TT_Vert
Well-known member
I'm not going to run this as I cannot easily bend 1" EMT so i'll leave it to the pros. Anyway the run is less than 40'. I am having them run 4AWG THHN to a service disconnect. THHN is rated at 95A derated to 76A for continuous use. I am only running 3 current conductors and have no thermal derate so I should be good w/a 70A breaker based on my calcs. What is throwing me is that I am reading about people derating their breaker. In essence people w/ 60A breakers are saying they can only charge at 48A. Is this because they are ASSUMING (rightfully so) that the wiring is the bare minimum for a 50A NON continuous load? This would make sense to me but I just wanted to confirm. In my case, knowing my derates and running the appropriate breaker for them (70A) I could safely run a continuous 70A load correct? I won't be doing that but I may be using two 30A chargers at some point.
Thanks much,
Dave