So tell me what you think. I am having solar installed and they promised a 125amp panel (i originally wanted a 200 amp setup but the cost to run all new wire from down the street was just to much money)and they said that the wire coming into the house was enough to handle the 125amp load.
so on Wednesday their electrician came out to replace the old 100amp zinsco style with my so called 125 system. i came home to find this installed. now correct me if i am wrong, but isn't this just a normal 100 amp panel? along with poorly written labeling
and miss matched brands of breakers. it has 12 spots for breakers and as it sits they are all filled now
i sent a email to my contractor telling him it looked like a 100 amp setup was installed and this was his response.
so whos right here?
thanks for your time.
so on Wednesday their electrician came out to replace the old 100amp zinsco style with my so called 125 system. i came home to find this installed. now correct me if i am wrong, but isn't this just a normal 100 amp panel? along with poorly written labeling
and miss matched brands of breakers. it has 12 spots for breakers and as it sits they are all filled now
i sent a email to my contractor telling him it looked like a 100 amp setup was installed and this was his response.
the panel is a 125amp rated buss with a 100amp main. This gives us the ability to have the 30amp beaker required for you PV system. The combination of yhe main & solar beaker cannot exceed 125% of the panel rating. Bottom line, it is a 125amp panel. Hope this clarifies for you.