Quick conduit fill question
rust buster
VA
Can someone verify whether or not I can do this?
Can I run (3) #6 THHN conductors, (3) #10 THHN conductors, and (3) #12 THHN conductors in a 3/4" EMT conduit? I'm getting mixed results on the online calculators I am reading.
Running from my panel in the shop to a two post lift, so it's the lift power, a welder outlet, and a 20A general use outlet.
Thanks in advance.
R
rust buster
VA
Thanks for the quick response Stuart. I can't get that link to work, but it might be my computer.
Stuart in MN
Minneapolis
That's odd, I'll try posting the link again: http://www.electrician2.com/calculators/rf_calculator.html
edit: fixed the link.
A few other things to consider. I'm assuming the #6 wires are for the welder circuit, if so you can probably downsize the ground wire to a #10. Secondly, depending on what you're doing at the far end (is all this going into a junction box, then splitting off to each circuit?) you can share a single ground wire. Third, if the EMT is a continuous metallic path you may be able to use it as the ground connection instead of running separate wires. However, there may be local restrictions on this method; also some prefer not using the conduit as the ground connection as there's the possibility of a loose conduit fitting in the future.
FarmerPete
Lansing, MI
You're going to have to derate with that many conductors. From my experience working with #6 in a 3/4 EMT, I would recommend going to 1".
R
rust buster
VA
Yeah, based on all replies, I think I am going to run two different runs of 3/4" conduit. Keep the #6 in one run and then the #12 and #10 in another. I already have plenty of the 3/4" and this will allow me to keep the wire length down since I can run them in a direct route to their end location.
ddawg16
S. California
If the run is of any distance, I would up size to 1". Especially if you have 2-3 90's in there. It just makes life a whole lot easier and the cost difference is minimal.