First saying Hello, New Member here. I ran a #8 3 wire thhn (20ft) to my detached garage from my house panel that had to open spots. So I ran double pole 40 amp breaker so I could have 220 to the garage. I used 1 and 2 to the hot of the breaker and 3 to the ground of the panel in the house. I never used the bare ground wire at all. I hook the 1 and 2 to the hot of the sub panel is garage and 3 to the bus bar that the neturals from the 110 outlets go to. Everything is working great, but now I have a 4 wire oven I going to use for a powder coating project. I am asking do I hook up the two hots and put the netural on the bus bar and leave the ground from oven off?
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
This sounds like a mess.

Since you have one post to your name, I'll recommend you do a search in this forum on previous posts detailing how to properly wire a detached garage. It's been covered many many times, so I'm sure you shouldn't have any problem finding the info you're looking for.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Your detached garage, by code should be fed with four wires, two hots, a neutral to an insulated bar, NOT bonded to the panel, and a ground wire to a ground bar that is bonded to the panel. If you did not do this, you did not do it according to any of the codes from recent years.

You need to hook the oven up correctly.

Charles
 
OP
J

J00f150

Member
Joined
Apr 18, 2012
Messages
14
got it I will take care of it. I will hook up the bare wire to ground and hook the netural up correctly now, thanks.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Just asking.. do you have two ground rods at your detached garage? If you have one or none you need to have two. The diagram you posted only says you need one.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
got it I will take care of it. I will hook up the bare wire to ground and hook the netural up correctly now, thanks.

you need to have a ground wire from the garage panel back to the house.
 

coolreed

Well-known member
Joined
Apr 10, 2012
Messages
595
Location
Oklahoma City, It's a Windy Heat.
You should have ran a four wire conductor to your detached garage for 220 VAC operation. Black, Red, White and Green conductors. That is code. The gauge of your conductors should be appropriate for the size load you are going to use. You are stating you are going to expect a 40A load. Then if it was me I would run at least a #8 4-wire copper conductor.

I strongly suggest you look at the National Electric code requirements for your area.
 
OP
J

J00f150

Member
Joined
Apr 18, 2012
Messages
14
Yes coolreed, I ran #8 wire 4-wire out to the garage. Guys I hooked it up as per diagram I posted eariler, and I feel much safer now, and everything working good. thanks
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Just asking.. do you have two ground rods at your detached garage? If you have one or none you need to have two. The diagram you posted only says you need one.
If using ground rods ONE rod is code. You only need two if you can't prove the 25 ohm resistance. Since very few of us have the $1200 tester to make this test we just install two.
I will say, in my area inspectors rarely if ever ask for the test/results.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I'm very well aware that one rod is code if you meet the 25 ohm requirement, but common practice is to just use two. Our AHJ will ask for two regardless.

If using ground rods ONE rod is code. You only need two if you can't prove the 25 ohm resistance. Since very few of us have the $1200 tester to make this test we just install two.
I will say, in my area inspectors rarely if ever ask for the test/results.
 

VHF

Well-known member
Joined
Oct 27, 2008
Messages
420
Location
NW Wisconsin
Now that you have the correct 4-wire feed to your detached garage, did you make sure to remove the neutral-ground bonding screw in your subpanel? The neutral and ground should only be bonded in your main panel.
 