you have some heavy wire you'd like to use for some down the road powering of some larger loads. If that is as far as you can commit at this juncture then:

Run conduit and install a subpanel at the end of the run. With the correct size conduit and breaker in the main panel, you will be able to power many many different types of loads in a code complaint fashion.

Sub panels are cheap. A main lug panel is sufficient.
My dream garage is being framed as I type this. I want to future-proof the electrical as much as possible before drywall goes up.

Based on earlier feedback, (THANKS), I'm leaning towards a small subpanel (#2) on the wall opposite my other subpanel (that feeds rest of new garage) and putting 3 ea 2 gang boxes pre-wired each on their own circuit from subpanel #2.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,610
Location
BC
I want to future-proof the electrical as much as possible before drywall goes up.
You can spend loads of time and money on this goal; and still miss something. Or a costly change later for something that didn't suit your needs. Not to mention all the compromises in insulation and air seal.

Utility spaces are better served with surface conduit imho.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
My dream garage is being framed as I type this. I want to future-proof the electrical as much as possible before drywall goes up.

Based on earlier feedback, (THANKS), I'm leaning towards a small subpanel (#2) on the wall opposite my other subpanel (that feeds rest of new garage) and putting 3 ea 2 gang boxes pre-wired each on their own circuit from subpanel #2.
the best way to future proof something is actually by running conduit in the walls to possible future needed locations and leaving it empty until needed....
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,610
Location
BC
Tray normally requires approved cable types. Better rated cable again for hazardous locations.

Cable types normally used inside walls may be considered mechanically protected by elevation alone. That height in my jurisdiction is 5'. A garage/shop may present a grey area.
 