Question Regarding Duplex 220V Receptacle

superskaterxes

Well-known member
Joined
Jul 31, 2013
Messages
418
Location
Maryland
So right now i have a #2 SER wired to a 30A 220V receptacle in the basement for my air compressor (the #2 wire was existing so i reused it even though its overkill). I now have a 220v welder in my garage which is only about 20 feet from this receptacle and requires a 30A breaker.

How do i go about splitting the #2 wire to two separate 30A 220v receptacles so that i can also plug in the welder? I dont intend to run both items at the same time so the 30A breaker in my main panel can stay the way it is.
 
To avoid these ads, REGISTER NOW!

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
You know that the #2 won't fit the recp so you need a large j-box to pigtail the #2 to two #10's or even 8 stranded. I'd use wire clamps in a separate box and run the wires individually to each recp.
 
OP
S

superskaterxes

Well-known member
Joined
Jul 31, 2013
Messages
418
Location
Maryland
You know that the #2 won't fit the recp so you need a large j-box to pigtail the #2 to two #10's or even 8 stranded. I'd use wire clamps in a separate box and run the wires individually to each recp.

This was more of my question but i did learn something from stuart as well!

Can you post a link to the wire clamps your talking about? i know the #2 is ginormous but i wasent sure what other options i had to attach down to a smaller gauge.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I'm surprised you got #2 to fit a 30A outlet. You should put in a small sub-panel and then put the 240V outlets on separate circuits. How many wires does the SER have; 3 or 4?

Edit: Is the SER copper or aluminum? If aluminum you shouldn't hook it directly to copper using clamps/split bolts. You need the proper splice/reducer to transition from aluminum to copper. Look at Polaris connectors. The proper way is to use a sub-panel and have 2 circuits.
 
Last edited:
OP
S

superskaterxes

Well-known member
Joined
Jul 31, 2013
Messages
418
Location
Maryland
I'm surprised you got #2 to fit a 30A outlet. You should put in a small sub-panel and then put the 240V outlets on separate circuits. How many wires does the SER have; 3 or 4?

It was very temporary and this thread is going to serve as a more permanent replacement. I contemplated doing the sub-panel but i havent quite decided yet and the fact that i have a 2-2-2-4 SER ran all the way back to my main panel already makes it convenient to just use what i have already.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You can get a 2 space 60A main lug panel for less than $15 and a couple breakers for less than $10, so for $25 you have an easy way to add the two 240V outlet circuits.
 
OP
S

superskaterxes

Well-known member
Joined
Jul 31, 2013
Messages
418
Location
Maryland
You can get a 2 space 60A main lug panel for less than $15 and a couple breakers for less than $10, so for $25 you have an easy way to add the two 240V outlet circuits.

hmm i guess that makes sense. Is the rule regarding the max # of circuits in a subpanel w/o having a main breaker 6 spaces or 6 circuits?
 
To avoid these ads, REGISTER NOW!

volleyball

Well-known member
Joined
Aug 29, 2011
Messages
4,127
Location
NY, not NYC
I'd go wit something bigger like
http://www.lowes.com/pd_536990-296-HOM12L125C_1z0yt2s+1z10xme+2z8vm__?productId=50085324&Ns=p_product_qty_sales_dollar|1&pl=1&currentURL=%3FNs%3Dp_product_qty_sales_dollar|1%26page%3D1&facetInfo=Square%20D|$25%20-%20$50

So you can add more if you want. Yo are going to use 4 spaces for those 2 breakers, that would leave 2. You don't want the boxes that can have double the number of circuits as there are spaces.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
So you can add more if you want. Yo are going to use 4 spaces for those 2 breakers, that would leave 2. You don't want the boxes that can have double the number of circuits as there are spaces.

Why are you saying not to use a panel listed with more circuits than spaces?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The requirement of having a main disconnect when there are more than 6 circuits to be disconnected applies to panels that are located in a different structure from where the main service panel is located.

hmm i guess that makes sense. Is the rule regarding the max # of circuits in a subpanel w/o having a main breaker 6 spaces or 6 circuits?
 
OP
S

superskaterxes

Well-known member
Joined
Jul 31, 2013
Messages
418
Location
Maryland
The requirement of having a main disconnect when there are more than 6 circuits to be disconnected applies to panels that are located in a different structure from where the main service panel is located.

Really? so an attached garage wouldent qualify for that? If the rule is really 6 throws then i should be way under for what i plan on adding anyway.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Since the sub-panel will be in your house where the main panel is you aren't required to have a main breaker in the sub-panel. If the sub-panel is located far away from the main panel then you may want a main breaker in the sub-panel as a matter of convenience.

Really? so an attached garage wouldent qualify for that? If the rule is really 6 throws then i should be way under for what i plan on adding anyway.
 

volleyball

Well-known member
Joined
Aug 29, 2011
Messages
4,127
Location
NY, not NYC
Why are you saying not to use a panel listed with more circuits than spaces?
If you are getting a box, go by the number of spaces you will need plus room for expansion. To get the extra circuits, you will need expensive double circuit breakers which are 120 only.
You can use a 6/12 but wit your 4 used it leaves 2 spots. If you are sure you will never add on, go for it. But with a convenient panel maybe you do or a future owner will and then you wish you had a little bigger panel.
I had a 20/40 sub and I replaced it with a 40 because it would be easier and cheaper in the long run.
 